6.6 kV and 11 kV Transmission Line

08/28/2012 3:09 AM

Hi,

We have a system where we can transmit from 6.6 kV or 11 kV transmission line to feed load at 500 metres apart at headworks. 6.6 kV is generator voltage where two generator are bussed, and stepped up to 11 kV using three phase transformers. If the load is 25 kVA, shall we use 6.6 kV transmission line or 11 kV transmission line? In my opinion, we should do it at 11 kV transmission line because 6.6 kV voltage being bus voltage, any voltage fluctuation can cause the powerplant failure by generator tripping, but partly this can also be avoided by using on load tap changer.

Regards,

sks

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#1

Re: 6.6 kV and 11 kV Transmission line.

08/28/2012 3:14 AM

25 kVA sounds way too podunk for this MV discussion....

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#2

Re: 6.6 kV and 11 kV Transmission line.

08/28/2012 3:39 AM

25kVA? Is that all?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Power-User
Engineering Fields - Electrical Engineering - New Member

Join Date: Dec 2009
Posts: 247
#3
In reply to #2

Re: 6.6 kV and 11 kV Transmission line.

08/28/2012 6:19 AM

should it be around 135 kVA?

sks

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#4
In reply to #3

Re: 6.6 kV and 11 kV Transmission line.

08/28/2012 6:37 AM

Without the original poster specifying which one it is, there seems little scope for further comment in this thread.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Power-User
Engineering Fields - Electrical Engineering - New Member

Join Date: Dec 2009
Posts: 247
#5
In reply to #3

Re: 6.6 kV and 11 kV Transmission line.

08/28/2012 6:42 AM

i mean, the station transformer should be around 135 kVA,

Regs,

sks

Register to Reply
Power-User
Engineering Fields - Electrical Engineering - New Member

Join Date: Dec 2009
Posts: 247
#6
In reply to #5

Re: 6.6 kV and 11 kV Transmission line.

08/28/2012 6:45 AM

this is for 2*1650 kVA hydropower plant in Nepal.

regs,

sks

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#7
In reply to #6

Re: 6.6 kV and 11 kV Transmission line.

08/28/2012 6:49 AM

Then at least 3.5MVA is needed.

The location is irrelevant.

As there is so much at issue with this thread, perhaps it would be better to start a different thread containing all the attributes needed to elicit a swift and comprehensive solution, and abandon this one?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#8
In reply to #7

Re: 6.6 kV and 11 kV Transmission line.

08/28/2012 7:33 AM

I'm glad you can follow this thread PW, it makes no sense to me!!

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#10
In reply to #8

Re: 6.6 kV and 11 kV Transmission line.

08/28/2012 10:04 AM

It is difficult to follow as the original poster is 'in too deep'. The job needs to be farmed-out to a local specialist, and not designed by a CR4 Committee!

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: May 2010
Location: Liverpool, NY
Posts: 961
Good Answers: 131
#9

Re: 6.6 kV and 11 kV Transmission Line

08/28/2012 8:33 AM

From your post, I am making the following assumptions:

1. The 25kVA is for house power (to run the generator and plant controls and protection).

2. You are able to choose whichever you want of the 6.6kV or 11kV to derive your house power.

3. You expect that at least one of the generators is going to be running all the time, or else all the lights go out.

You have not specified where the outgoing connection to the utility is, at 6.6 or 11kV.

Any critical control and protection equipment should be powered by DC anyway, from a battery bank. The charger for it would be run by house power. That way, even if the lights go out you have power for your controls, relays, and circuit breakers / switchgear to operate. Where you take the power to run these is incidental, but I would suggest it is best to pick a connection where utility power can run the charger and other AC loads if both your generators are shut down. If utility connection is at the 11kV level, then that will also give you house power when the main transformer is taken out of service for testing and maintenance (it has to be done occasionally!).

A transformer LTC cannot operate fast enough to deal with voltage fluctuations such as motor starts, etc. Typical tap changing delays result in the LTC changing for longer, slower "trend" changes in voltage level. Again, that's why critical equipment should run off DC.

Otherwise, without a single-line diagram to know how your plant is set up, it is hard to see what advantages or disadvantages each of the connections might have. You could choose either.

__________________
To get the right answers, first you need to ask the right questions.
Register to Reply