01/13/2013 8:30 AM
for York compressor ,Oil level Sight glass shows some foams floating upon oil surface, While some other compressor with pure oil ( NO foam)
So my questions 1 - Why this foam
2 - Does this foam affects compressor performance.
3 - do we need to change oil , or there is other solution to release that foam
Re: Foaming oil
01/13/2013 8:40 AM
You have used a detergent oil.
If that's what the specs call for, don't worry about the foam; it's normal.
If the specs call for a non-detergent oil.............change it.
Re: Foaming oil
01/13/2013 2:44 PM
It's not detergent oil , Its YORK "E" oil" As specified by York
Re: Foaming oil
01/13/2013 4:06 PM
Okay. It was just a thought.
I've come close to making that mistake in the past.
Thanks to whoever undid my OT. I didn't think it was outside the realm of possibility.
Re: Foaming oil
01/13/2013 8:37 PM
Clean out the entire foam system, especially if stored for an extended period of time
Foam concentrate can cause the lines and tank to gum up, impeding foam performance. Add foam tank cleaner (part number N205701) in the tank and lines. Use according to label directions. If switching brands of foam concentrate, clean out the system tank and lines. (For best results, use John Deere Spraymaster ULTRAX foam concentrate.)
I am turned into a sort of machine for observing facts and grinding out conclusions——http://industrialmachine1.appspot.com/
Re: Foaming oil
01/13/2013 10:20 AM
it has nothing to do with detergents, refrigerant oil and refrigerant have a high affinity for each other, the refrigerant migrates to the oil. make sure your crankcase heater is working properly and you aren't overfilled with oil. a little foaming on start up is normal, if you get too much you'll washout the bearings and have a complete failure. so verify the heater is installed correctly and functions. do an acid test and possibly drain and replace the oil to the proper level. if this a "built up system" you might want to check the piping design for traps and low spots where oil is accumulating....causing people who work on the system to be fooled and having them overfilling the case, good luck
Re: Foaming oil
01/13/2013 3:21 PM
Thanks Fredsky And G.A
It's a fearful matter, So oil changing is not the solution without eliminating reasons of this phenomena.
any more suggestions are fully appreciated.
Re: Foaming oil
01/13/2013 4:02 PM
I wasn't suggesting that. because you have refrigerant in the oil (cause of foam) you can't tell just how much oil is in your system) checking for acid is standard practice. do whatever you want, those are just my suggestions based on over 30 years of experience.. I'd be looking close at the crankcase heater(s). as already stated a little foam is usual and isn't a problem....maybe you could include a pic of the bullseye?
Re: Foaming Oil
01/13/2013 12:08 PM
What refrigerant--ammonia or halocarbon?
Depending on piping layout, if there is a small amount of liquid refrigerant returning with the vapor, it may cause oil foaming in some compressor(s) but not others.
Re: Foaming Oil
01/13/2013 2:39 PM
Dear tornado
thanks for your input.
For refrigerant ,It's R22
if there is a small amount of liquid refrigerant returning with the vapor, it may cause oil foaming.
now we have reached for another question. Why some or a lot of liquid refrigerant return with vapor.
Is it a result for defected or un calibrated expansion valve,water cooler problems ,low cooling load or any others .
Re: Foaming Oil
01/13/2013 3:01 PM
I have the answer but yo asked Mr Twister so I'll wait
Re: Foaming Oil
01/13/2013 3:16 PM
An expansion valve may be adjusted for insufficient superheat, or it could be worn and thus not close tightly enough under light load.
If there are trapped double oil risers, you might occasionally get a slug of oil returning in the suction, which could have some liquid refrigerant mixed in.
If the foaming is light (a layer on top of the oil) or brief, it should be no problem, as it still contains some oil.
(I'm more of an ammonia guy; some "Freon" folks might have further ideas.)