Drop Pump Load

10/31/2012 7:31 AM

Suppose a centrifugal pump is running on 70% electrical load. I want to drop this load upto 60% without changing the motor, flow rate and head.

Any suggestions please?

__________________
au.umair
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#1

Re: Drop pump load

10/31/2012 7:59 AM

Lower the specific gravity of the fluid being pumped.

Dropping the load, "upto 60% without changing the motor, flow rate and head" will be very difficult.

You can't get something for nothing.

Register to Reply Score 1 for Good Answer
Guru
Hobbies - Fishing - Old Salt Hobbies - CNC - New Member United States - US - Statue of Liberty - New Member

Join Date: Mar 2007
Location: Rosedale, Maryland USA
Posts: 5197
Good Answers: 266
#2

Re: Drop pump load

10/31/2012 8:40 AM

Bucket brigade to do the work you want to save on electrical load.

The 70% represents the work the motor is doing. Sort of like asking a race horse to run a race in the same time on half rations.

__________________
Life is not a journey to the grave with the intention of arriving in a pretty, pristine body but rather to come sliding in sideways, all used up and exclaiming, "Wow, what a ride!"
Register to Reply Score 1 for Good Answer
Guru
Hobbies - CNC - New Member Hobbies - DIY Welding - New Member Engineering Fields - Electromechanical Engineering - New Member

Join Date: Aug 2007
Posts: 23647
Good Answers: 420
#3
In reply to #2

Re: Drop pump load

10/31/2012 9:14 AM

I think it comes down to someone may have spec'd something wrong.

__________________
“ When people get what they want, they are often surprised when they get what they deserve " - James Wood
Register to Reply Off Topic (Score 4)
Guru

Join Date: Aug 2012
Posts: 1071
Good Answers: 92
#4

Re: Drop Pump Load

10/31/2012 1:53 PM

Change the pumped fluid to one with a specific gravity that is 6/7th of the original fluid. Or find a pump that is better suited to your requirements by the same amount and install it on your existing motor. As noted in previous posts, you can't get something for nothing.

Also note: unless this is just a mental exercise, the motor is likely not running at full efficiency at 70% load. If this is a typical operating parameter, you may find that replacing the motor with a high efficiency unit that is correctly sized will give you the same result- but that's a question for your pump supplier.

Register to Reply
Guru
Hobbies - CNC - New Member Hobbies - DIY Welding - New Member Engineering Fields - Electromechanical Engineering - New Member

Join Date: Aug 2007
Posts: 23647
Good Answers: 420
#5
In reply to #4

Re: Drop Pump Load

10/31/2012 2:02 PM

Change the pumped fluid to one with a specific gravity that is 6/7th of the original fluid.

Come on, you size the pump for the process, not design the process around the pump.

__________________
“ When people get what they want, they are often surprised when they get what they deserve " - James Wood
Register to Reply
Guru

Join Date: Aug 2012
Posts: 1071
Good Answers: 92
#8
In reply to #5

Re: Drop Pump Load

10/31/2012 2:15 PM

True, but that's not what was asked!

Register to Reply
Guru
Hobbies - CNC - New Member Hobbies - DIY Welding - New Member Engineering Fields - Electromechanical Engineering - New Member

Join Date: Aug 2007
Posts: 23647
Good Answers: 420
#9
In reply to #8

Re: Drop Pump Load

10/31/2012 2:21 PM

it was more of a statement than an answer.

As far as looking for a solution to the question from the op, it was a poor one as far as having an understanding of centrifugal pumps. Or actually electric motors for that matter.

Leaves one to speculate the budget is tight.

__________________
“ When people get what they want, they are often surprised when they get what they deserve " - James Wood
Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#6
In reply to #4

Re: Drop Pump Load

10/31/2012 2:07 PM

I think the OP is confused.

"I want to drop this load upto 60%". Reducing the SG by 6/7 will not help them realize their dream.

Register to Reply
Guru

Join Date: Aug 2012
Posts: 1071
Good Answers: 92
#7
In reply to #6

Re: Drop Pump Load

10/31/2012 2:14 PM

Very!!

(Actually, I didn't read the OP very well- I saw 60% load instead of reduction in load! But if they change from pumping somethin like mercury to acetone they might pull it off!)

Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#10
In reply to #7

Re: Drop Pump Load

10/31/2012 2:45 PM

Maybe they do want a 10% reduction in load, but I can't tell by the question.

I see this mentality a lot. Please tell me how to reduce costs/increase efficiency, without putting forth any effort, or money.

Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#11

Re: Drop Pump Load

10/31/2012 4:41 PM

What is "70% electrical load"?

Perhaps a different pump selection could operate closer to its best efficiency point (BEP) than the present one. Unfortunately, sufficient details were not given.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#12
In reply to #11

Re: Drop Pump Load

10/31/2012 4:50 PM

70% electrical load is too much.

The OP wants Froggy to plunk his magic twanger and make the electric bill go down.

Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#13

Re: Drop Pump Load

10/31/2012 5:08 PM

au.umair,

Do you know what the pump curve for your pump looks like?

I'll stop here, before the devil tempts me to ask the obvious question.

Register to Reply
Guru

Join Date: Dec 2005
Posts: 1602
Good Answers: 19
#14

Re: Drop Pump Load

10/31/2012 11:06 PM

Increase the efficiency of your impeller. A more efficient pump impeller will require less energy to move the same flow and head.

__________________
Eventually, one needs to realize that it is far less important to be the smartest person in the room than it is to sit next to that person and make friends.
Register to Reply
Guru
Hobbies - CNC - New Member Hobbies - DIY Welding - New Member Engineering Fields - Electromechanical Engineering - New Member

Join Date: Aug 2007
Posts: 23647
Good Answers: 420
#15

Re: Drop Pump Load

11/01/2012 8:10 AM

I do not believe you have a viable solution here.

__________________
“ When people get what they want, they are often surprised when they get what they deserve " - James Wood
Register to Reply
Guru

Join Date: Dec 2005
Posts: 1602
Good Answers: 19
#16
In reply to #15

Re: Drop Pump Load

11/01/2012 9:19 AM

I'm not sure this is a viable question either.

However, on further thought, you are partly correct. Moving x amount of weight (flow) through y amount of distance (head) takes a minimum certain amount of work plus whatever friction or other inefficiencies exist in the process. If the pump has a low efficiency impeller and you replace it with a high efficiency impeller, the less energy will be lost in the process. However there is still that theoretic work definition that cannot be changed.

__________________
Eventually, one needs to realize that it is far less important to be the smartest person in the room than it is to sit next to that person and make friends.
Register to Reply Off Topic (Score 5)
Guru
Hobbies - CNC - New Member Hobbies - DIY Welding - New Member Engineering Fields - Electromechanical Engineering - New Member

Join Date: Aug 2007
Posts: 23647
Good Answers: 420
#17
In reply to #16

Re: Drop Pump Load

11/01/2012 9:33 AM

I agree,

I like challenges but everything here is too vague.

__________________
“ When people get what they want, they are often surprised when they get what they deserve " - James Wood
Register to Reply Off Topic (Score 5)
Guru

Join Date: Aug 2012
Posts: 1071
Good Answers: 92
#18
In reply to #17

Re: Drop Pump Load

11/01/2012 10:03 AM

Well, if you want a challenge try nailing down this specific from the OP:

  1. the OP is running the motor pump combination at 70% electrical load
  2. the OP wants to reduce this by "up to 60%"
  3. this new load would equal a minimum running draw of 28% (40% of 70%)
  4. Now throw in an assumption- regardless of actually pumping anything, lets say the motor is a standard AC induction motor operating at nameplate speed and line voltage without any form of controller, and is only experiencing operating losses of the motor and the pump
  5. In my experience, a free running motor is going to draw at least 30% plus losses in the pump or other drivetrain item!! Where do you go from here??
Register to Reply Off Topic (Score 4)
Guru
Hobbies - CNC - New Member Hobbies - DIY Welding - New Member Engineering Fields - Electromechanical Engineering - New Member

Join Date: Aug 2007
Posts: 23647
Good Answers: 420
#20
In reply to #18

Re: Drop Pump Load

11/01/2012 1:01 PM

ha, you forgot #6 not to change the motor or pump?

Now where did I put my magic wand?

__________________
“ When people get what they want, they are often surprised when they get what they deserve " - James Wood
Register to Reply Off Topic (Score 5)
Power-User

Join Date: Feb 2010
Posts: 103
Good Answers: 2
#19

Re: Drop Pump Load

11/01/2012 10:52 AM

Simple...just magically change the eficiency oif the pump at that specific point of its perfprmance curve. Otherwise slow the pump or start closing the discharge valve. Watch hte amp meter until you get to the desired 60% electrical load.

I'm not being sarcastic, merely silly.

The painful truth of the matter is if using the same pump either the head must be increased or the speed reduced, both of which will reduce the GPM and the BHP. The other choice is rep;acing the pump and motor. Another choice is trimming the diameter of the pump's impeller...this will also reduce GPM ,head and BHP basically the same as replacing the pump but at a lower cost. The pump manufacturer can give you guidance in this process.

Good luck...Lou Bindner

Register to Reply
Register to Reply 20 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

JNB (4); Lou Bindner (1); lyn (5); ozzb (1); phoenix911 (6); Ried (2); Tornado (1)