Why there is many times voltage pick at an induction after the supply to it get interrupted ?
Re: voltage increase at the induction
08/19/2012 12:06 PM
08/19/2012 12:09 PM
Better to put my qwestion so:
Why instantaneous voltage rise on an disconnected coil can exceed many times the nominal supply level ?
08/19/2012 12:20 PM
Why not make it easy on us all?
Download this site, thoughtfully provided by the sponsors of this forum:Engineering Toolbar
Re: Voltage Increase at the Induction
08/19/2012 8:45 PM
dI/dt.
08/19/2012 8:51 PM
That, too.
Good Answers: 73
08/20/2012 11:13 AM
In the text book under inductors you will find an equation for voltage that looks like this: v=di/dt
This says that the voltage on the inductor = rate of change of the current.
So if the current was flowing along, just minding its business and you come along and change it by disconnecting it, the rate of change is very very small.
Now, what happens when you divide by something very very close to zero?
08/20/2012 2:48 PM
So, it is also true for an active load too ?
08/21/2012 6:23 AM
#8↓ is true for all loads.
Anonymous Poster #2
08/21/2012 6:22 AM
V=di/dt
V=L.di/dt
08/21/2012 1:47 PM
Thanks ! - now I am aware of this.