Fit a level control on the tower pond, a solenoid valve driven by it on the make-up line and a totalising flowmeter in the make-up line itself. Read the flowmeter at intervals and record.
__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
I think they want the calculations, formulas and examples, with pictures. Along with a step-by-step breakdown of your thought processes during the calculations.
Too bad - especially as practically no-one else does it like that.
__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Evaporating water accounts for about 1000 Btu/lb. A surplus of water ("bleed-off") should also be provided. The surplus amount varies with the mineral content of the water and any treatment, but a rule of thumb is that it can equal the amount evaporated.
__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
M = Make-up water in gal/min
C = Circulating water in gal/min
D = Draw-off water in gal/min
E = Evaporated water in gal/min
W = Windage loss of water in gal/min
X = Concentration in ppmw (of any completely soluble salts … usually chlorides)
XM = Concentration of chlorides in make-up water (M), in ppmw
XC = Concentration of chlorides in circulating water (C), in ppmw
Cycles = Cycles of concentration = XC / XM
ppmw = parts per million by weight
A water balance around the entire system is:
M = E + D + W
Since the evaporated water (E) has no salts, a chloride balance around the system is:
From a simplified heat balance around the cooling tower:
(E) = (C) (ΔT) (cp) / HV
where:
HV = latent heat of vaporization of water = ca. 1,000 Btu/pound
ΔT = water temperature difference from tower top to tower bottom, in °F
cp = specific heat of water = 1 Btu/pound/°F
Windage losses (W), in the absence of manufacturer's data, may be assumed to be:
W = 0.3 to 1.0 percent of C for a natural draft cooling tower
W = 0.1 to 0.3 percent of C for an induced draft cooling tower
W = about 0.01 percent of C if the cooling tower has windage drift eliminators
Concentration cycles in petroleum refinery cooling towers usually range from 3 to 7. In some large power plants, the cooling tower concentration cycles may be much higher.
(Note: Draw-off and blowdown are synonymous. Windage and drift are also synonymous.) for metric....
__________________
All living things seek to control their own destiny....this is the purpose of life
CR4 Admin: Spam: This post was modified because it contained advertising outside the Commercial Space forum. Please review Section 14 of the CR4 Site FAQ about advertising.
Approx. 1 pound of water for each 1000 Btu of heat rejected, plus a similar amount for bleed-off or blow-down (or whatever you call it), plus maybe 2% for drift (droplets that blow away).
__________________
In vino veritas; in cervisia carmen; in aqua E. coli.