Testing of Three Phase Transformer

07/13/2012 5:07 AM

if we short LV blue phase(b) and HV blue phase(B) of 33kv/430v 1ooKVA step down transformer and supply a single phase voltage to HV red (R) phase with respect to Y phase then what would be the other voltages for a transformer to work normally.

ie. RY voltage is known(say it is 200v) what would be the values of:

RB, YB, ry,rb,yb...

what this test z called???

thanking in advance

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: testing of three phase transformer

07/13/2012 5:18 AM

Does it say do this in the equipment manufacturer's commissioning instructions? Come to think of it, where is the manufacturer's Commissioning Engineer in all this?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply Off Topic (Score 5)
Power-User

Join Date: Nov 2011
Posts: 286
Good Answers: 15
#2

Re: Testing of Three Phase Transformer

07/13/2012 6:56 AM

Can only agree with Mr Slack on this. The questions you are asking suggest you are a little out of your depth.

Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#3

Re: Testing of Three Phase Transformer

07/13/2012 7:14 AM

Hmm.... This sounds like a good Newsletter Challenge.

The energized primary winding will induce voltages in the other two, but not in normal 120° phase relationship....

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#4

Re: Testing of Three Phase Transformer

07/13/2012 11:10 PM

This, in fact, is called the vector group test in transformers.

Register to Reply
Guru

Join Date: Aug 2010
Posts: 687
Good Answers: 21
#5

Re: Testing of Three Phase Transformer

07/14/2012 3:37 PM

Goggle

PROF. V. G. PATEL, he has a paper posted on web that explains this test.

Fixitorelse

Register to Reply