Q1: We used level transmitter (interface oil & water type:float), k-TEk suddenly the readings change fast from high reading then goes down to normal (like the pulse) why?
ABDULLAH
Regards, ABDULLAH
Re: K-TEK LEVEL TRANSITTER
12/29/2012 9:14 AM
It's broken. Get it fixed, or replace it.
Good Answers: 34
12/29/2012 9:14 AM
Is the level transmitter based on magnetostrictive principle? Is there aeration of the liquid? Can you post a sketch & type no of the K-TEK LEVEL TRANSITTER?
12/31/2012 1:27 AM
It is in dyhydrtion tank oil and water only
This is the model No of Float: EC/CST/4/FOFOW2/WR21/1219mm
Serial No; 10909 0023 01
This is the model No of Transmitter: AT100/S6/LW/A/R1/H1/M4A/X/CEX/(WP)CST-R41/FXX/1534MM
Serial No; 09-T4619
Regards, ABDULLAH
Good Answers: 34
12/31/2012 2:10 AM
Without product manufacturer's name/web address it is impossible to gather info on the products. Normally, aeration/bubbles in the path of level transmitter signal will give rise to wrong reading.
Good Answers: 34
Re: K-TEK Level Transmitter
12/31/2012 3:37 AM
Good Answers: 176
12/31/2012 1:50 PM
There's a jumper that defines whether the output goes to 21.0mA (upscale) or 3.6mA (downscale) during 'failsafe' conditions:
3.4 Jumper Settings
The jumpers located on the face of the electronics module (top left hand side) can be setup as follows, as described in the manual section (page 6) below:
See Section 6.11
ALARM (Fail Safe): (left jumper)
-The Alarm jumper will determine the output of the transmitter in the event that there is a failure in detecting the return signal from the sensor tube. This jumper should be set in the location which will send the control structure into a safe state.
-Placing the jumper to the lower position causes the output to go to 20.99 mA when there is a loss of signal or transmitter malfunction.
-Placing the jumper to the upper position causes the output to go to 3.61 mA when there is a loss of signal or transmitter malfunction.
You might be seeing momentary, intermittent failsafe conditions, which return to normal due to process conditions.
01/02/2013 7:56 AM
The release of a large bubble of air somewhere below the transmitter might do that, though the original posting makes no reference to the vessel in which the equipment is located, its size, the piping arrangements, the flowrates, the temperatures and pressures, etc., etc.