Bitumen Hazardous Area Classification

03/04/2013 11:06 PM

Hello All,

Can some one please let clarify if Bitumen (or fumes from Bitumen) generate a Hazardous Zone around a potential leakage point for example flanges. Does Bitumen stored in tank generate Zone 0 up to the roof?

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#1

Re: Bitumen Hazardous Area Classification

03/05/2013 12:55 AM
__________________
All living things seek to control their own destiny....this is the purpose of life
Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#2

Re: Bitumen Hazardous Area Classification

03/05/2013 3:21 AM

Hazardous area zoning cannot be carried out over the internet. Hire a consultant to carry out the exercise. However, some general points:

  • Zone 0 applies to the insides of closed tanks, usually.
  • In general, if there are large areas of Zone 1 then the facility has a serious process containment problem to tackle.
  • If an operator is placed in Zone 1, the facility can face prosecution on Health & Safety grounds.
__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply Score 1 for Good Answer
Member

Join Date: Mar 2011
Posts: 5
#3
In reply to #2

Re: Bitumen Hazardous Area Classification

03/05/2013 4:32 AM

You are of no help mate. You have provided some age old information

Thanks for wasting your precious time anyway...

Reply Score 1 for Off Topic
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#4
In reply to #3

Re: Bitumen Hazardous Area Classification

03/05/2013 5:01 AM

<...mate...>

How abstruse.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply Off Topic (Score 5)
Guru
Hobbies - Fishing - Old Salt Hobbies - CNC - New Member United States - US - Statue of Liberty - New Member

Join Date: Mar 2007
Location: Rosedale, Maryland USA
Posts: 5197
Good Answers: 266
#5

Re: Bitumen Hazardous Area Classification

03/05/2013 7:44 AM

Zone 0

Flammable atmosphere highly likely to be present - may be present for long periods or even continuously

Zone 1

Flammable atmosphere possible but unlikely to be present for long periods

Zone 2

Flammable atmosphere unlikely to be present except for short periods of time - typically as a result of a process fault condition.

__________________
Life is not a journey to the grave with the intention of arriving in a pretty, pristine body but rather to come sliding in sideways, all used up and exclaiming, "Wow, what a ride!"
Reply
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#6

Re: Bitumen Hazardous Area Classification

03/05/2013 1:39 PM

Bitumen (or Asphalt) produces Hydrogen Sulphide as a byproduct when heated, and as such the area in the tank and around the flanges will need to be zoned (based on your local hazardous area standards and the construction and function of the flanges).

You will need a local inspector or similar to zone the areas as the location, shape and even height of the zones depend on your site construction and layout and will probably consist of zone 0 inside the tank with areas of zone 1 and 2 around the tank and surrounding area.

Does Bitumen stored in tank generate Zone 0 up to the roof?

Without detailed knowledge of the site and building it is impossible to give an accurate answer, but I would say yes if the area is completely sealed and gas has a chance to build up and stay in explosive concentrations for extended periods of time.

__________________
jack of all trades
Reply Score 1 for Good Answer
Member

Join Date: Mar 2011
Posts: 5
#9
In reply to #6

Re: Bitumen Hazardous Area Classification

03/05/2013 5:05 PM

Thanks for your efforts and your answer.

Reply
2
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#7

Re: Bitumen Hazardous Area Classification

03/05/2013 2:28 PM

Here we go again, see this thread to see the divergent opinions from a similar question...

The short answer is that as far as the NEC and NFPA are concerned, only areas where a flammable gas or liquid having a flashpoint at or below 100ºF are required to be classified. According to this MSDS, Bitumen has a flashpoint of 166ºC and no autoignition point, however it is flammable when heated above its flashpoint and exposed to a source of ignition.

"...

A. The hazardous Class I location requirements contained in Art. 514 only apply where a flammable liquid having a flash point below 100°F [Art. 100 Volatile Flammable Liquid] is stored, handled, or dispensed [514.3(B)]. The flash point of diesel fuel is 100°F or above; thus, the area involving diesel fuel is typically not a classified location. But if the conduit for the diesel dispenser passes through the Class I area around the gasoline dispenser, then the installation must comply with the sealing and wiring method requirements of Art. 501 ( Figure )..."

From http://ecmweb.com/qampa/code-quandaries-6

Extending this to Bitumen which is a heavier and less volatile fraction than diesel fuel, the answer to the OP's question is "No". However, as other posters will be quick to point out, only someone who is familiar with your installation (you could have a leaky flange above a 1000ºC surface, something none of can see from here) has any right/responsibility/liability to answer your question with any authority.

Protect your client and yourself, hire a professional familiar with your local codes and AHJ.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Reply Good Answer (Score 2)
Member

Join Date: Mar 2011
Posts: 5
#8
In reply to #7

Re: Bitumen Hazardous Area Classification

03/05/2013 5:04 PM

Thanks for the efforts and you answer.

Reply
Reply to Forum Thread 9 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

jack of all trades (1); ozzb (1); PWSlack (2); RAMConsult (1); SolarEagle (1); sonsan (3)