Transformer Outgoing Cable Getting Heated Up

11/25/2012 10:43 PM

6.6KV/415 V transformer having LT side CU 5CX400 sqmm armoured cable for each phase connected with LT breaker. During full plant load the current is having 1400A. After 2/3 hrs running one of the B phase cable getiing to 105 deg C at breaker end gland whereas other 14 cables gland is around 45 deg C. We have done armour earthing at transformer end. still the problem is there. Please help.

Register to Reply
Pathfinder Tags: cable glanding cable heating
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
4
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#1

Re: Transformer Outgoing Cable Getting Heated Up

11/25/2012 11:17 PM

Sounds like a poor connection to me. An infrared image will discern where the excess heat is being generated.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply Good Answer (Score 4)
Guru

Join Date: Oct 2012
Location: 100 miles North from the World Center
Posts: 879
Good Answers: 42
#2

Re: Transformer Outgoing Cable Getting Heated Up

11/25/2012 11:59 PM

The source of heating could be:- the cable lug-the contact with the breaker terminal or the contact between conductor and the lug [not well crimped or short or else],

-the metallic gland is not split and the magnetic field generated by current will heat the gland,

-the armor is, accidentally, once more grounded not far from the end.

__________________
Julius
Register to Reply
Guru

Join Date: Oct 2007
Location: India
Posts: 1246
Good Answers: 34
#3

Re: Transformer Outgoing Cable Getting Heated Up

11/26/2012 12:03 AM

Measure current load on each phase, in-coming & out-going cables. If Amps are balanced, check for corroded/loose/arcing on the joints of offending phase cable.

Register to Reply
Active Contributor

Join Date: Apr 2011
Location: Jamshedpur, India
Posts: 17
#4

Re: Transformer Outgoing Cable Getting Heated Up

11/26/2012 12:15 AM

just to clarify , the heating observed not in the socket terminal connection at breaker.

It is observed at the cable entry gland of the cubicle.

Register to Reply
Guru

Join Date: Oct 2007
Location: India
Posts: 1246
Good Answers: 34
#5
In reply to #4

Re: Transformer Outgoing Cable Getting Heated Up

11/26/2012 12:22 AM

Has the cable entry gland of the cubicle, shorted inadvertently with the cable screen?

Register to Reply
Active Contributor

Join Date: Apr 2011
Location: Jamshedpur, India
Posts: 17
#6
In reply to #5

Re: Transformer Outgoing Cable Getting Heated Up

11/26/2012 12:38 AM

yes. cable glanding done as per norms.

Register to Reply
Guru

Join Date: Oct 2007
Location: India
Posts: 1246
Good Answers: 34
#7
In reply to #6

Re: Transformer Outgoing Cable Getting Heated Up

11/26/2012 12:44 AM

What I meant was whether there is a short circuit between cable screen & metallic part of the gland? Is there any current flow between cable gland & cable screen?

Register to Reply
Active Contributor

Join Date: Apr 2011
Location: Jamshedpur, India
Posts: 17
#8

Re: Transformer Outgoing Cable Getting Heated Up

11/26/2012 5:57 AM

definitely cable gland check nut is through the armour only. and i've measured the current flowing in the transformer side armour earthing around 1.5 A.

Register to Reply
Guru

Join Date: Oct 2007
Location: India
Posts: 1246
Good Answers: 34
#9
In reply to #8

Re: Transformer Outgoing Cable Getting Heated Up

11/26/2012 6:08 AM

How much Amps, if any, flowing at the gland nut & armour joint? Some current is flowing there, otherwise it would not get so hot. Will it?

Register to Reply
Guru

Join Date: Oct 2012
Location: 100 miles North from the World Center
Posts: 879
Good Answers: 42
#10

Re: Transformer Outgoing Cable Getting Heated Up

11/26/2012 6:18 AM

First of all, the LT side of the transformer does it not mean the "low voltage side"?

So why the cable is with screen provided?

Second, if there are 5*1/c 400 sqr.mm cables that means 2 cables per phase. It could be a strong unbalance between currents depending on the laying configuration.

I agree with Joshi: you have to check the current distribution between cables.

If the cable armor is exposed it could touch the metallic gland-if it the gland of the opposite end to transformer end.

__________________
Julius
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#11

Re: Transformer Outgoing Cable Getting Heated Up

11/26/2012 6:49 AM

"Earth/ground loops".

Make sure each earthed/grounded conductor is only connected to earth/ground at one end.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
4
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#12

Re: Transformer Outgoing Cable Getting Heated Up

11/26/2012 8:08 AM

What I suppose is you have connected all the five cores of a 5c x 400 sq.mm cable 1 to R phase, all the 5 cores of the 5c x 400 sq.mm cable-2 to Y phase and all the 5 cores of the 5c x 400 sq.mm cable-3 to B phase. If so, I am not surprised at the gland. This is becuase of the circulating currents in the cable armour due to induced emf from the stray flux. Advised is to divide the cores of each cable to R, Y, B, N & E/G. (i.e.) R of Cable-1, R of cable-2 & R of cable-3 should be connected to R terminal of the trafo & at the CB. Simlarly, Y1, Y2 & Y3 to Y, B1, B2 & B3 to B, Bl 1, Bl 2 & Bl 3 to Neutral, G1, G2 & G3 to E/G Terminal.

If such distribution is not possible, perhaps owing to the small termination space, you may still continue as you have done at present but replace the gland plates with non-magnetic plates. Your problem would be solved.

Register to Reply Good Answer (Score 4)
Member

Join Date: Nov 2012
Location: Pune, India.
Posts: 5
#13

Re: Transformer Outgoing Cable Getting Heated Up

11/26/2012 1:14 PM

There may be major possibility of unbalanced current and may reason of poor lugging at breaker end .

Register to Reply
Guru
Australia - Member - New Member

Join Date: Feb 2008
Location: Australia
Posts: 2181
Good Answers: 255
#14

Re: Transformer Outgoing Cable Getting Heated Up

11/26/2012 3:47 PM

I don't discount earth loops, but suggest that since all 14 other cores are consistent the issue is specific to that connection.

You seem to have done checks on all the external connections to eliminate that source, but is it possible that the poor connection/termination is inside the enclosure on that specific connection and heat is being conducted and becoming apparent at the gland.

__________________
Just an Engineer from the land down under.
Register to Reply
Guru

Join Date: Jun 2007
Location: chennai,India
Posts: 592
Good Answers: 19
#15

Re: Transformer Outgoing Cable Getting Heated Up

11/26/2012 10:53 PM

Gland plate material is it magnetic or non magnetic ?

__________________
Ramesh,Freelance Electrical/automation Consultant
Register to Reply
Active Contributor

Join Date: Apr 2011
Location: Jamshedpur, India
Posts: 17
#16

Re: Transformer Outgoing Cable Getting Heated Up

11/28/2012 1:48 AM

one more clarification: there is 15 run of 400 sqmm cable from trafo low voltage side to breaker

Register to Reply
Guru

Join Date: Oct 2012
Location: 100 miles North from the World Center
Posts: 879
Good Answers: 42
#17
In reply to #16

Re: Transformer Outgoing Cable Getting Heated Up

11/28/2012 3:17 AM

Thank you. My mistake.

__________________
Julius
Register to Reply
Active Contributor

Join Date: Apr 2011
Location: Jamshedpur, India
Posts: 17
#18

Re: Transformer Outgoing Cable Getting Heated Up

12/06/2012 11:23 PM

few days back i solved the problem. I want to share with you for ur remarks if any.

i did the following:

a) trefoil arrangement of cables done (earlier it was R phase through one tray, Y-phase and B-phase in similar maner through individual trays. This may result into voltage formation in the armour and result into week gland heating in one cable)

b)LT breaker pane in coming cable glad plate made non magnetic with firm grounding(earlier it was grounded also)

c) grounding pit resistance improve from 5 ohm to 1.1 ohm(combined)

d)chicken mesh provided at the back of the LT cable entry panel in breake cubicle.

on giving 1400 amps load in this bus found the gland temperature was max 43 deg in the same place after 6 hrs of running. till date it is the same.

hope i have taken correct measures.

Register to Reply
Guru

Join Date: Oct 2007
Location: India
Posts: 1246
Good Answers: 34
#19
In reply to #18

Re: Transformer Outgoing Cable Getting Heated Up

12/07/2012 7:49 AM

Congratulations, sostoall, well done.

Register to Reply
Commentator

Join Date: Apr 2012
Location: Sanskrit
Posts: 57
#20

Re: Transformer Outgoing Cable Getting Heated Up

03/16/2013 11:07 AM

How do i determine the maximum current which the station transformer can produce ??

say in a substation we have a station transformer which is being used to fed the Main switch Board from there the supply thus received will be given to all the control panels , Battery charger , lighting Panel , and the AC motor in the circuit breaker as well as the 3 phase Motor in the OLTC , AC System , control room fans , and so on ..

Now i have to varify by making necessary calculations that the Bus bar Ampere rating in the Main Switch Board is okey , So please guide me on this ?

I am trying to learn these designing calculations and hence know about the designing calculations

Register to Reply Off Topic (Score 5)
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#21
In reply to #20

Re: Transformer Outgoing Cable Getting Heated Up

03/16/2013 11:26 AM

Contact the transformer manufacturer. They have all the pertinent information.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply Off Topic (Score 5)
Register to Reply 21 comments

Good Answers:

These comments received enough positive votes to make them "good answers".
Copy to Clipboard

Users who posted comments:

7anoter4 (3); electricalexpert65 (1); Joshi (5); Just an Engineer (1); Madhav jindamwar (1); minggrabber (1); PWSlack (1); ramvinod (1); redfred (2); sostoall (5)

Previous in Forum: How to Check Diesel Generators Sensors   Next in Forum: Electro Magnets

Advertisement