Damaged MV Voltage Buried Cable

08/20/2012 1:11 AM

Dear all,

I have a 300 meters (it was around 1Km, I did find the other damaged parts) )damaged mv (15KV)voltage cable (buried) and I do not want to dig the all length of the buried cable(there are also a lot of buried water pipes around, I already damaged some pipes). I do have a megger(a Fluke 1550B MegohmMeter), is there a way/method which could help me to just pin point the exact location where this cable is damaged so that I could just dig there and fix the cable? The location where I am (Angola) right now there are not other devices which could help me at the moment to pin point the location where the cable is damaged. Values measured showing under 500ohms(all 3 phases). I am considering above 1 Giga ohm as good.

Thanks,

Page

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#1

Re: damaged MV voltage buried cable

08/20/2012 1:18 AM

There are devices called "pingers" or "thumpers" that send a signal down the cable. The signal reflects back from the fault, and the time gives the distance to the fault. This may be what you need.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#2

Re: damaged MV voltage buried cable

08/20/2012 6:12 AM

Do not energise the cable.

  • Should the cable become energised inadvertently, after the circuit protective device has operated, simply enlarge the hole where the explosion happened, and the damaged area will be found.
__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Associate

Join Date: Jan 2012
Posts: 25
#4
In reply to #2

Re: damaged MV voltage buried cable

08/21/2012 12:31 AM

Do you think if I put 380 v (from a generator)between phases I might get an explosion where the cable is damaged ? (the cable is buried 1m into the ground)

Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#5
In reply to #4

Re: damaged MV voltage buried cable

08/21/2012 12:37 AM

Right, and where the gophers pop up, dig there....

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#3

Re: Damaged MV Voltage Buried Cable

08/20/2012 10:57 AM

The official name for the "pinger / thumper" is a Time Domain Reflectometer, also known as a TDR. It sends a pulse down the conductor and times it's reflection. Wherever there is a leak to ground, that is where it reflects and by timing the speed of the pulse and reflection return, the TDR tells you how far down the conductor the leak is. This however is a linear measurement, it cannot compensate for turns and curves so it is approximate but it's the best method available. There is nothing you can do with a VOM that will be of any use.

By the way, once you fix the first one, you do the test again, and again, and again, until you end up with a result that equals your known conductor length.

Once you find the leak(s), use a heat shrink repair sleeve rated for your voltage and for underground use.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Associate

Join Date: Jan 2012
Posts: 25
#9
In reply to #3

Re: Damaged MV Voltage Buried Cable

08/21/2012 7:58 AM

I was just wondering ... using ohms´s law and the megohmeter (megohmeter tells me the current that is leaking) and knowing the resistance of the cable wouldn´t there be a formula around to help get the approximate distance where this thing is damage? In the past we did not have TDR around ...

Register to Reply
Guru

Join Date: Jun 2011
Location: Phnom Penh
Posts: 4019
Good Answers: 102
#10
In reply to #9

Re: Damaged MV Voltage Buried Cable

08/21/2012 9:23 AM

Depends on the type of fault. A fault will not alter the cable's characteristics in a predictable manner so once its wallaby ted then the absolute resistance is moot.

Indirect or comparative detection is really the only way to find the fault without visible inspection and all the joys of getting up close to it.

__________________
Difficulty is not an obstacle it is merely an attribute.
Register to Reply
Guru

Join Date: Jun 2011
Location: Phnom Penh
Posts: 4019
Good Answers: 102
#6

Re: Damaged MV Voltage Buried Cable

08/21/2012 1:58 AM

I don't think that OP has access to a TDR where he is.

Rough and ready, might work....measure the resistance to ground form each end (I'm assuming the cable is in ground fault condition). They should be different due to conductor's resistance. Compare the two values. If they are the same then the hole is in the middle section, if they are different then the hole is closer to the end with the lower resistance. That could cut your digging down by half.

__________________
Difficulty is not an obstacle it is merely an attribute.
Register to Reply
Power-User

Join Date: Sep 2011
Posts: 267
Good Answers: 7
#7

Re: Damaged MV Voltage Buried Cable

08/21/2012 2:50 AM

He/She might be able to "wing it". See this article: http://www.eetimes.com/electronics-blogs/engineering-investigations-blog/4212190/It-s-cold--It-s-dark--And-the-TDR-you-need-is-missing-

Register to Reply
Guru

Join Date: Jun 2011
Location: Phnom Penh
Posts: 4019
Good Answers: 102
#8
In reply to #7

Re: Damaged MV Voltage Buried Cable

08/21/2012 3:47 AM

I was thinking similarly but figured a CRO and a pulse generator might also be a bit of a tall ask in Angola.Then how to work out the Vp.....

Who knows? Maybe he can get his hands on a CRO and some parts and build his own cable radar.

He has options now.

Great story thanks.

__________________
Difficulty is not an obstacle it is merely an attribute.
Register to Reply
Associate

Join Date: Jan 2012
Posts: 25
#11
In reply to #8

Re: Damaged MV Voltage Buried Cable

08/22/2012 3:51 AM

I will try theses options today if does not work, we are probably running a 15KV aerial line due to several pipes buried around(also people dig too much in that area). Thanks guys!

Page

Register to Reply
Power-User

Join Date: Sep 2011
Posts: 267
Good Answers: 7
#12
In reply to #11

Re: Damaged MV Voltage Buried Cable

08/22/2012 4:46 AM

With CR4 having issues, I didn't get to post this: http://adslm.dohrenburg.net/troubleshoot/bridgetaps.php and in particular, this article: http://www.epanorama.net/circuits/tdr.html

Register to Reply
Power-User

Join Date: Jun 2010
Location: Kolkata, West Bengal, India
Posts: 172
Good Answers: 1
#13

Re: Damaged MV Voltage Buried Cable

08/24/2012 5:44 AM

Cable fault location can be done by using cable fault locating machine/ system comprising of TDR, SURGE GENERATOR/ THUMPER, MAGNETIC CUM AUIDBLE AMPLIFIER with SEARCH COIL etc. This system is costly and special expertise is required to use and finding/pinpointing underground cable faults. Alternatively High Resistance cable fault locator bridge(based on Wheatstone Bridge principle) can be used if there is a healthy core in the faulty cable and cable length is known. You may also adopt a very cheap method if you have a current or voltage sensor which may be used overground and if there is no other live cable running in the close vicinity of the faulty cable. From the source end of the cable you may connect a welding machine to the faulty core and earth and start welding process. The current through the faulty core travels upto the ground fault location point and returns back to the source through ground( if gound fault resistance is low value ,say,few hundred ohms) and if you move the current/voltage sensor during welding process, the sensor will not glow beyond fault point.

Thanks,

Manindra.

__________________
Manindra
Register to Reply