DK-20 Paralleling Problem

01/18/2013 4:42 PM

I AM IN A SHIP WITH 3 DK-20 900RPM 60HZ 440KW AND WE DISCHARGING CEMENT BY 4 CRANES AND SHIPS CRABS!IF RUNNING AND THE 4 TOGETHER THE LOAD GOING ABOUT 200 KW EACH GENERATOR BUT COMING ALARM MSB BUS LOW FREQUENCY FOR A LITTLE AND AFTER GOING AGAIN NORMAL!SO ALL THE TIME HAPPENING THIS!THE FUEL PRESSURE ITS NORMAL!HAVE ANYBODY ANY IDEA TO HELP ME?THKS

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#1

Re: DK-20 Paralleling Problem

01/18/2013 9:21 PM

With the all-caps and so many exclamation points, this looks like a comic book.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
2
Power-User

Join Date: Jan 2010
Location: Atchison Village
Posts: 383
Good Answers: 39
#2

Re: DK-20 Paralleling Problem

01/18/2013 11:54 PM

Translation: You're operating four cranes and some kind of ship's equipment with three 440kw generators, and when all cranes are operating you're getting low frequency alarms fairly continuously. Fuel pressure is normal. Each generator is showing 220kw under these conditions, and should not be throwing low frequency alarms. I'm not familiar with load balancing, but are you checking fuel pressure at the time of low frequency? Is there a filter AFTER the fuel pressure gauge, that might be clogged? Is one generator lagging so much it's dragging the others down" How many hours on the generator? How are the exhaust temperatures on the three generators? Have you ever tested the generators singly for full output?

Have you tried with just two generators, since the load is only 600 kw (three gens at 200kw)

__________________
Align culture with nature...
Register to Reply Good Answer (Score 2)
Guru
Engineering Fields - Systems Engineering - New Member Hobbies - Model Rocketry - New Member

Join Date: Dec 2006
Location: Long.92E,Lat.26N
Posts: 1336
Good Answers: 14
#3

Re: DK-20 Paralleling Problem

01/19/2013 8:05 AM

You are doing just fine!

Don't meddle with the setup.

Register to Reply