Posts: 2

Is There Any VFD for MV Motor of Voltage Level 11KV?

01/04/2013 4:06 AM

Does any of the vendor supplies a VFD for incoming voltage as 11KV? I have ideas about 6.6KV voltage VFD, but are the VFD's available for 11KV operation.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Anonymous Poster #1
#1

Re: Is there any VFD for MV motor of voltage level 11KV?

01/04/2013 4:59 AM

Yes, May visit abb.com for further reading.

Register to Reply
5
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#2

Re: Is There Any VFD for MV Motor of Voltage Level 11KV?

01/04/2013 10:34 AM

Yes, but they are usually LCI (Load Commutated Inverter) drives, which just means they must be engineered with the motor they serve. That typically isn't an issue with motors at that level because even the motors are custom engineered. ABB, Siemens, Converteam (ex Cegelec), GE and TMIC (Toshiba / Mitsubishi joint venture) all have LCI drive offerings last I checked. Robicon also used to have a true 15kV class PWM transistor based drive in their "Harmony" series, but I don't know if they still do since being taken over by Siemens since it would conflict with Siemens' LCI offering. But transistors present some serious risks of reliability at voltages above 7.2kV and often the protection they require starts to out strip the economic viability, that's why nobody else does it.

Rockwell (Allen Bradley) offers 11kV drives that are CSI (Current Source Inverter) design, which uses a transformer at the front and back to do the control at 6.6 kV inside, but that issue is transparent to the user, it is just 11kV in, 11kV out as far as the installation goes. The AB design is good for applications where the motor already exists because unlike LCI designs the drive does not rely on the motor impedance to accomplish the switching, therefore less up-front engineering is required so the drive can typically be built and commissioned faster.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply Good Answer (Score 5)
Guru
Canada - Member - Specialized in power electronics

Join Date: Feb 2008
Location: Montreal, Canada.
Posts: 1372
Good Answers: 80
#5
In reply to #2

Re: Is There Any VFD for MV Motor of Voltage Level 11KV?

01/05/2013 9:06 AM

GA! Once again. You certainly know your drives!

__________________
Experienced is earned, common sense is taught, both are rare essentials of life.
Register to Reply Off Topic (Score 5)
Guru

Join Date: Oct 2009
Location: sometimes Wales,UK.. was Libya, now Oman!
Posts: 1715
Good Answers: 117
#3

Re: Is There Any VFD for MV Motor of Voltage Level 11KV?

01/05/2013 12:11 AM

Not really.. as stated earlier, you can get them, but you also get a whole world of problems with 'harmonics'

WE in the oil industry use a step down transformer to feed the VSD, then a step up on the output, we also use 'K rated' transformers, active front ends and passive rear end filters for harmonics, which reduce the overall THD to less than 5% I & 8% V, better than IEEE 519.

If you need info on K rated transformers.. PM me and I'll send you a data sheet

__________________
The square root of nothing is what you make it!
Register to Reply Score 1 for Good Answer
Guru
Engineering Fields - Mechanical Engineering - New Member

Join Date: May 2008
Location: CHENNAI, TAMIL NADU, INDIA.
Posts: 1851
Good Answers: 65
#4

Re: Is There Any VFD for MV Motor of Voltage Level 11KV?

01/05/2013 4:21 AM

Dear Mr.Monirako,

YES, is the Answer for your Question. Siemens are manufacturing VFD MOTORS suitable for 11 KV OPERATION. You have not indicated the application, H.P. range etc. You can log on to www.siemens.com., and find out.

As the personal mail Id. is prohibited, pl. send details through CR4 personal messaging system. I will try to furnish details. By the way, where are you.?

DHAYANANDHAN.S

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#6

Re: Is There Any VFD for MV Motor of Voltage Level 11KV?

01/05/2013 6:26 PM

Given the size and potential value of such equipment, it would be worth some telephone calls to suitable vendors to find out.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Register to Reply 6 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); brich (1); dhayanandhan (1); JRaef (1); marcot (1); PWSlack (1)

Previous in Forum: No-Break Switch 2 Way Circuit   Next in Forum: Motor Protection

Advertisement