Convection Inside Electrical Enclosure

10/31/2012 5:22 AM

Problem : An electrical panel(figure of real product on left hand side) Dimensions - 400X450 mm, depth - 100 mm encloses the following components - busbars (3mm thick), modular devices etc. In temperature rise test (IEC:2009 61439), the enclosure exhibits ambient of upto 104 C (initial ambient is 50 C).

1.) What are the various sources of heat (as of now, we know I^2*R for copper busbars)?

2.)How is the enclosure ambient absorbing heat (through convection or radiation)?

3.) How does one analyse accurately, the heat transfer mechanism?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Convection inside electrical enclosure

10/31/2012 5:42 AM

A1) Check all connections inside the enclosure are "clean, tight and bright". Otherwise insulation materials are going to degenerate.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#2

Re: Convection inside electrical enclosure

10/31/2012 8:10 AM

1) Anything hotter than the surrounding environment.

2) Yes, and conduction.

3) Measure it accurately.

Register to Reply
2
Guru

Join Date: Dec 2008
Location: Cd. Juarez, Chihuahua, Mexico.
Posts: 1023
Good Answers: 69
#3

Re: Convection inside electrical enclosure

10/31/2012 8:47 AM

I have seen heat build-up, false contacts, charred insulations, breakers tripping and loss of one phase, all due to poor tightening; this causes carbon deposits and makes copper less conductive, requiring a good scrap and clean or even cut off and strip to remake the conection.

Take out the back plane, start checking joint screws' torque, right from the incomming busbars, all the way to the last circuit breaker in your box.

Use a clamp-on Amp. meter to make sure you're not exceding the rated current for each wire gauge in your panel.

__________________
No hay conocimiento ni herramienta que sustituya al sentido comun.
Register to Reply Good Answer (Score 2)
Guru

Join Date: Dec 2005
Posts: 1602
Good Answers: 19
#4

Re: Convection Inside Electrical Enclosure

10/31/2012 11:22 PM

Besides the numerous CBs, what other devices in this panel have of cause a voltage drop? Any voltage drops (undersize conductors, loose terminals, resistors, etc.) will generate heat.

__________________
Eventually, one needs to realize that it is far less important to be the smartest person in the room than it is to sit next to that person and make friends.
Register to Reply Score 1 for Good Answer
Power-User

Join Date: Feb 2009
Posts: 176
Good Answers: 6
#5

Re: Convection Inside Electrical Enclosure

11/01/2012 2:04 AM

First thing I'd be doing is going to my box of meters & getting my non contact IR thermometer & finding out where the hot spot is to establish where the heat is being created. Once this has been identified take the appropriate action as the other posters have said.

Register to Reply Score 1 for Good Answer
Register to Reply 5 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

brettj1au (1); lyn (1); PWSlack (1); Ried (1); Yahlasit (1)