Anonymous Poster #1

Double Pole Ciecuit Breaker

01/24/2013 5:04 PM

Why should Low Voltage Distribution boads units for lighting and small power distribution have double circuit breakers?

Also why the incoming CB to a DB is limited to only 60 or 1oo Amps and not more than that, say 200 or 300 Amps?

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#1

Re: Double Pole Ciecuit Breaker

01/24/2013 5:08 PM

Code.

Look at your local building codes.

Reply
Guru

Join Date: Jul 2008
Posts: 1688
Good Answers: 145
#2

Re: Double Pole Ciecuit Breaker

01/24/2013 5:11 PM

IF you are in the US or a country with similar power THEN the only time I have seen double pole breakers is for 230V circuits. In the US a home does not have a 230V line but has two 115V lines that are 180 degrees out of phase.

Q2: If 60A or 100A is enough then the builder and power company were probably cost sensitive and only provisioned as required.

__________________
Few things limit our potential as much as knowing answers and setting aside questions.
Reply Score 1 for Good Answer
Guru
Engineering Fields - Instrumentation Engineering - EE from the the Wilds of Pa.

Join Date: Feb 2006
Location: middle of nowhere, Pennsylvania
Posts: 2603
Good Answers: 63
#7
In reply to #2

Re: Double Pole Ciecuit Breaker

01/25/2013 8:19 AM

Exception to your rule - let an European designer do the schematics for the panel you are building for USA use, and you'll have double pole circuit breakers and fuse blocks with the one fuse a brass dummy on 120V circuits - and yes they know the one side is connected to N as evidenced by the dummy fuse. Been there and done that. I have redesigned more than a few European designs in the past three years to make them more acceptable for use here.

__________________
Remember when reading my post: (-1)^½ m (2)^½
Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#3

Re: Double Pole Ciecuit Breaker

01/24/2013 6:42 PM

It's economical, the higher the voltage the lower the amp draw, the smaller the wire size required, the cheaper the cost of installation....

__________________
All living things seek to control their own destiny....this is the purpose of life
Reply
Guru
United Kingdom - Member - Not a New Member Hobbies - Musician - New Member Hobbies - Fishing - New Member

Join Date: May 2006
Location: Reading, Berkshire, UK. Going under cover.
Posts: 9684
Good Answers: 468
#4

Re: Double Pole Ciecuit Breaker

01/24/2013 7:02 PM

Q2 - If the incoming CB was rated at 300A, all the wiring to the next protective devices would also have to be rated at 300A. That's chunky wire in a little DB.

__________________
"Love justice, you who rule the world" - Dante Alighieri
Reply Score 1 for Good Answer
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#5

Re: Double Pole Ciecuit Breaker

01/24/2013 11:21 PM

If both conductors are ungrounded, the CB must interrupt both poles.

There is no such 60 or 100A limitation if the bus bars are sized for greater current, except for the vagaries of local codes.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Reply Score 1 for Good Answer
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#6

Re: Double Pole Ciecuit Breaker

01/25/2013 3:19 AM

Switching a neutral is prohibited under British Standard 7671. So the question is a non-starter.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply Score 1 for Good Answer
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#8
In reply to #6

Re: Double Pole Ciecuit Breaker

01/26/2013 2:04 AM

Should the main disconnect(isolator,cb,lbs) in a switchboard/load centre/consumer unit have neutral disconnect together with phase disconnect?.

__________________
pnaban
Reply
Guru
Hobbies - DIY Welding - Wannabeabettawelda

Join Date: May 2007
Location: Annapolis, Maryland
Posts: 7940
Good Answers: 458
#13
In reply to #6

Re: Double Pole Ciecuit Breaker

01/28/2013 2:26 PM

Even if you are on ship?

Reply
Guru

Join Date: Jul 2006
Location: Eastern Kansas USA
Posts: 1503
Good Answers: 128
#9

Re: Double Pole Ciecuit Breaker

01/26/2013 2:21 PM

Friend,

It's hard to answer your question with details when we don't know the location you refer to. As you can see from posts already, CR4 has membership around the world.

With typical residential or small commercial installations, the power is single-phase. If it is brought in as a single-voltage (such as 120VAC), one of the two wires is grounded/earthed for safety (and is called the neutral) and the other one requires a fuse or CB to provide short circuit or overload protection (and is called the hot). However, by adding one more hot wire from the source, with voltage opposite to the first hot wire, you can double the amount of power with only the addition of 50% more wires. You then would need a double-pole CB, because safety requires that both wires be de-energized if either one has a short or serious overload.

Therefore the answer to Q1 is add 50% more wires and get 100% more power capacity. A pretty economical move.

Regarding Q2, many have answered it well already. Generally you are balancing the anticipated load with the cost of providing power to it. In the USA: 100 years ago, the typical service was 30A @ 110V single-pole and two circuits branching from it. More uses for electricity have become common, so the typical service size rose to 60A @ 220-240V, double-pole. More recently, the minimum size is 100A @ 240V, double-pole. During all these years, there have been exceptions for people planning a long-ways ahead or having larger homes. [My father rewired the family home in 1952 and went from 30A/120V to 200A/240V; the only way the utility could sell him electricity was with a small business rate, because nobody else had a home with that large a service. Of course, 60-years later, that home still has plenty of power available.]

--JMM

Reply
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#10
In reply to #9

Re: Double Pole Ciecuit Breaker

01/26/2013 10:51 PM

In UK when they disconnect power to a premises(home/industry)by the main switch/breaker in switchboard/consumer unit does the neutral remain connected?.

__________________
pnaban
Reply
Guru

Join Date: Jul 2006
Location: Eastern Kansas USA
Posts: 1503
Good Answers: 128
#11
In reply to #10

Re: Double Pole Ciecuit Breaker

01/28/2013 12:29 AM

Pnaban,

I work in the USA and don't know the UK rules on this. Someone out there???

--JMM

Reply
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#12
In reply to #11

Re: Double Pole Ciecuit Breaker

01/28/2013 2:45 AM

To P.W.Slack

__________________
pnaban
Reply
Reply to Forum Thread 13 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Brave Sir Robin (1); BruceFlorida (1); jmueller (2); JohnDG (1); lyn (1); Phys (1); pnaban (3); PWSlack (1); SolarEagle (1); Tornado (1)