08/16/2012 8:52 PM
Power factor in dry type transformers. Is there a standard that is used for motor loads combined with resistive loads?
Thank you for your help - By far the best info site!
Re: Power Factor in Dry Type Transformers
08/17/2012 1:36 AM
As long as the total KVA (loads summed vectorially) is less than the transformer rating....
08/17/2012 5:04 AM
...otherwise the overcurrent protective device will disconnect it.
Good Answers: 15
08/17/2012 9:36 AM
Will your resistive load affect the pF??
08/17/2012 10:17 AM
yes! as all the rest of the loads.
“For no man can forbid the spark nor tell whence it may come.” ? Francis Bacon
Good Answers: 44
08/17/2012 11:07 AM
Purely resistive loads are not considered for power factor correction. Concentrate on the inductive load.
08/17/2012 7:35 PM
HI Jraubsr. If you have a need for a motor to drive a reasonably constant load you could use a synchronous motor and adjust the field exitation to help adjust load pf. This is not the cheapesyt opption but pf can be easily adjusted using this method.
08/17/2012 8:47 PM
There no difference as long as power factor concerned between Oil Type or Dry type transformers. There is also no standard for power factor. It depends upon loads in KVA. Resistive load offer the unity power factor where as the induction motor offer the lagging power factor.
B.E, M.I.E, M.S