Generator Rotor Earth Fault in 600 MW Steam Generator

07/30/2012 9:07 AM

Actually I am writing from a power House. We have two units of 600 MW capacity out of two units in unit no#1 there is a problem in Rotor Earth fault. Our generator is of static excitation system. The generator was running in 300 MW and tripped due to some system disturbance in Electrical fault like Differential protection. Just after tripping of generator we are found there is 1-3 HZ Rotor earth fault protection has been acted and it is not getting resetted. After checking found the IR value of Rotor is about of 0 ohms during turning gear of about 2500 RPM. And we got the same IR value of rotor up to about 48 hours when turbine is running in turning gear also. After about 48 hours we got during turning gear IR value of 200 Mega ohms and during half cycle of turning gear the IR value was 0 ohms and in remaining half cycle IR value was of >200 M ohms. And again after 10 hours we are found the IR value of rotor is 300 mega ohms in complete cycle of rotation. So, Again we have run the generator and when the turbine speed was coasting up at about of 300 RPM , we found that the 1-3 HZ Rotor earth fault relay was acted and it is not getting re-seted. when we have checked the IR value in this condition found of 0 mega ohms. Now we are not getting any fault. Kindly suggest.

__________________
Binod Kumar Panda
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Generator Rotor Earth Fault in 600 MW Steam Generator

07/30/2012 9:25 AM

Believe the earth fault relay, and refer to the original equipment manufacturer's operation and maintenance manual under the section called "troubleshooting". If a suitable solution cannot be found there, contact the manufacturer directly by telephone.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply Score 1 for Good Answer
Active Contributor

Join Date: Jan 2009
Location: Anpara,sonebhadra,UP
Posts: 14
#9
In reply to #1

Re: Generator Rotor Earth Fault in 600 MW Steam Generator

08/02/2012 10:41 AM

Thanks for Reply, Actually we got the IR value of 0 ohms between Rotor Shaft and Slip rings. So, there is not doubt over Earth fault Relay.

__________________
Binod Kumar Panda
Register to Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#2

Re: Generator Rotor Earth Fault in 600 MW Steam Generator

07/30/2012 10:47 AM

By the by, Are you from Anpara 'C'?

Register to Reply
Guru
Engineering Fields - Mechanical Engineering - New Member India - Member - New Member

Join Date: Aug 2008
Location: City of destiny, INDIA
Posts: 775
Good Answers: 67
#3
In reply to #2

Re: Generator Rotor Earth Fault in 600 MW Steam Generator

07/30/2012 11:45 AM

Long ago, may be about 30 years back I was passing through Anpara, I saw a huge board written APSEB site for 3100 MW thermal power Plant.

Register to Reply
Active Contributor

Join Date: Jan 2009
Location: Anpara,sonebhadra,UP
Posts: 14
#10
In reply to #2

Re: Generator Rotor Earth Fault in 600 MW Steam Generator

08/02/2012 10:42 AM

Yes, I am in Anpara "C".

__________________
Binod Kumar Panda
Register to Reply
Anonymous Poster #1
#15
In reply to #10

Re: Generator Rotor Earth Fault in 600 MW Steam Generator

08/29/2012 7:30 AM

OK

Register to Reply Off Topic (Score 5)
Active Contributor

Join Date: Jan 2009
Location: Anpara,sonebhadra,UP
Posts: 14
#14
In reply to #2

Re: Generator Rotor Earth Fault in 600 MW Steam Generator

08/29/2012 7:27 AM

No, Iam From MP.

__________________
Binod Kumar Panda
Register to Reply
Guru

Join Date: Jun 2011
Location: Phnom Penh
Posts: 4019
Good Answers: 102
#4

Re: Generator Rotor Earth Fault in 600 MW Steam Generator

07/31/2012 1:31 AM

.....So, Again we have run the generator and when the turbine speed was coasting up at about of 300 RPM , we found that the 1-3 HZ Rotor earth fault relay was acted and it is not getting re-seted. when we have checked the IR value in this condition found of 0 mega ohms. Now we are not getting any fault. Kindly suggest.

Suggestion 1

Decide whether you do or don't have a fault.

Suggestion 2

Ask your technical director to actually give you the resources to do your job and to stop diverting the maintenance budget.

Suggestion 3

Don't let anyone there know who you work for until the contemporary massive blunder has been forgotten.

__________________
Difficulty is not an obstacle it is merely an attribute.
Register to Reply
Power-User

Join Date: Sep 2008
Posts: 196
Good Answers: 6
#5

Re: Generator Rotor Earth Fault in 600 MW Steam Generator

07/31/2012 11:13 AM

Pandabinod;

"The generator was running in 300 MW and tripped due to some system disturbance in Electrical fault like Differential protection. Just after tripping of generator we are found there is 1-3 HZ Rotor earth fault protection."

Your description of the trip event coupled with earth fault relay event(s) resulting in generator "lockout" and the different values in Megohms being observed when the rotor is on turning gear indicates you have suffered serious rotor conductor failure. Most likely the wedging and/or binding has become loose and damage has been done to the winding insulation allowing contact between the conductor(s) and the rotor laminations. If the windings are not secure, the rotation of the rotor coupled with the weight of the conductors will allow different amounts of pressure to be applied to the contact point thereby resulting in random values of impedance when referenced to earth.

This is a high critical safety risk not only to the machine but also to all personnel working in the immediate area. You need to hire a competent generator service company to perform a thorough electrical test of the generator before attempting a re-start of the machine.

Because of the 600MW size of the unit I am assuming it is Hydrogen cooled which if ignited by the electrical arc/spark from an earth contact can result in catastrophic (explosive) failure of the generator.

If this should occurr, the damage will be extensive, is unbelievable when observed, and will cause damage to periphial structure and adjacent equipment.

You need to be extremely cautious and careful with this machine and you really need expert advice and help. Now!

Register to Reply
Guru

Join Date: Feb 2010
Posts: 1013
Good Answers: 36
#6
In reply to #5

Re: Generator Rotor Earth Fault in 600 MW Steam Generator

07/31/2012 11:35 AM

Hydrogen Cooled?! In my view it should have blown long time ago!

Register to Reply
Power-User

Join Date: Sep 2008
Posts: 196
Good Answers: 6
#7
In reply to #6

Re: Generator Rotor Earth Fault in 600 MW Steam Generator

07/31/2012 12:39 PM

The fuel-to-air ratio has to reach the exact proportion in order for the hydrogen to ignite.

This has happened way too many times due to poor maintenance & operations practices and is fueled by ignorance of the cooling system operation and inherent risk . The most recent event I am familar with was over in the Arab Immigrate area in late 2011 wherein a 350 MW unit failed and took out everything around it from the basement up to the roof and both units on each side. Amazingly there was not any fatalities other than the equipment. This particular event was triggered by the mechanical failure of the "jack" shaft between the prime mover and the generator.

Below is a link with good information as to the mechanics of the cooling system.

I have some pictures taken at the site that will send chills down your back if you think about what could have happened.

http://search.yahoo.com/r/_ylt=A0oG7uAFBhhQKRgAgYpXNyoA;_ylu=X3oDMTE1dTZma2ZnBHNlYwNzcgRwb3MDMgRjb2xvA2FjMgR2dGlkA01TWTAwM18xMjU-/SIG=12f8t6eqt/EXP=1343780485/**http%3a//en.wikipedia.org/wiki/Hydrogen-cooled_turbogenerator

Register to Reply
Guru

Join Date: Feb 2010
Posts: 1013
Good Answers: 36
#8
In reply to #7

Re: Generator Rotor Earth Fault in 600 MW Steam Generator

07/31/2012 12:53 PM

More reason not to temper with such installations if not qualified by the OEM! Immagine if some fault has developped and these signs should be telling the maintenance people to call the big guys before going any further with experimenting/testing!

Register to Reply
Active Contributor

Join Date: Jan 2009
Location: Anpara,sonebhadra,UP
Posts: 14
#11
In reply to #6

Re: Generator Rotor Earth Fault in 600 MW Steam Generator

08/02/2012 10:45 AM

Thanks for reply. Yes our generator of Hydrogen cooled. but we are getting variable IR value in diffrent position of Rotor when it is running in turning gear.

__________________
Binod Kumar Panda
Register to Reply
Guru

Join Date: Jun 2011
Location: Phnom Penh
Posts: 4019
Good Answers: 102
#12

Re: Generator Rotor Earth Fault in 600 MW Steam Generator

08/02/2012 12:17 PM

Are you hoping that somebody will tell you that something isn't rubbing?

Denial is not a river in Africa......deal with the problem, start taking things apart slowly and looking really carefully.

__________________
Difficulty is not an obstacle it is merely an attribute.
Register to Reply
Power-User

Join Date: Mar 2010
Location: BHOPAL, INDIA
Posts: 201
Good Answers: 20
#13

Re: Generator Rotor Earth Fault in 600 MW Steam Generator

08/19/2012 8:01 AM

This type of rotor earth fault is called "flying rotor earth fault". This indicates that there is contact of rotor conductor and rotor body due to:

1. loose conducting particle making contact at certain position of the rotor and moving to some other position at other position of rotor. This position may change from time to time (as the particle is loose).

2. The slot insulation damaged and changes position at different speed / position of rotor.

One thing you could attempt to burn the fault by running the rotor at speed where earth fault appears and stays. You may get this condition even at stand still position. Apply small variable voltage between one slip ring and rotor body. You may reach rotor body through rotor earthing brush. Increase the voltage till loose particle burns due to passage of current. If you are lucky, your rotor may become healthy else the fault will become permanent. Then you need to get it attended by OEM or other agency competent to take repair work.

Do not run the generator with this type of fault as second earth fault may prove to be catastrophic.

Register to Reply Score 1 for Good Answer
Participant

Join Date: Jun 2017
Posts: 2
#16

Re: Generator Rotor Earth Fault in 600 MW Steam Generator

06/03/2017 1:43 PM

Dear sir

Can u please tell what are the faults you got in the rotor after that or what action u had taken ?

Register to Reply
Register to Reply 16 comments

"Almost" Good Answers: