Actually I am writing from a power House.
We have two units of 600 MW capacity out of two units in unit no#1 there is a problem in Rotor Earth fault. Our generator is of static excitation
system. The generator was running in 300 MW and tripped due to some system
disturbance in Electrical fault like Differential protection. Just after
tripping of generator we are found there is 1-3 HZ Rotor earth fault
protection has been acted and it is not getting resetted. After checking found
the IR value of Rotor is about of 0 ohms during turning gear of about 2500
RPM. And we got the same IR value of rotor up to about 48 hours when
turbine is running in turning gear also. After about 48 hours we got during turning
gear IR value of 200 Mega ohms and during half cycle of turning gear the IR value was 0 ohms and in remaining
half cycle IR value was of >200 M ohms. And again after 10 hours we are found the IR value of rotor
is 300 mega ohms in complete cycle of rotation. So, Again we have run the generator
and when the turbine speed was coasting up at about of 300 RPM , we found that the 1-3 HZ Rotor earth fault relay was acted and it is not getting re-seted. when we have checked the IR value in this condition found of 0 mega ohms. Now we are not
getting any fault. Kindly suggest.