Transformer Calculation

07/20/2012 4:49 AM

Hi,

I am living in Lahore, Pakistan. We have 40 houses in our lane and are using following appliances

No. of Air conditioners (18000 BTU)= 2/house

No. of refrigerators (16 Cubic Ft) =2/house

No of Ceiling Fans (150W) =4/house

No. of lights (40W) =6/house

No. of TV =2/house

No of Computers =2/house

No. of Washing Machines =1/house

No. of Microwaves =1/house

No.of Water pumps =1/house

Question is how many KVA transformer would be enough for 40 Houses ?

Thanks with regards

TIRMIZI

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Associate

Join Date: Feb 2012
Posts: 28
#1

Re: Transformer calculation

07/20/2012 5:34 AM

kw=pf*kva(t/f rating)... each house 350KW/HOUSE,350*40=14MW.IF YOU HAVE MANY MOTORS USED TO PF IS VERY LOW.APPROXIMATLY PF 0.8,

KW=14000.

PF=0.8,

KVA=17500KVA. YOU HAVE 17.5MVA RATING TRANSFORMER SUITABLE FOR YOUR HOUSES. THIS IS APROXIMATLY NOT EXACTLY....

Register to Reply Off Topic (Score 8)
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#2

Re: Transformer calculation

07/20/2012 5:34 AM

The local utility company will have ready-reckoners for this sort of thing that are based upon local experience, so these people would be the best ones to approach.

  • In the UK, for instance, each home will usually have a 100A rated and fused single-phase feeder at 230V. However, no home draws 100A all the time, and a measure of diversity will be used to size the transformer; locally the average current drawn over a quarter-year is 2A or so for a home that uses electric cooking and if the cooking is otherwise then the average draw will be somewhat less. Larger homes might run to a three-phase supply at a higher tariff, though the single-phase loads will be split across the three phases; there is little of a domestic nature that requires a three-phase supply in itself.
__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Anonymous Poster #1
#13
In reply to #2

Re: Transformer calculation

07/24/2012 12:14 PM

thank you for advice..

Register to Reply Off Topic (Score 5)
2
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#3

Re: Transformer Calculation

07/20/2012 7:29 AM

Without knowing what diversity factors you are allowed (or required?) to use, my estimate is 250 KVA, which at 0.8 PF would equate to 200 KW.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply Good Answer (Score 2)
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#4

Re: Transformer Calculation

07/20/2012 11:17 PM

In a Ms excel sheet enter the loads,diversity factor,load factor etc and calculate. If not sure show it to an experienced engineer and verify.

__________________
pnaban
Register to Reply Score 1 for Good Answer
Associate

Join Date: Sep 2011
Posts: 26
#5

Re: Transformer Calculation

07/21/2012 1:38 AM

Trimzi sb, would u take 11KV feeder from LESCO? which area is that in Lahore? Transformer is the property of LESCO in Lahore and they provide it according to your load.

Register to Reply
Participant

Join Date: Jul 2012
Posts: 4
#7
In reply to #5

Re: Transformer Calculation

07/21/2012 2:12 AM

Zaman Sb Assalam O Allaikum,

We all are layman, Let me brief you, As I told you that we have 40 houses in our lane. there are 5 lanes that are running on 1 transformer of 250 KVA. Every day that transformer turns out of order and we spend our whole night in the street. We have requested LESCO several times but they did not agree that its overloaded. After several years of efforts they agreed to provide one more transformer of 100 KVA that will share the load of previous one of 250 KVA for the same 5 lanes (each contains 40 house). When I do calculate our one lane need approximately 200 KVA load, so how come they dont agree in providing at the rate of 200 KVA for each lane.

I am living in Nizam block, Allama Iqbal town Lahore.

How can we ask them to provide 11 KV feeder from them? or even we dont know which feeder supplies here.

This was the reason I wanted to know from experts that what should be the capacity of that transformer for 1 lane ?

regards

TIRMIZI

Register to Reply
Participant

Join Date: Jul 2012
Posts: 4
Good Answers: 1
#6

Re: Transformer Calculation

07/21/2012 2:00 AM

The total KW will come around 200KW and if the power factor will be taken =0.8

then the total KVA required will be around 250KVA

but the above calculations based on total connected load without diversity factor consideration.

Register to Reply Score 1 for Good Answer
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#8

Re: Transformer Calculation

07/21/2012 2:26 AM

I don't know what LESCO's thinking would be, unless they are trying to size the transformer on average load rather than near peak load. Wouldn't it be more profitable for them to provide adequate transformer(s) and thus sell more electricity?

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Participant

Join Date: Jul 2012
Posts: 4
#9
In reply to #8

Re: Transformer Calculation

07/21/2012 4:10 AM

Yes Tornado, you are absolutely right, but the problem is we have load shedding of 12 hours a day, they don't have electricity (according to them).

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#10
In reply to #9

Re: Transformer Calculation

07/23/2012 9:49 AM

If the supplier simply doesn't have the electricity to sell, then it explains why the supplier is reluctant to replace the transformer with a larger one, and it also explains the power outages. Demand has simply outstripped supply.

However, this would point to a significant investment opportunity for the supplier. Point it out to them.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#11
In reply to #10

Re: Transformer Calculation

07/23/2012 10:04 AM

The Client should submit to the Utility a technical report prepared by an experienced engineer(C.Eng/P.E) showing calculations or readings taken by a power analyser to convince them the actual demand.

__________________
pnaban
Register to Reply
Participant

Join Date: Jul 2012
Posts: 4
#12
In reply to #10

Re: Transformer Calculation

07/24/2012 4:25 AM

They have monopoly, no other party has right to enter as a power supplier directly. If in case someone wants to produce electricity, new entrant will supply to LESCO who has the only distribution rights all over the city LAHORE. ITS A BIG WHITE ELEPHANT working under our beloved MINISTERS

Register to Reply
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#14
In reply to #12

Re: Transformer Calculation

07/24/2012 11:25 PM

Approach a good lawyer or consumer protection authority.

__________________
pnaban
Register to Reply
Register to Reply 14 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); Mushtak T.Majeed (1); pnaban (3); PWSlack (2); rambabugopisetti (1); tirmizi (3); Tornado (2); zamanengineer001 (1)

Previous in Forum: Reactive Power   Next in Forum: HIGH VOLTAGE CABLE SELECTION

Advertisement