Anonymous Poster #1

Change Over Switch

01/31/2013 4:57 PM

We often change between two methods of control, remote and pendant this means each time we have to swap the plugs which houses the control cable.There are 30 cores in each one.We did try a rotary switch with extra contact block, it does work but looks very flimsy and makes fault finding a nightmare.We have 24volts AC available in the panel.I was going to try using 30 of the slimline relays, but if anyone has any other ideas please let me know.

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#1

Re: Change Over Switch

01/31/2013 6:36 PM

30 of the 1 pole double throw relays is actually likely the least expensive, but is fraught with the dangers of what happens if only one goes bad.

I would use what are called "Machine Tool Relays", far more reliable and they can handle up to 12 poles. Your configuration would still require multiple relays because the 12 poles are all single throw, so you only get 6 DT poles per relay. But I would also have a master-slave arrangment, where you control only one relay, IT then controls the others.

Click for link

Relay 1 (Master, 8 pole) = 5 NO contacts feeding the coils of Relays 2, 3, 4, 5 and 6.

Relay 2 through 6 (slaves, 12 pole each) = 6 sets of CO (Change Over; 1NO, 1NC)contacts for your control stations, 30 total.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Reply Score 1 for Good Answer
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#2

Re: Change Over Switch

01/31/2013 10:03 PM

How about wiring both up permanently, with a lockout bag/barrier to prevent use of the idle item?

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Reply
Power-User

Join Date: Nov 2012
Posts: 142
Good Answers: 14
#3

Re: Change Over Switch

02/01/2013 12:28 AM

You don't say what load current or voltage (AC or DC, or level) the loads operate at, only that 24v AC is available in the panel.

If AC, have you considered using Triacs for this purpose.

If you use AC for the supply then the devices will switch off within the first half cycle after the gate is de-energised - highly inductive loads may pose a switch off problem, but this can be mitigated with an appropriate snubber circuit.

No relays will be required, but you will need 30 Triacs for each cable with a common gate feed for each set of 30.

Energising either gate circuit would switch on the relevant set of Triacs, which would remain in conduction until either the gate is isolated or the supply is removed

Depending on the load and supply voltage, they may be far cheaper and definitely more reliable than relays.

Heat sinking may be required for heavier loads.

Having said all of that, if you require guaranteed electrical isolation of the separate circuits for handling purposes then the relay or other mechanical switching methods would be preferential.

Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#4

Re: Change Over Switch

02/01/2013 4:13 AM

One could always replace the pendant with a piece of string and hang the remote on it from time to time.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply Score 1 for Off Topic
Guru

Join Date: Feb 2010
Posts: 1013
Good Answers: 36
#5

Re: Change Over Switch

02/01/2013 7:27 AM

If your controls require that the swap is complete and does not tolerate the case of having any one contact not changing over, then apply this method, if using multiple relays to cover the 30 contacts:

Suppose that you have relays each with n number of Change/Over contacts (example n = 4). You should use one of the C/overs, on each relay, connected in series on all of them, in such a way that the control power does not reach the part of the circuit doing the actuations, unless all the contacts in series, are closed ( for both cases). This means using an extra relay/contactor to supply the circuit.

The Swapping relays will have their supply before the extra relay/contactor, and controled by a switch (?!).

With n = 4, you will need 10 relays + the extra one relay/contactor.

Depending on the currents being switched, you might get relays with more than 4 c/overs.

Reply
Associate

Join Date: May 2010
Posts: 46
Good Answers: 1
#6

Re: Change Over Switch

02/01/2013 8:55 AM

I would suggest a simple PLC which can eliminate the need for relays and changeover switch. If you could send the details of 30 wire connections to the pendant and how they are connected to the control circuit, I might be able to tell how a PLC can achieve this.

Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#7
In reply to #6

Re: Change Over Switch

02/01/2013 9:29 AM

Chances are if Anonymous Poster#1 cannot figure out how to do this with electromechanical components, then using a PLC is likely WAY beyond his skill set, not only for initial installation but for future troubleshooting. Plus, pendant control often indicates cranes or other moving machinery, and safety becomes more complex if you have a PLC (again, assuming a skill set that could not include a Safety PLC). You or I might choose to do it this way, but I have had bad experiences applying PLCs in applications where the users are not sophisticated enough, even when I do all of the initial programming and commissioning.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Reply Score 1 for Good Answer
Guru
Canada - Member - If there is a way to screw someting up, there is someone to do so! Safety - Hazmat - New Member

Join Date: Mar 2007
Location: Iqaluit, NU. Canada
Posts: 1854
Good Answers: 140
#8

Re: Change Over Switch

02/01/2013 1:04 PM

Why do you not...

Permanently wire both control systems, then add a simple selector switch on the console that select which method is active, the selector switch will then kill the contol power going to the different control switches. That way, only one set of pushbuttones/switches is energized at a given time.

__________________
Joe Contractor to Electrical Inspector, "What do you mean you are going to make me follow the code?".
Reply Score 1 for Good Answer
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#9

Re: Change Over Switch

02/03/2013 7:20 PM

If this is for crane control, I would seriously look at the legal and safety implications before doing anything.

__________________
The reports of my death are greatly exaggerated.
Reply
Reply to Forum Thread 9 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

bwilko (1); JRaef (2); LAA_Lucke (1); North of 60 (1); Priyadarshan (1); PWSlack (1); TonyS (1); Tornado (1)