Feedback Signal from a Control Valve

09/16/2012 3:16 AM

Dears

how can i receive a feedback signal from a control valve using SIPART ps2 . showing on my SCADA the actual position for the valve?

Register to Reply
Pathfinder Tags: control valves
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#2

Re: feedback signal from a control valve

09/16/2012 9:53 AM

Well if you identified something about the control valve (fluid controlled, pressure range, control mechanism, manufacturer, etc.) then we might be able to guide you to an efficient way to obtain your feedback. Come to think of it, you don't even ask for an efficient method. You just asked for a possible method. I cannot draw very well but I've always admired Rube Goldberg's work.

Glue a protractor to the valve shaft and focus a web camera onto a pointer that indicates the shaft position. Send this image to a musical conductor of your local Baroque music ensemble. He will use the degree shown in the image to select the tempo and musical piece to be played by the orchestra. This music will then be piped to a musicologist with a stop watch to identify the musical composition and the beats per minute used in this performance. He'll write a review of the performance in your local paper and its web review. A grad student will copy the web review to their blog. You will read the review and translate the review to the valve position and type this value into your SCADA system.

(Just trying to add some humour.)

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Guru

Join Date: Jul 2010
Posts: 669
Good Answers: 176
#3

Re: feedback signal from a control valve

09/16/2012 10:09 AM

There are two means to read position

1) analog output 4-20mA representing position

The LY module is an analog output module option for the PS2:

2) Read the primary HART variable which is position in units of percent

Register to Reply Score 1 for Good Answer
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#4

Re: Feedback Signal from a Control Valve

09/17/2012 3:33 AM

The position of the valve is of less value than information about what is happening to the process variable that the valve is being used to control.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Register to Reply 4 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Iris (1); Joshi (1); PWSlack (1); redfred (1)

Previous in Forum: BOE Exams   Next in Forum: Gravity Damper Capacity Calculation

Advertisement