Magnetic Starter for Air Compressor

09/02/2012 7:45 PM

My new (to me) used air compressor has a 5HP 23.5 Amp 240V single phase motor. It came witha Square D 3 pole 3 phase Size 1 class 8536 magnetic starter. Following the Square D wiring instructions I've put a jumper from T2 to L3; Line 1 to L1 and Line 2 to L2; T1 and T3 to motor.

When energized, nothing happens. There is no "click" of the contacts connecting. There is 240 v between L1 and L2, and 0 V at either T1 or T3.

How do I troubleshoot?

Thanks.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
2
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#1

Re: magnetic starter for air compressor

09/02/2012 8:11 PM

Push the Reset button, if it was new, generally the Overload Relay comes in a Tripped state, because it was tested as the final step before packaging.

But also, you do know that you have to give it control power, right? If not, please go hire an electrician.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply Good Answer (Score 2)
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#2

Re: Magnetic Starter for Air Compressor

09/03/2012 3:16 AM

Has the breaker tripped on the incoming supply as a result of energising this thing?

If so, then disconnect it and hire a professional electrician.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
Hobbies - DIY Welding - New Member

Join Date: Apr 2008
Location: Bristol, Tennessee
Posts: 1177
Good Answers: 58
#3

Re: Magnetic Starter for Air Compressor

09/03/2012 7:23 PM

Inside the cover is a schematic. The coil is probably 220 volts, will have to be wired right. If it was three phase before, the coil wire was hooked up different.

Manually push the solenoid in with something non-conductive, the motor should run. If it doesn't, your wiring is wrong, call and electrician before you hurt something.

__________________
mike k
Register to Reply
Participant

Join Date: Jun 2012
Posts: 4
#4

Re: Magnetic Starter for Air Compressor

09/03/2012 8:30 PM

Obviously you are not equipped with knowledge on how to connect it...in energizing motors you have to consider two things ...... POWER CIRCUIT and CONTROL CIRCUIT...

You've never mention A1 and A2....switch...these components are under control circuit...

Register to Reply
Power-User

Join Date: Feb 2009
Posts: 176
Good Answers: 6
#5

Re: Magnetic Starter for Air Compressor

09/04/2012 12:27 AM

It is a simple thing to wire or fault find a motor starter especially if you have a diagram & basic knowledge. I agree with the others get a qualified electrician to check it all out & fix the problem. Obviously there is a problem & you have the potential to do some real damage to the starter & It'll cost you a lot more to replace it than paying an electrician for an hour of his time & the other more important reason is the safety of all concerned using the compressor.

Register to Reply
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#6

Re: Magnetic Starter for Air Compressor

09/04/2012 1:07 AM

send us the wiring diagram of the starter.

__________________
pnaban
Register to Reply
Guru

Join Date: Jan 2007
Location: Edinburgh, Bonnie Scotland
Posts: 1335
Good Answers: 23
#7

Re: Magnetic Starter for Air Compressor

09/04/2012 1:52 AM

Have you checked connections as per page 43, diagram 3 here?

A 3-phase starter will require all three lines to have the same (within tolerance) voltage & current across the phases to keep from tripping. If only two are connected, a trip condition is created.

__________________
Madness is all in the mind
Register to Reply
Participant

Join Date: Jul 2012
Posts: 4
#8

Re: Magnetic Starter for Air Compressor

09/04/2012 2:14 AM

check first if the coil of the contactor is good or not(you can check it by multimeter in Ω selection. note:need to cut the power and to remove the control cable )

Also need to be check if the control is 240v or 24v because same control run in 24v and need to be check if the coil of the contactor have power (240v or 24v) in run mode if not need to be check the controller for this system .if you need any help you can send to me an email *

CR4 ADMIN - email address removed

From the CR4 Rules: Do not post phone numbers or email addresses. The CR4 Admin will delete all phone numbers and email addresses posted in threads or comments. You can share this information via the CR4 internal messaging system.

Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#9

Re: Magnetic Starter for Air Compressor

09/04/2012 6:03 AM

Try this. Because it's a 3 pole starter the overload needs the wiring altered.

__________________
The reports of my death are greatly exaggerated.
Register to Reply Score 1 for Good Answer
Guru

Join Date: May 2010
Location: Metro.Manila, Philippines.
Posts: 1269
Good Answers: 27
#12
In reply to #9

Re: Magnetic Starter for Air Compressor

09/04/2012 7:36 AM

Tony-

The motor is rated to operate on 240V, single phase. The wiring diagram you provided has a supply connection marking using N and L. You may have provided an incorrect wiring diagram since the supply lines for a single phase 240 Volts source are normally labeled as L1 and L2.. here in the U.S.

Thanks,

vsar

__________________
vsar
Register to Reply
Guru

Join Date: Jan 2007
Location: Edinburgh, Bonnie Scotland
Posts: 1335
Good Answers: 23
#13
In reply to #12

Re: Magnetic Starter for Air Compressor

09/04/2012 7:46 AM

Only the labeling is different. The two wires in question are 240V apart.

__________________
Madness is all in the mind
Register to Reply
Guru

Join Date: May 2010
Location: Metro.Manila, Philippines.
Posts: 1269
Good Answers: 27
#14
In reply to #13

Re: Magnetic Starter for Air Compressor

09/04/2012 8:02 AM

GM1964 - possibly true, but proper labeling / designations are very important in electrical schematic diagrams or technical drawings..

__________________
vsar
Register to Reply Off Topic (Score 6)
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#15
In reply to #9

Re: Magnetic Starter for Air Compressor

09/04/2012 8:13 AM

Parallel to the start button there should be an auxiliary contact to keep the coil energised when your finger pushing the coil is released and an off button in series with the coil to switch off.

__________________
pnaban
Register to Reply
Active Contributor

Join Date: Aug 2012
Location: Nevada
Posts: 13
#10

Re: Magnetic Starter for Air Compressor

09/04/2012 6:25 AM

Sounds to me like you forgot to wire in your "start stop station". Look again very carefully for that section. Remember that you have to energize the motor starter with voltage to the starter "coil". Look for the coil terminals on the starter. It will tell what voltage it is. My guess would be 120 volts. You can omit the jumper if you put Line 2 to L3 terminal if you have the motor connected to T3. You're going to have one set of contacts not being used with your single phase supply. I would leave the T terminals disconnected to the motor till you get the starter working. Hope that helps.

__________________
Don't panic, and never give up.
Register to Reply
Guru

Join Date: Jan 2007
Location: Edinburgh, Bonnie Scotland
Posts: 1335
Good Answers: 23
#11
In reply to #10

Re: Magnetic Starter for Air Compressor

09/04/2012 6:34 AM

One set of contacts not being used will lead to tripping due to imbalanced load. This is worked round by feeding the supply through two sets in series, as per the drawing in the post before yours.

__________________
Madness is all in the mind
Register to Reply
Active Contributor

Join Date: Aug 2012
Location: Nevada
Posts: 13
#16
In reply to #11

Re: Magnetic Starter for Air Compressor

09/04/2012 8:54 PM

What imbalanced load? It's pretty straight forward. L1-T1, L2-T2, L3-T3 are all closed when energized. It's a relay! Sorry folks. I am going to bow out of this discussion. I don't want to cause confusion for the one asking the question.

__________________
Don't panic, and never give up.
Register to Reply
Power-User

Join Date: Feb 2009
Posts: 176
Good Answers: 6
#17

Re: Magnetic Starter for Air Compressor

09/04/2012 9:13 PM

What appears to be forgotten is that this is a compressor & generally you don't use a latching contact to hold the contactor in, there has to be a pressure switch included in the control circuit to start & stop it or this thing will just keep running until something gives way.

In my 30 years I have never had a problem with overloads tripping from an imbalance when I have not used 1 leg of the overload & contactor & I think the extra wiring is not needed, unless specifically stated it is required by the manufacturer in the instructions for the starter.

There are many safety aspects & requirements that the OP will not know about & are not being discussed & I would recommend that the OP gets a qualified electrician to connect the starter & associated equipment correctly for the safety of every 1 using the compressor

Register to Reply
Associate

Join Date: Dec 2007
Location: Dubai
Posts: 32
Good Answers: 1
#18

Re: Magnetic Starter for Air Compressor

09/05/2012 2:00 AM

Your wiring is correct, assuming that L1(Hot) and L2(N) - what you need to check are as follows:

1. Disconnect motor, and dry run control. - jumper any link that you may suspect

1. Check on/off switch should be wired to the coil of the magnetic starter.

2. check for any LP/HP and auxiliary switch for any open link

3. seek assistance from A/C technicians if you have no skills on electrical troubleshooting

__________________
nlp
Register to Reply
Participant

Join Date: Sep 2012
Posts: 2
#19
In reply to #18

Re: Magnetic Starter for Air Compressor

09/05/2012 9:49 AM

Thank you, thanks all. Consulted an electrician, and despite the fact that this compressor was in service as is prior to my getting it, the starter is not even the correct one. What one gets off a ranch ...

Register to Reply
Register to Reply 19 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!