Motor Protection

01/04/2013 5:38 AM

I've a MV motor that is fed via a current limiting fuse and a vacuum contactor. A numerical motor protection relay is being used. should i set the relay for instantaneous Short circuit protection or let the fuse do its work? Relay catalogue suggests that in case of motors fed thru fused contactors, instantaneous short circuit protection unit of the relay should be bypassed. But tripping the contactor for a fault shall save the cost of replacing the fuse. What is the ideal practice in such a case?

Register to Reply
Pathfinder Tags: Motor Protection
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Anonymous Poster #1
#1

Re: Motor Protection

01/04/2013 6:27 AM

Your answer lies in the answer of following question,

1. What is short circuit breaking capacity of VC? Is it sufficient for system to which is connected.

2.How many (number) short circuits a VC can interrupt before replacement.

3. What is cost of replacement of VC Vs MV Fuse.

Register to Reply Score 1 for Good Answer
Guru

Join Date: Feb 2011
Posts: 7025
Good Answers: 207
#2

Re: Motor Protection

01/04/2013 7:25 AM

some of your terminology isn't quite right, let me assist. overload relays and fuses don't really have the "job (as you say to stop or protect you from "short circuits". a short simply means voltage is finding it's way through a winding or to ground before it was intended to. in both cases your protection devices ( fuses, overload relays are designed to stop excessive current (amps) from going through your wiring and windings. I'd suggest you fuse before the load side (line side) of your contactor. hope that helps

Register to Reply
3
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#3
In reply to #2

Re: Motor Protection

01/04/2013 10:05 AM

With all due respect Fredski, he does have the fuses ahead of the contactor, he is just asking if he should set the instantaneous trip of the very high end motor protection relay to a value that will open the contactor on a short circuit ahead of the fuse clearing level in a attempt to keep from blowing the very expensive MV fuses if possible.

Minu,

The answer lies in further investigation. Typically, a MV motor controller is designed such that the let-through current of the current limiting fuses is below the withstand rating of the vacuum contactor, but the thermal trip curve of the relay is meant to provide the running overload protection to prevent the fuses clearing on long time over current. The setting of the instantaneous trip of the protective relay can be set below the fuse short circuit curve to help pervent clearing of the fuses if possible, but must still be below the withstand rating of the vacuum contactor as well.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply Good Answer (Score 3)
Guru

Join Date: Feb 2011
Posts: 7025
Good Answers: 207
#4
In reply to #3

Re: Motor Protection

01/04/2013 10:07 AM

I had to read that twice

Register to Reply
5
Guru

Join Date: Jun 2007
Location: chennai,India
Posts: 592
Good Answers: 19
#5

Re: Motor Protection

01/04/2013 10:52 PM

Relay has to be set for over current protection, starting protection, unbalanced and earth fault protection and stall protection only when the motor is controlled thru contactor

For High short circuit currents it will be better to allow the fuse to blow out instead of opening the contactor, as breaking the contactor for short circuit current will damage the contacts.

There is a write up about this in ABB site ,please go thru ."contactor control Motor app guide 756085E"

__________________
Ramesh,Freelance Electrical/automation Consultant
Register to Reply Good Answer (Score 5)
Guru
Engineering Fields - Mechanical Engineering - New Member

Join Date: May 2008
Location: CHENNAI, TAMIL NADU, INDIA.
Posts: 1851
Good Answers: 65
#6
In reply to #5

Re: Motor Protection

01/05/2013 9:53 AM

Dear Mr. ramvinod,

You are absolutely right and agree with you. The Contact making Current and Breaking Current itself is a big subject - and will damage the Contactor due to severe Arcing.

THANKS.

DHAYANANDHAN.S

Register to Reply
Commentator

Join Date: May 2011
Posts: 84
Good Answers: 1
#8
In reply to #5

Re: Motor Protection

01/11/2013 6:22 AM

Thanks for this very informative article of ABB.

Register to Reply
Member

Join Date: Sep 2009
Posts: 8
#7

Re: Motor Protection

01/06/2013 5:12 AM

My dear:

for more practical comment please let me know your motor pow.,contactor model and it's manufacturer.

abootorab

Register to Reply
Register to Reply 8 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

abootorab (1); Anonymous Poster (1); dhayanandhan (1); Fredski (2); JRaef (1); muditmah (1); ramvinod (1)

Previous in Forum: Is There Any VFD for MV Motor of Voltage Level 11KV?   Next in Forum: Network and Analysis

Advertisement