I am quite dismayed with the responses on this site to my post "Double Pole Breaker - The Sequel", as a very wromg answer received a 2 rating. One response receiving a 2 rating said neutrals must never be switched. WRONG!
You all better read NEC 240.22 and NEC 430.105. Yes - they may - particularly in the case I was describing.
In an industrial panel, which I was describing, no-one would use the branch circuirt breakers in one of these as a switch. To begin with, such a panel requires shutting off all power to the panel before the door can be opened to access the breakers. Then what? - repower by defeating the door interlock and procede to turn motors on and off with the breakers as a means of control - of course not. They are manually switched only as an aid to maintence. They are over current devices covered by the 240.22 mentioned and as long as the "heat" is disconnected with the neutral, everything is fine.
The thing that really concerns me is that this site is promoting the idea that a circuit breaker should routinely be used as a switch. A 489 rated breaker for an industrial panel simply is not made for repeated manual tripping. The manufacturer of the breakers in question never mentions using them as switches, but certainly indicates how many fault trip cycles they can handle.