What happens if run a thermal power plant of more than it s capacity. For example, we are having 135MW unit, but we are running it at 140-142MW. What happens if we continuously running more than its rated capacity?
Re: PLF of Thermal power plant
09/05/2012 4:17 AM
One or more of these, sooner or later:
  • Supply shortage constraint
  • Waste disposal constraint
  • Equipment (wo)manpower constraint
  • Process fluid throughput constraint
  • Process fluid condition/quality constraint
  • Something will run too hot and fail
  • Something will wear out and fail
  • An overcurrent device will operate, disconnecting the load
  • Supply quality constraint
  • Maintenance backlog constraint
  • Catastrophic self-disassembly
  • etc., etc.
09/05/2012 5:11 AM
In effect you will be shortchanging the factor of safety built into the system when designed.
bioramani
Re: PLF of Thermal Power Plant
09/05/2012 11:11 AM
In thermal power plant output is electricity & inputs are water, coal & air. These three inputs & their product works on your system (boiler, turbine, generator, their aux, etc) and electricity generated. If any one system run continuously over rated that system may fail & your production may stop. For example your system is designed for 135 MW normal running & you continuously run with 145 MW i.c. approx 7% higher. More coal to be burn in boiler & for more coal more air is required means more tube lkg in boiler , quality of steam may not maintained by your chemistry tends to turbine blade damage & same analogy for your generator also . Your PLF (yearly basis) ultimately reduce by running continuously more than 5%.
09/05/2012 4:03 PM
Normally we get questions about overloading small kW-sized generators or motors, but the same goes when you scale up to MW size.
Try reading the manuals or manufacturer's literature regarding operation in this way for more information as the detailed answer is rather complex and application, equipment and environment specific.
09/06/2012 12:07 AM
I am also into Operations of 135 MW set. well ur running ur unit at 142 MW and if its constant ur Days PLF wud be higher no doubt. but then consider the amount of Main steam pressure ur operating on which if its lower fine but in case its arnd n above the rated design pressure (14MPa) guess....then surely ur water wall tubes and drum r getting more pressurised than required. If the coal quality is gud then its fine but else it wud very soon cause boiler tube failure for sure.
"No matter how hard the past,you can always begin again."
09/06/2012 12:44 PM
Dear Mr. pradeepdhoni,
You should not run continuously. Continuos over-loading means, the design parameters will undergo changes, which may lead to problems by way of break-down etc.
For best performance - the loading should be between 85 to 90%. Occassionally we can load 100% for a short, very short duration since machinery, supplier keeps some margin 5% to 10% in design/Capacity.
DHAYANANDHAN.S
09/06/2012 1:01 PM
Thanks for all answers, But I heard from my plant operator that they can run upto a maximum of 10% of the rated. I also do not see any problems since they are running at the rated main steam pressure of (13.6-13.8)MPA. And the boiler tubes can withstand the maximum temperature of 540C.
The Specific steam consumption is very good and it is meeting the rated.
09/12/2012 3:24 AM
Then either the design is wrong or #1↑ applies. What do the commissioning records say about plant performance?
Good Answers: 445
09/12/2012 12:28 AM
Many things happen, most of them hidden and none of them good. Your plant operators are conveniently forgetting that the the hidden cost of running above design specs will be the reduced life of the plant. Heat is a silent destroyer of nearly everything mechanical and electrical.
Consider for a moment the ramifications of running the generator at 110% of its rating, although the current goes up by (roughly) 10%, the resultant heating effect (I²R) goes up by (1.1)² or 21%, and since you can't increase the cooling effect of the internal cooling fans (they operate at synchronous speed regardless of the load), the excess heating can quickly raise the temperature of the insulation and bearing lubrication, resulting in both electrical and mechanical deteriation.
Then there's the boiler to consider. The designers built-in wear factors for both the water-side and the fire-side of the tubing, both based upon the design conditions. Although you may feel that everything is OK because the temperature and pressure limits are not being exceeded, you are ignoring the eroding effect of the increased mass flow-rate inside the tubes, and the abrasive effect of additional combustion gas and fly ash over the outside of the tube. The combined effect results in excessive tube wall thinning long before the design life of the plant is ever reached.
You're also ignoring the additional wear and tear on the auxiliaries and process control equipment. Pumps may be pushed to cavitation, bearings exhibit excess wear, control valve cages erode, orifice plates go out of spec, etc., all of which will have a negative effect on the overall operation of the plant.
Perhaps you're thinking that those decisions are being made by the "higher-ups" so you're safe. But not to worry, by the time tube failures become a daily occurrence and the turbine blades start routinely cracking, those operators will have moved on or been retired, and you will have been promoted to their position and left to explain to the plant owners why you can't run the plant at more than half load for more than 50% of the time even though theoretically it still has 50% of its life left.
TANSTAAFL (There Ain't No Such Thing As A Free Lunch)
09/16/2012 3:06 AM
Power supply in your case is from Boiler -> turbine -> generator. Each have its limitation and efficiency ratings. Abuse any one in the chain and as rightly pointed out above will start to shorten their respective life cycles.
Your operator may have told you that they are running within rated design of the boiler pressure ( 13.6 -13.8 Mpa) against 14 Mpa. Congratulations, but have you checked the steam flow rate coming out of the boiler ? Is it within the Boiler MCR ( max continuous rating) ? Have you checked the flue gas quality emitting from the stack ? Has the colour changed from a healthy grey to a darker shade ? have a look at the stack during night - do you see sparks streaking out from the stack top?
How about your turbine - check to see the effect of the poorer steam quality on your rotor blades ? And also wear at the nozzle block.
It will be interesting to do a IR test on your generator stator. See how far the overheating has affected them.
It is better that the system is run to design spec to safeguard your company against a huge re-engineering job later, my friend.