Flowmeter Electromagnetic Siemens Mag3100

11/26/2012 1:27 AM

good morning everyone ,

kindly i need some clarifications about the earthing for the the electromagnetic flow meter type Siemens ,is it important to connect earthing cable from the both flanges side ,or connect one flange side only enough ? kindly advice .

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru

Join Date: Oct 2007
Location: India
Posts: 1246
Good Answers: 34
#1

Re: Flowmeter Electromagnetic Siemens Mag3100

11/26/2012 1:41 AM

Your electromagnetic flow meter is made by Siemens. What is the model/type no? What does the installation instruction say about grounding? I suppose you are installing/commissioning this instrument. Have you sought support from Siemens?

Register to Reply
Guru

Join Date: Oct 2007
Location: India
Posts: 1246
Good Answers: 34
#2
In reply to #1

Re: Flowmeter Electromagnetic Siemens Mag3100

11/26/2012 2:39 AM

Please visit https://eb.automation.siemens.com/goos/catalog/Pages/ProductData.aspx?language=en&nodeid=10061921&tree=CatalogTree&regionUrl=/#topAnch&activetab=product&

and download the manual. It gives all installation instructions, including methods for required grounding. How come you do not have a manual? Or you do not understand the grounding methods described there-in? Please revert back with the results.

Register to Reply
Active Contributor

Join Date: May 2011
Posts: 17
#3
In reply to #2

Re: Flowmeter Electromagnetic Siemens Mag3100

11/26/2012 2:58 AM

yes sure am have the manual the problem here that my manager need to fix from both side not one flange side as the manual and so i need support with field experience to help

thanks

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#4
In reply to #3

Re: Flowmeter Electromagnetic Siemens Mag3100

11/26/2012 3:24 AM

OK, so read the manual and telephone the Siemens technical support line if anything is unclear.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Oct 2007
Location: India
Posts: 1246
Good Answers: 34
#5
In reply to #3

Re: Flowmeter Electromagnetic Siemens Mag3100

11/26/2012 3:36 AM

Show the manual to your Manager, or make him speak to & confirm with Siemens. Read carefully, the entire manual. Highlight the text relating to grounding.

Register to Reply
Commentator

Join Date: Oct 2009
Posts: 60
#6

Re: Flowmeter Electromagnetic Siemens Mag3100

11/29/2012 3:06 PM

Many of these Siemens mag meters do not require separate earthling as they have earthling electrodes. If you see 3 electrodes in the tube then the one 90 degrees out from the other two is the earthling electrode.

If you only have two electrodes then you need an earthling ring and it is best to put it at the inlet side of the sensor.

If flow goes both ways then use two rings.

Hope this helped.

Cheers,

Eric

Register to Reply
Register to Reply 6 comments
Copy to Clipboard

Users who posted comments:

Ahmadnaggar (1); Ducdude (1); Joshi (3); PWSlack (1)