How To Connect 3 Phase Transformer in 2 Phase Line

12/01/2012 2:21 AM

i have 3 phase 25 kva transformer but there is two phase line so howcan i connect it into 2 phase line?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#1

Re: 3 phase trans former how to connect in 2 phase line

12/01/2012 2:41 AM

You can't.

Register to Reply Score 1 for Good Answer
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#2

Re: 3 phase trans former how to connect in 2 phase line

12/01/2012 3:14 AM

Terminology may vary around the world for "line" vs. "phase". For illustration, one might have a 415Δ/240Y transformer with lines/phases ABC and neutral N. For a single-phase 415-volt circuit, you would connect to A and B, B and C, or C and A. (Even though two lines/phases are connected, the waveform is still only single-phase.) For a single-phase 240-volt circuit, you would connect to A and N, B and N, or C and N.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru

Join Date: Feb 2011
Posts: 7025
Good Answers: 207
#3

Re: 3 phase trans former how to connect in 2 phase line

12/01/2012 7:02 AM

you just scared me

Register to Reply Score 1 for Good Answer
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#4

Re: 3 phase trans former how to connect in 2 phase line

12/01/2012 9:44 AM

True two phase power distribution with a 90° phase difference is not done any more. What you probably have is more accurately called a split phase where the power lines are 180° different.

To make a split phase power into three phase requires more than just a transformer. A three phase motor driver circuit will work. A split phase motor connected to a three phase generator is also done. It is also the easiest to understand.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#6
In reply to #4

Re: 3 phase trans former how to connect in 2 phase line

12/01/2012 11:38 AM

The semantics of the term "2-phase".

When i worked at Siemens, it took me a while to figure out this semantics issue, until i sat down with some German counterparts and talked about it.

Outside of North America, they have never heard of true 2-phase power, other than maybe EEs in class. When they use the term "2-phase", they are meaning 2-out-of-3 phases, what we call single phase. For them, "single phase" ALWAYS means phase to neutral.

The only place this gets confusing is in international discussions, like this one. What he meant was that he has a 3 phase transformer but only has 2 lines of his location's 3 phase system to feed to it. He wants to know if there is a way to use that 3 phase transformer as a single phase transformer, and the answer is no.

But as Tornado was pointing out, it may be unnecessary, albeit we do not know what voltage he is trying to attain with the transformer, or if he has a neutral available. Far too little information given to get a meaningful suggestion from afar.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply Score 1 for Good Answer
Guru
Engineering Fields - Instrumentation Engineering - EE from the the Wilds of Pa.

Join Date: Feb 2006
Location: middle of nowhere, Pennsylvania
Posts: 2603
Good Answers: 63
#9
In reply to #6

Re: 3 phase trans former how to connect in 2 phase line

12/03/2012 11:24 AM

Just to be sure - ALL 230 volt service in the continental USA is really 2 phase - correct? No Euro style single phase anywhere?

I have a mixer control panel at the plant that was built in Europe. The tank it goes on is shipping to Louisianna. I have insisted we remove the single fuse/neutral terminal block system in the control panel and install 2 pole fuses for the power circuits before we ship this, as the wiring on one phase would technically have no protection, other than the protection on the plant incoming power, which would be too large for the wires used.

__________________
Remember when reading my post: (-1)^½ m (2)^½
Register to Reply Off Topic (Score 7)
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#10
In reply to #9

Re: 3 phase trans former how to connect in 2 phase line

12/03/2012 3:32 PM

God help you if that was ever to come up at a European accident inquiry. You'd be hung out to dry.

__________________
The reports of my death are greatly exaggerated.
Register to Reply Off Topic (Score 5)
Member

Join Date: Nov 2012
Location: Pune, India.
Posts: 5
#5

Re: 3 phase trans former how to connect in 2 phase line

12/01/2012 11:20 AM

It is not possible..........

Register to Reply Score 1 for Good Answer
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#7

Re: How To Connect 3 Phase Transformer in 2 Phase Line

12/02/2012 12:14 PM

Actually the answer is "...it depends..." We really don't have enough information from the OP to give a definitive answer, and as Jraef has said, semantics gets in the way. Nor has the OP provided any info about voltages, ratings, windings, loading, or intended use.

However, if the voltages are consistent with his supply system, its configuration, and the windings of the transformer can be separated in to six separate leads, then it would be possible to use one pair of HV/LV leads to use the transformer as a single phase unit.

There's also nothing inherently "wrong" with wiring across one phase to ground on both sides of a grounded wye transformer attached to a grounded wye system and hanging a single phase load on it; after all a three phase transformer is "just" three single phase transformers sharing a common core.

But if the OP expects to get the full rating or three phase power out of it then "no" is the answer.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#8

Re: How To Connect 3 Phase Transformer in 2 Phase Line

12/02/2012 8:01 PM

You can't do it with a conventional transformer.

The Scott transformer.

__________________
The reports of my death are greatly exaggerated.
Register to Reply Score 1 for Good Answer
Register to Reply 10 comments

"Almost" Good Answers: