Fan Design

08/09/2012 3:08 AM

Centrifugal Fan designed for Ambient Temp of 45 'C , Altitude of 100 M & Pressure of 450 DaPa is propsed to be used at Ambient of 25'C & Altitude of 1000M. What would be the Pressure Drop & change in Vol. Present fan capacity is 130,000 AM3/hr.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: FAN DESIGN

08/09/2012 3:58 AM

Ask the designer.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#2
In reply to #1

Re: FAN DESIGN

08/09/2012 10:13 AM

What designer? It's a homework problem.

Register to Reply
Guru

Join Date: Feb 2011
Location: Atlanta, GA
Posts: 1053
Good Answers: 110
#4
In reply to #2

Re: FAN DESIGN

08/10/2012 10:40 AM

If ever there were one!

__________________
Think big. Drive small.
Register to Reply
Active Contributor

Join Date: Oct 2011
Posts: 10
#3

Re: Fan Design

08/10/2012 12:25 AM

Sorry did not get pls reply if u got the answer Iam from HVAC

Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#5
In reply to #3

Re: Fan Design

08/10/2012 10:41 AM

How's the weather in HVAC?

Register to Reply
Guru

Join Date: Dec 2005
Posts: 1602
Good Answers: 19
#6
In reply to #5

Re: Fan Design

08/10/2012 11:46 AM

Kind of windy in here!

__________________
Eventually, one needs to realize that it is far less important to be the smartest person in the room than it is to sit next to that person and make friends.
Register to Reply Off Topic (Score 5)
Guru

Join Date: Jun 2008
Location: Oman
Posts: 612
Good Answers: 14
#7

Re: Fan Design

08/10/2012 2:02 PM

Check any reputed fan manufactures technical literature. You can also refer any good academic books on fan & blowers or refer ASHRAE handbook

Register to Reply
Guru

Join Date: Dec 2005
Posts: 1602
Good Answers: 19
#8

Re: Fan Design

08/10/2012 3:37 PM

Get a copy of the fan affinity laws and review them carefully. These will guide you in the adjustments needed for changes in temperature and air density (altitude).

Once you understand the laws, the affects of changes will be straightforward to calculate.

__________________
Eventually, one needs to realize that it is far less important to be the smartest person in the room than it is to sit next to that person and make friends.
Register to Reply
Guru

Join Date: Jul 2005
Location: Stoke-on-Trent, UK
Posts: 4496
Good Answers: 137
#9
In reply to #8

Re: Fan Design

08/11/2012 5:55 AM

Homework or not, this is an interesting question. Fan data I've seen is flow vs pressure rise, with inlet at atmospheric pressure. Do the fan affinity laws give more information?

Take a fan delivering a certain flow to a system which has ΔP as Q2 (likely to be simplest case) and ΔP say 45 mbar to take OP's figure (low enough for compression to be negligible), the whole lot being at sea level.

If it's then taken up to where the pressure is 0.5 atm, what happens? My guess is the actual flow stays the same, ΔP falls to 1/2 (same velocity, density halved) and power drawn falls to 1/2 (same flow, ΔP halved).

What do you (and others) think?

__________________
Give masochists a fair crack of the whip
Register to Reply
Guru

Join Date: Dec 2005
Posts: 1602
Good Answers: 19
#10
In reply to #9

Re: Fan Design

08/11/2012 10:03 AM

Its been 40 years since I was in school. But I think you are getting close to understanding this. If in Codemaster's case pressure is halved, what happens to the mass flow of the fan while the volume delivered remains the same?

Is the pressure drop a result of volume flow, or mass flow, or velocity?

__________________
Eventually, one needs to realize that it is far less important to be the smartest person in the room than it is to sit next to that person and make friends.
Register to Reply
Guru

Join Date: Jul 2005
Location: Stoke-on-Trent, UK
Posts: 4496
Good Answers: 137
#11
In reply to #10

Re: Fan Design

08/11/2012 12:10 PM

Thinking about this a bit more (prompted by your comments), halving the inlet pressure (and hence air density) is equivalent to reducing the liquid SG in a centrifugal pump. In that case, as is well known, if it's pumping into an all-friction, Q2 system, the generated head in m liquid stays the same, so the pressure rise halves, and the system pressure drop also halves. That seems to support my guess.

To answer your question 1 - the mass flow halves (same flow, 1/2 density)

Is the pressure drop a result of volume flow, or mass flow, or velocity? Either volume flow or mass flow, velocity, and also density come into it. Whether you use actual volume flow, or mass flow (which is equivalent to standard or normal volume flow) density is still in the formula.

__________________
Give masochists a fair crack of the whip