I WANT TO RUN INDUCTION MOTOR FORM 0 TO 50HZ THROUGH A VARIABLE FREQUNCY DRIVE. WILL THERE BE ANY ISSUES?
Re: MOTOR FREQUENCY
01/18/2013 3:27 AM
The first one is the unwarranted use of Caps Lock.
  • To what is the motor coupled?
  • What does its torque/speed characteristic look like?
  • Where on that curve is the motor going to need maximum cooling?
  • Is it worth over-sizing the motor and the drive to clear the peak of that curve with capacity to spare?
  • What are the hazardous area implications?
  • How far is the distance along the cable from the drive to the motor?
  • Is there a competent person available to select the motor/driven component/variable frequency drive correctly?
  • Is there a competent person available to programme the drive correctly?
  • Is the supply adequately sized for the job?
  • Etc., etc.
Re: MOTOR FREQUENCY
01/18/2013 3:33 AM
THIS IS FOR A SCREW AIR COMPRESSOR
Re: MOTOR FREQUENCY
01/18/2013 3:43 AM
So what?
Re: MOTOR FREQUENCY
01/18/2013 4:55 AM
YES. IF YOU WANT THE SHAFT TO GO ROUND N ROUND.
Re: MOTOR FREQUENCY
01/18/2013 9:05 AM
A screw compressor would be considered a constant-torque load. Select the type of VFD accordingly. Also check whether the lubrication system will function properly at less than full speed.
Good Answers: 804
Re: MOTOR FREQUENCY
01/18/2013 1:36 PM
Start with Why!
Not every application can benefit from having a VFD applied to it, despite the marketing materials that come from VFD mfrs.
Re: MOTOR FREQUENCY
01/18/2013 3:49 PM
BUT IF I TOUCH THE "CAPS LOCK" KEY, HOW WILL I GET MY CAPS UNLOCKED?
Good Answers: 804
Re: MOTOR FREQUENCY
01/19/2013 12:36 PM
Step AWAY from the computer!
The International Cabal of Users Technical Oversight Ombudsmen (ICUTOO) has determined that if you cannot figure out how to unlock your Caps Lock feature, you are likely to do something that will harm the internet.
Cease and desist immediately!
Re: MOTOR FREQUENCY
01/20/2013 12:01 AM
thanks for your inputs. i was able to succefully commisionin on 20hz