Rating Selection Criterion of GT, UAT and ST

12/27/2012 2:24 PM

We have a coal based thermal power plant of 2x600 MW, generator for each unit tech details r 600 MW, 0.85pf,706 MVA,20 kV,H2 cooled 0.5 Mpa, Brushless Excitation; IPB of 25 kA to GT (20/420 kV); Tapping IPB to 2 UATs (20/11.5 KV) r 1250 A. There is no GCB only HVCB used for connecting to the 420 kV grid. Mines query which is nagging me a lot: how would one reach to the rating of Generator transformer and unit auxiliary transformer. For UAT if one knows the auxiliary(unit bus' load) then what others r the parameter governing its final selection apart from (1) auxilary bus load (2) continuous, running, standby motor/other load from load profile (3) highest rated motor inrush current requirement from load sequence (4) voltage regulation/voltage drop during 3. parameter

I usually do above procedure for the normal power/distribution transformers but GT, ST (station transformer) and UAT are some special transformers and I don't know how to size them especially when the grid has come into picture. IEEE Std C57.116-1989 puts some light on these but beyond the GTs approx MVA rating selection I'm at sea, I'm unable to take into a/c of GTs other vitals: Z,tap-setting/range,VAR requirements,xmer ratio as per IEEE, as it keeps on stressing graph plotting..... similarly i heard that SC criterion is also a dominant factor for UAT selection. Similarly I don't have a clue for ST. IEC/other stdds don't shed much light on rating selection, so I seek your valuable experience and suggestion from you.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Oct 2007
Location: India
Posts: 1246
Good Answers: 34
#1

Re: Rating Selection Criterion of GT, UAT and ST

12/27/2012 11:09 PM

Get the services of a competent electrical engineer locally. No CR4 members IMHO can see/visualise all your sorrow & do justice to your OP.

Register to Reply Score 1 for Good Answer
Guru

Join Date: Oct 2012
Location: 100 miles North from the World Center
Posts: 879
Good Answers: 42
#2

Re: Rating Selection Criterion of GT, UAT and ST

12/28/2012 1:22 AM

As Joshi already said it is a serious problem and only a specialized team with sufficient

experience can appreciate all these data.

You have to state the general scheme at 400 kV[H scheme,1 1/2 and so on] and state the medium voltage for Boiler Feed Water Pump motor and for Force Draft and Induce Draft Fan motors and other auxiliary-and so to state the UAT and ST necessary power. It is important to state also the starting mode-D.O.L. or VSD- for instance- and calculate the limited voltage drop. If you intend-for black start-to employ a Gas Turbine included a Diesel Generator it could be another problem. Other auxiliary facilities as Ash Handling, Coal Handling, and Desulphurizing Plant and so on could change the ST power level.

So, for an inexperienced engineer this is an exercise only.

__________________
Julius
Register to Reply
Member

Join Date: Dec 2012
Posts: 5
#3

Re: Rating Selection Criterion of GT, UAT and ST

12/28/2012 1:06 PM

thanx for urs replies and i'll see how to find an experienced person/team...as per 7anoter4 420 kV switchyard scheme is: 2 Bus and Transfer Bus scheme (2000A, 1000A respectively;40 kA) 11 Bays in total: 2 for GTs, 2 For STs, 4 lines, 1 Buscoupler, 1 Transfer coupler and 1 Spare. For motors BFP rating is 9.5 MW,11 kV,562/4.5 In; 2x4.2 MW,11 kV,266/5.9 ID Fans fed from unit bus; 2x3.65 MW,11 kV 217/6In PA fans fed from unit bus; 2x1.4 MW,3.3 kV,289/5.5In FD Fans again fed from unit bus; 4x2.150 MW,11 kV CW pumps and CHP switchgears all fed from Station bus... all the aforementioned motors r DOL started....i'd like to say that right now i don've any load list of unit n station buses n in absence of that i can't approximate the load sum of buses.

But given said that, hypothetically if i've unit bus load and station bus load then how can i reach to GT rating, i again guess that with unit bus n station bus loads one would be able to select UAT n ST rating...if i'm wrong then please correct me if u can spare the time on mines post

Register to Reply
Guru

Join Date: Oct 2012
Location: 100 miles North from the World Center
Posts: 879
Good Answers: 42
#4
In reply to #3

Re: Rating Selection Criterion of GT, UAT and ST

12/29/2012 3:48 AM

I am sorry. I cannot design the Power Station. First of all there is not enough data. Second, it is a problem where are involved many engineering domains: electrical, mechanical, civil design and so on. As I already said a minimum of 10-15 engineers has to works a few weeks in order to produce a suitable one line diagram at 420 ,20,11 and 3.3 kV, a workable general lay-out and so on.At first glance only [my opinion only]:GT=700 MVA [17%]; UAT1+UAT2=20 MVA/11 KV +20 MVA/3.3 KV; ST=50 MVA [14%]You would need a Gas Turbine of 20 -30 MW and a DG of 2000 HP [at least].You will need [probably] a 5000 sqr.m for the main building and facilities. You have to check voltage drops,calculate the short-circuit currents, the load flow and so on.

__________________
Julius
Register to Reply
Member

Join Date: Dec 2012
Posts: 5
#5
In reply to #4

Re: Rating Selection Criterion of GT, UAT and ST

12/29/2012 11:01 AM

thank you for urs input, i'll keep in mind these vitals next time

Register to Reply Off Topic (Score 5)
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#6

Re: Rating Selection Criterion of GT, UAT and ST

12/29/2012 11:36 AM

At a minimum "We" need to hire a competent Electrical Power Engineer who has many years of experience doing what you have been asked to do. From my experience the design and engineering of the generating station main and auxiliary power transformers involves much more than just a list of name plate ratings and includes a lot of questions and requirements that most electrical engineers wouldn't even know to ask about.

If you are passing yourself off as a consulting engineer the only ethical thing to do is to inform your client that this work is out of your area of expertise. There is at least 200 manhours of dedicated study required to this properly, double or triple that if you want to pay for someone's learning curve, anything less will result in your posting questions such as "....Help, my TG just tripped and I don't know why..." that are seen on this site and others like it.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply
Guru

Join Date: Jun 2007
Location: chennai,India
Posts: 592
Good Answers: 19
#7

Re: Rating Selection Criterion of GT, UAT and ST

12/29/2012 11:56 PM

Detailed engineering has to be done then we have to do the diemensioning of the devices We can do it for cost

__________________
Ramesh,Freelance Electrical/automation Consultant
Register to Reply
Member

Join Date: Dec 2012
Posts: 5
#8

Re: Rating Selection Criterion of GT, UAT and ST

12/30/2012 11:55 AM

"....Help, my TG just tripped and I don't know why..."

of course we take help of DCS,DEH, protection panels & other dedicated schemes, and why not, itz what they r meant for :) only then we'd be able to know that whether its a Class A,B,C tripping,MFT,Turbine tripping,Islanding/House Loading,Grid Failure & so many other things

i was just asking u people's advice & surely would do the needful in due course of time but it doesn't mean that if the world don't know the answers, one should stop asking questions, IMO the only irrelevant question is which has never been asked n someone rightly said "There are always answers. We just have to be smart enough" .....

Register to Reply Off Topic (Score 5)
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#9
In reply to #8

Re: Rating Selection Criterion of GT, UAT and ST

12/30/2012 12:09 PM

Sorry if you were offended, none was intended. I was just passing along my experience of having answered your exact question for generating stations from from 40 to 1,300 MVA; GT, fossil, and nuclear. I'm your resource for this type of study; been there, done that, many times over.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply Off Topic (Score 5)
Member

Join Date: Dec 2012
Posts: 5
#10
In reply to #9

Re: Rating Selection Criterion of GT, UAT and ST

12/30/2012 2:58 PM

i'm not honest if i say that i wasn't offended, i was a bit; but good heavens! that i chose the right forum where by urs expertise n resources people get benefits...in reality i was a bit impatient for not able to find mines answers...maybe i need to learn some patience first,but again thanx for this

Register to Reply Off Topic (Score 5)
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#11
In reply to #10

Re: Rating Selection Criterion of GT, UAT and ST

12/30/2012 5:09 PM

Understood, now when you do your study keep in mind that the answer that you seek cannot be determined in haste from a handbook. Best of luck in your search.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply Off Topic (Score 5)
Register to Reply 11 comments