Conductors for Inverse Duty Motors

12/12/2012 11:29 AM

What's the difference in conductor type between a vfd and an inverse duty motor vs. a conventional motor

Register to Reply
Pathfinder Tags: inverse duty motors
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#1

Re: Conductors for Inverse Duty Motors

12/12/2012 11:35 AM

It's inverter duty, not inverse duty. Please try to get the terms correct.

General Purpose vs Inverter Duty - Motors from AutomationDirect

A search revealed millions of answers, given the right information.

Conductors conduct electricity, regardless of the motor type.

I hope this wasn't homework, or an interview question.

Register to Reply Score 1 for Good Answer
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#2

Re: Conductors for Inverse Duty Motors

12/12/2012 11:39 AM

Given the spelling correction above is meaningful, then as far as British Standard 7671 is concerned, none whatsoever.

Ask a competent electrician as well. The answer will be the same.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#3

Re: Conductors for Inverse Duty Motors

12/12/2012 11:49 AM

Would converting a motor into a generator be considered an inverse duty motor?

I agree that this is likely about an inverter duty motor and that the conductors will be identical.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
3
Guru

Join Date: Dec 2008
Location: Cd. Juarez, Chihuahua, Mexico.
Posts: 1023
Good Answers: 69
#4

Re: Conductors for Inverse Duty Motors

12/12/2012 1:43 PM

Hello IMS;

All in this thread agree that conductors between the two types of motors are basically the same; however, there is a substantial diference in the insulation of such conductors (propperly called magnet wire), the standard duty motor receives a sine wave of a very low frequency, 50 or 60 hertz tipically, while the inverter duty motor is subject to high frequency voltage pikes, due to the carrier frequency that the drive uses to generate the PWM from its power IGBTs (all this is just to have the equivalent to a variable frequency applied to the motor).

This stresses the insulation of the magnet wire to the point that it will fail prematurely, if it is not rated for inverter duty. A standard magnet wire shows the copper color thru the varnish, but an inverter duty wire of the same caliber exhibits a solid color (commonly brown) and feels much stiffer than a standard wire, it is shiny, slippery and not easy to peel off.

__________________
No hay conocimiento ni herramienta que sustituya al sentido comun.
Register to Reply Good Answer (Score 3)
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#5
In reply to #4

Re: Conductors for Inverse Duty Motors

12/12/2012 1:54 PM

Interesting point!

I was considering the conductors between source and motor, not the motor windings. You're quite correct that the OP did not clearly specify which conductors should be considered.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Guru

Join Date: Feb 2011
Location: Atlanta, GA
Posts: 1053
Good Answers: 110
#6
In reply to #5

Re: Conductors for Inverse Duty Motors

12/12/2012 6:42 PM

... although the OP does say "between a vfd and an inverse duty motor" which at least suggests he is talking about the conductors between the drive and the motor. Of course, he might also be using the idiomatic "difference between."

I'd say that an inverse duty motor is a motor that becomes less prone to failure the more you abuse it. (The human analogy would be a masochist.) Or perhaps it is a motor that runs cooler with greater load.

__________________
Think big. Drive small.
Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#7
In reply to #5

Re: Conductors for Inverse Duty Motors

12/12/2012 6:51 PM

I'd say that the OP would be one of less than 63 people on the planet who would ever refer to motor winding as motor conductors.

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#13
In reply to #4

Re: Conductors for Inverse Duty Motors

12/13/2012 3:26 AM

Not in CE-marked inverters.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Oct 2006
Location: 44.56024"N 15.307971E
Posts: 8277
Good Answers: 270
#14
In reply to #13

Re: Conductors for Inverse Duty Motors

12/13/2012 3:43 AM

To my knowledge, an inverter cannot carry a CE marking.Only an approved motor-inverter pair can be marked CE.

Or has my knowledge data base been obsoleted since my retirement?

__________________
"A man never stands so tall as when he stoops to help a child." "Never argue with a stupid person.They will drag you down to their level and beat you with experience" "To create an apple pie from scratch, first you must create a universe"
Register to Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#16
In reply to #14

Re: Conductors for Inverse Duty Motors

12/13/2012 9:10 AM

CE marking just indicates that the manufacturer claims the product meets European safety standards. CE marking does not come from an independent lab. A Nationally Recognized Testing Laboratory (NRTL) verifies that the whole package design has been safely designed. NRTL certification does not test the overall quality of a design. It only certifies that when this design fails it will likely fail in a safe manner if it is not tampered.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#17
In reply to #16

Re: Conductors for Inverse Duty Motors

12/13/2012 9:23 AM

That's correct. Self certification is the cheap way out.

It's smarter to combine CE marking with tests though.

Been through the process before with a noise cancelling headset design. We had Underwriters Lab. test/certify our stuff. Orbital Sciences also did some certification for us. Then we affixed the CE mark.

If one wants to market the product globally, the CE mark is essential. (Unfortunately, as redfred pointed out, testing is not necessarily required)

Register to Reply
Power-User

Join Date: Jan 2009
Posts: 250
Good Answers: 7
#15
In reply to #13

Re: Conductors for Inverse Duty Motors

12/13/2012 5:28 AM

"Not in CE-marked inverters."

Would you please explain this?

Register to Reply
3
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#8

Re: Conductors for Inverse Duty Motors

12/12/2012 10:19 PM

Actually OP's use of conductor is probably the best choice. As English-speakers we don't realize how idiomatic our native language is, i.e., "windings" could refer to how the "conductors" are placed in the slot, etc.

Getting back to the question, here's an interesting piece from of all places the US Dept. of Energy:

https://www1.eere.energy.gov/manufacturing/tech_deployment/pdfs/motor_tip_sheet14.pdf

"...Inverter-duty motors are wound with voltage spike-resistant, inverter-grade magnet wire to minimize adverse effects of ASD (Adjustable Speed Drive)-produced waveforms. Improved insulation systems do not degrade as readily when subjected to transient voltage spikes. A greater thickness or build-up of premium varnish (through multiple dips and bakes) minimizes the potential for internal voids, and a lower heat rise design results in improved resistance to voltage stresses..."

Guess what, the conductor from the drive to the motor can make a difference also:

"...When the motor impedance is larger than the conductor cable impedance, the voltage wave form will reflect at the motor terminals, creating a standing wave (see Figure 1). Longer motor cables favor the formation of higher amplitude standing waves. Voltage spikes have been reported with peak values as high as 2150 volts in a 460 V system operating at 10% overvoltage..."

Live and learn....

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply Good Answer (Score 3)
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#9
In reply to #8

Re: Conductors for Inverse Duty Motors

12/12/2012 10:43 PM

GA

Register to Reply
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#10
In reply to #9

Re: Conductors for Inverse Duty Motors

12/12/2012 10:52 PM

Lyn, thanks for the GA. I wonder if this may be the "root cause" of many of the "Help, my VFD driven motor just failed" postings.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#11
In reply to #8

Re: Conductors for Inverse Duty Motors

12/12/2012 11:49 PM

I wonder if motor wiring failures have occurred because of this. I haven't heard of any, but it might not be surprising. Maybe some day codes will require VFD-powered motors to be fed with wire of 2x or 3x the usual voltage rating.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru

Join Date: Oct 2006
Location: 44.56024"N 15.307971E
Posts: 8277
Good Answers: 270
#12

Re: Conductors for Inverse Duty Motors

12/13/2012 2:12 AM

Yes,there is a difference in insulation of the motor and leads,but there are other differences in the design of a VFD motor.You cannot expect good service life from a standard motor used in a VFD mode.The ball bearings and races and retainers in a VFD motor are designed to dissipate induced eddy currents in the rotor due to high frequency harmonics.Without this design, ball bearings will pit and fail prematurely.There are grounding rings made for retrofitting standard motors to properly ground the shafts and bearings, but this is only one facet of the problems encountered.

The harmonics can also induce currents in nearby conductors and equipment if not properly shielded.This can cause havoc in sensitive controllers, like elevators,etc.

So before you retrofit an existing motor to VFD,hire a qualified electrical engineer to review the application and analyse the site for potential problems.

Good Luck!

__________________
"A man never stands so tall as when he stoops to help a child." "Never argue with a stupid person.They will drag you down to their level and beat you with experience" "To create an apple pie from scratch, first you must create a universe"
Register to Reply
Guru

Join Date: Jul 2006
Location: Eastern Kansas USA
Posts: 1503
Good Answers: 128
#18

Re: Conductors for Inverse Duty Motors

12/13/2012 7:58 PM

Friends,

  • Valid answers regarding the difference in magnet wire for the motor windings.
  • valid point regarding the reflection of the voltage waveform at the point where there is the significant impedance difference between the conductors to the motor and the internal motor winding conductors.
  • valid point regarding the creation of induced noise on nearby conductors in a plant.
  • My reading and study generally states that the conductor damage from the impedance change is within the first few turns of the motor winding, and not in the conductors leading to the motor.
  • My study decades ago on pulse waveforms and standing waves was that the upper limit of the voltage was a doubling, so I am surprised to hear of 2160V on a 480V system. Allowing for 480x2x1.414=1360v. Perhaps someone can double-check this point.
  • All the drive manufacturers I have dealt with recommend shielded/screened cables for the conductors going out to the motor and will only certify the installation if the motor's grounding(earthing) conductor is connected to the grounding/earthing terminal in the drive, with the drive then being bonded.
  • The voltage spikes and related problems are lower with the most recent drive models, but line and load reactors are usually a good idea and are strongly desired if the motor conductors are near the limits of the recommended lengths.

--John M.

Register to Reply
Register to Reply 18 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

HiTekRedNek (2); jmueller (1); K_Fry (1); lyn (4); PWSlack (2); RAMConsult (2); redfred (3); Snel (1); Tornado (1); Yahlasit (1)