Dear All,
I am currently deciding on buying some cables for my instruments.
I would like to check for twisted pair type of cables, do these cables some with a shield wire?
Or only triad cables come with shield wire?
How do we wire this shield wire? Do we wire the shield wire to ground?
There is no limit towards how much one can learn.
Re: How to choose Instrument Cables for my cables
11/02/2012 4:14 AM
A1) Yes.
A2) Not applicable
A3) Best practice: connect the shield to a clean instrument earth bar at the panel end only.
Good Answers: 125
11/02/2012 9:27 AM
1. Yep
2. Yep
3. Yep
GA
Re: How to Choose Instrument Cables for My Cables
11/02/2012 10:55 AM
We have used cables such as these many times on our process skids where I work. Examples are Belden 1032A which is a true twisted pair with a drain wire under the shield for easy connection or Lutze A3091802 which is a pair but not twisted, also with a drain wire for connecting the shield to ground. both are AWG 18 which is a good size for instrumentation as long as you are not trying to run thousands of meters. I am not promoting these manufacturers. Many other manufacuters also make these cables. The references will give you a cross over number to choose a similar cable from your chosen manufacturer.
11/02/2012 7:05 PM
11/03/2012 12:52 AM
Twisted pair wires with a shield are available. If your instruments have a guard, then the shield should be tied to guard. If no guard or ground, then tie it to low. A ground should be used on one end only to avoid a ground loop. Typically the shield should be tied to guard and ground on the AC source if using one. The best book I have seen on this subject is Noise Reduction Techniques in Electronic Systems by Henry W. Ott.
11/03/2012 9:50 PM
I Agree with StandardsGuy Reference with Henry Ott's Book "Noise Reduction Techniques in Electonic Circuits", as being one of the Best References on this Subject. Another Book would be "Measurement Engineering: Basic Principles Volume I" By Peter K. Stein. There are also "Smith Charts" that can be extremely usefull.
This entire Subject Area, to me "Is an Art & a Science". I have been playing in this area for 40 years & I still discover unique situations/criteria.
I look at certain chacteristics such as Analog or Digital, Voltage, Current & Especially Frequency, along with the Input/Output Impedances. I believe that Low Level Low Frequency Analog (ie LLLFA) is the "Trickiest". This is the Most Senitive Scenario for "Gound Loops" with their Instability & Measurement Errors, but Cable Capacitance is Very Important & Must be "Balanced" in Certain Situations (ie C-BAL).