This plant has a Diesel engine driven generator, housed in the ground floor. On the roof top (open space) there is the diesel oil day tank located, from where diesel flows in to the engine fuel pump.
I have to install a flowmeter to measure the flow rate of diesel fuel. I am proposing to install a paddle wheel type flow sensor inserted in the 40mm dia pipe at the outlet.
Will this be considered as a Hazardous zone of any type? Will the flow sensor and fittings have to be intrinsically safe / explosion proof (by the virtue of this is going to be inserted into a liquid fuel pipe)?
Thanks for your help.
Re: Is this Considered Located in a Hazardous Area?
01/29/2013 7:59 PM
Is this considered a hazard zone now?
How would the addition of a flow meter have any influence on the designation of the area?
The flow meter doesn't care where you put it.
01/29/2013 9:33 PM
This thread is a fine example of questions from the uninformed that should be deleted.
Clearly, the OP is not qualified in any way to install equipment in a hazardous area. Especially if they don't know what a hazardous area is.
OP, an anonymous forum is not a good place to ask for advice that could have deadly implications if that advice is wrong.
Maybe it's just me.
01/30/2013 12:03 PM
Yep, it's just you...
common knowledge...less common than common sense
16
01/30/2013 10:52 PM
So let me get this straight......if someone is uninformed, then they shouldn'y bother seeking information from those that are apparently more informed?
Maybe....the OP came to an 'Engineering' forum, where he (I assume male) thought he may find skilled and knowledgable individuals that could shed some light and insight on his particular problem and assist him in some way/shape or form.
Maybe he is not qualified. Maybe thats why he is here.
Maybe we could explain that a hazardous area is an area that has the potential to cause harm/damage etc. Maybe we could tell him to start by consulting with his WHS representative/officer, and discuss the matter further, to ascretain the risk involved, if he is unsure.
Maybe he is a maint fitter on his first day in a new role, in a different working environment than he was ever exposed to in his previous roles.
Maybe he was sitting on the fence in regards to his opinion of engineers prior to posting. Maybe now he thinks most of them are rude and unhelpful.
And maybe next time he wants assitance with something, he definately wont bother with consulting field experts on CR4, and he will just do whatever the hell he reckons feels good on the day.
Dont get me wrong, it isnt the best question, but it doesnt mean we shouldnt attempt to give him our best answer.
Maybe you need a holiday Lyn. All these long days of reading 'dumb' questions appear to be getting to you.
Fish dont know they're underwater.......think.
Register to Reply Good Answer (Score 16)
Good Answers: 117
01/30/2013 11:27 PM
Yes! GA from me!
It would seem that someone here has a bug up their butt about something.... so the OP doesn't know about haz areas. Well point him in the right direction!
come on people.... no-one know everything!
I teach my students and trainees, "there is no such thing as a stupid question, it is only stupid NOT to ask!"
Good Answers: 25
01/31/2013 6:01 AM
I think OP will think CR4 as Hazardous Area if he is treated like this.
Good Answers: 25
01/31/2013 6:08 AM
If you feel so then my humble request to you is that simply do not answer such questions from OP who may not be as knowledgeable as seniors here in the forum.
01/31/2013 6:53 AM
it's clearly you, It is clear, right?
01/31/2013 8:04 AM
Woah - I design and build panels for hazardous areas and install instrumentation on equipment for use in hazardous areas. Our panel shop has a UL file to build panels for thses areas. I GET THE AREA DESIGNATIONS FROM THE FACILITY WHERE IT IS GOING. I would NEVER try to determine the rating of an area like this - ever.
The OP needs help, but above and beyond this sites capabilities. He needs an expert on site to determine this and should be instructed to head this direction. (usually the facilities insurer will help to determine the rating) From the brief description we could guess what the rating is, but that would be a very dangerous guess at best.
01/31/2013 5:58 PM
This is exactly the information the OP needed.
Someone could still enlighten them on the procedures that are required, and why the professional in that field should at be consulted before continuing.
I've known allot of great engineers, but not one would ever think that there is nothing left to learn.
02/01/2013 8:25 AM
Thank you. I am close to retirement but am still trying to learn.
01/29/2013 11:41 PM
If it is an area that could be exposed to fuel vapors or splashing fuel it is a hazardous area and electronics should be intrinsically safe.
To be sure you should have the project checked by your safety personnel and plant management to ensure you follow all guidelines.
Drew K
7
01/30/2013 3:54 AM
  • The extent of hazardous areas in any plant will be shown locally on a drawing.
  • The type of sensor has no bearing on the dimensions of the hazardous area.
  • The hazardous area has a bearing on the type of sensor to be selected and the method of installation.
  • Equipment can be selected as explosion-protected in itself, however only complete installations can be intrinsically safe or not as the case may be, as the cabling and the method of supply of the installation determines whether it is intrinsically safe or not.
  • Before selecting, installing, energising, testing or maintaining hazardous area equipment, ensure a suitable training programme has been completed.
  • Why does the flow sensor have to be electrically supplied at all? Many non-electrical flow instruments are available and suitable for diesel fuel. Is someone being lazy and not wanting to walk to read it at intervals?
  • That the CR4 good answer voting system is being used to indicate answers that are not liked, is abstruse.
01/30/2013 10:01 AM
Odd...someone must not have liked 2 rather rude posts on this thread but another decided that those rude comments were likeable? Wish I could vote again and put those disrespectful comments on the off topic list.
Madam Manners (not the OP)
Register to Reply Off Topic (Score 9)
01/30/2013 10:36 AM
The only rudeness I see here IS YOURS!!!!
Why not quit hiding behind the cloak of anonymity and attach a name to your whining.
01/30/2013 11:07 AM
In what world is this statement a courteous way to speak to a new member of this forum?
Just because you don't agree with the post or manner of questioning a fellow guest here does not mean you can police them with harsh words.
You may be the most prolific contributer here but that does NOT make it your job to police other contributors.
Same as my anonymous posting, if you don't like what the OP or I write then report it to the admin and let them do their job of judging my behavior.
The reason I post anonymously is to prevent your vigilante justice and retribution.
I realize the hypocrisy of my post criticizing your behavior and apologize for it.
Madam Manners
01/30/2013 11:34 AM
To give Lyn credit, I don't think he is trying to be rude, his point is that in a situation like this (safety) If you don't know what you are doing, you shouldn't be doing it. The consequences of making a mistake here could be deadly, not only for the OP but his or her coworkers. I work in a coating facility, we have flammables / combustibles all over the building. My company has spent allot of money to make those of us that work around flammables knowledgeable about what we are doing.
01/30/2013 12:15 PM
So your true goal was just to trash me for being honest?
Where's the helpful, constructive advice from you, or The.Tinkerer?
Never mind.
<unsubscribe>
01/30/2013 12:44 PM
My entire post was advice to you. Be courteous in your comments, don't be insulting especially to newcomers who have not been around long enough to learn the ropes.
I hope have not unsubsribed to get the last word in, or to spit your dummy out in protest.
Madam Manners
01/30/2013 1:18 PM
I'll gladly continue to monitor the post without further comment, except to say that it serves no good purpose to blindly answer questions posed here, regardless of the obvious lack of technical competence of the questioner. People get killed that way.
<Observing, so give it all you've got>
01/30/2013 1:31 PM
I agree with you completely, we do need to be careful what knowledge we share. It would be unethical otherwise.
And in afterthought I was a bit harsh in my comment to you. My intent was only to show you that I felt your response to the OP was harsh.
Madam Manners
01/30/2013 3:58 PM
Aww Lyn...I know you better than that!
Take my posts from the slant of witty sarcasm
I was just agreeing with you!
01/30/2013 11:10 AM
Sounds like a scolding to me.
01/30/2013 11:22 AM
If the truth hurts, maybe it should.
Should the OP be installing equipment in a fuel line if they do not know what constitutes a hazardous area?
I firmly believe that people such as this OP come here because they are too cheap/lazy to take the time to learn the various code and safety requirements but feel it is expedient/free to pick the brains of members in hopes of saving some money, or face.
Never mind that lives may be lost as a result of non-qualified people such as the OP, and maybe the AP1 preacher too, working in areas where they have no competence.
01/30/2013 11:37 AM
I am qualified as an expert in my field (12 years of experience) and know a thing or two about other fields.
I am learning about my new career and using my existing experience where it is applicable...so I come here to ask questions about things outside my experience.
The other plant engineers I work with are often tasked with projects that are on the fringe or outside of their specific experience, so they ask around for advice. Some might choose to ask their questions here.
I agree with AP1 that your comment was not appropriate or helpful.
I am not cheap or lazy, I posted a question yesterday about a bearing fault that I had never seen before because I value the knowledge and experience of the members here (including yours).
Your knowledge and experience would have had more impact on the OP if you had written a cautionary but helpful response instead of taking this antagonistical approach.
Drew K
01/30/2013 4:08 PM
Qualified as an expert? What the heck does that mean?
Certified? That's a different story...
Lyn's comment is more helpful than someone who just spoon feeds the correct answers to someone withhout providing a solid reference.
Asking such a broad question about installing devices in explosive environments should be handled the way an accident would handle the OP or innocent bystanders...with extreme prejudice.
Lyn is an antagonist...that's his nature, but it's also an effective method for dealing with people who are trying to do things that they think they are qualified for, but probably not certified for by a competent authority.
What are we here...a bunch of babies?
01/30/2013 4:15 PM
Expertise comes from experience and is qualified by years of service in your field.
Certifications come from training and education.
Your other comments are descriptions of how many questions are started here.
As for the final comment:
I thought we are adults who treat each other with respect and professionalism.
Drew K
01/30/2013 6:15 PM
Nah...we're obviously a bunch of childish punks raised on radio who survived into their older years through training, experience, and a modicum of common sense.
Plus, we were yelled at when we did stupid stuff...or attempted it
01/30/2013 5:22 PM
GA Tinkerer.
Good Answers: 122
01/31/2013 9:07 AM
What are we here ...a bunch of babies?
One of my fellow engineers just received a written warning and is being required to attend physcological counseling for stating nothing more in an email than: "We continue to experience problems with XXX Contracting when they order concrete cement for their part of the project and this is causing severe delays and increasing costs to the project budget. Obviously the person calculating the yardage requirements didn't pass first grade math."
Based on this recent development and a growing number of simular incidents, I would say "YES".
Too bad for all of us as some of my most productive mentoring was done in the same fashion as in Lyn's post.
Many times it was not comfortable nor by any means paletable but it served it's purpose well as it made me do my homework and research with an intensity that otherwise I might not have done so.
In our decaying, collapsing industrial and commercial world today we are so concerned with HR and interpersonal relationships that the technical expertise and competentcy is soon to become non-existant.
"Kids" live up to their parents/employers/cultures lowest requirements and we are all just "kids", we are just older "kids".
Low requirements => low results and high risk.
Ok, OK, I have fell off my soap box and I'm done.
All; Seriously, we need to accept the information for the intent, learn from it, and if it isn't what we need or want to hear, ignore it.
02/27/2024 7:13 AM
Definition of an expert: A person carrying a briefcase that is at least from 50 miles away.
No one can be an expert in their own hometown.
Good Answers: 125
01/30/2013 9:47 AM
I am pretty sure that any flow meter listed for use in a fuel line will be rated for hazardous area installation.
It should be obvious that any electrical equipment installed around fuel should be rated.
Read NEC article 500. There is a well defined "area of inclusion" around and above that you must understand completely before you begin what might otherwise turn deadly.
01/30/2013 11:23 AM
I will attempt to answer OP's question, but I will keep my sarcasm down so I too don't get scolded by AP.
From reading the entire NFPA section on flammable liquid storage and handling (a year ago) I believe any room that there could be explosive vapors do to spill or leaks is classified as Class 1, Div 2 hazardous location. A room that normally contains explosive vapors is Class 1, Div 1.
So your answer would be yes, you need to stay Class 1, Div 2 compliant. Everything needs to be intrinsically safe.
01/30/2013 11:30 AM
Or, put the damn meter on the roof, where the question would be moot.
01/30/2013 11:37 AM
That goes with out saying, if you are trained in hazardous locations, you know it has to be intrinsically safe or mounted outside the area. He obviously is not trained in this area.
01/31/2013 4:59 PM
Ah, excellent answer - thinking outside the box (or room as the case may be).
Good Answers: 125
01/30/2013 12:26 PM
"Everything needs to be intrinsically safe"
That is not accurate.
The installation can be wired intrinsically safe, subject to those wiring parameters and proper IS barrier use.
The "as common" method is to use rigid steel conduit with 5 full threads engaged, explosion proof boxes, and seal-offs (poured) at the exit point from the hazardous area.
Many industrial sites where I work prefer this type of installation as they consider it more robust (I have no opinion on that point).
01/30/2013 12:44 PM
Ok, I should have used the term "explosion proof". I too have wired items in hazardous locations exactly as you described. In my defence though, if you don't know the definition of a hazardous location, you probably don't know the difference between IS and EP.
02/03/2013 12:07 AM
WJM FIRE,
The NEC 70 codes in Article 500 2011 always prevails here, but allows the use of the EU harmonized seals from HAWK which allows the cables/wires to be sealed and dismantled-saves time/materials and costs.
These seal fittings (see 501.7) have been used for more than 25+ years in Chemical and Oil rig systems (is a better seal) along with the new ISO eXe and XP boxes from Appleton, Crouse and Killark with EXE/XP vents when in an intrinsically safe Class I div II-III or the Zone 0-2 areas as laid out in NFPA 497 plus 496 for any pressurized vessels. Diesel has been classified as a combustible fluid when exposed to heat above 130°F and vapors arise from the PAH contents that do exist around 165°F and up (85-90°F exterior temp can lead to 145-165°F internal temp, especially if a large are space exists)
Use Zenia barriers/Isolation barriers as part of the wiring (Article 504) (Siemens, P&F, E&H or Crouse/AB) then you cannot got wrong. All meet NEC 70 -ATEX directives
One point: on Diesel fuels some to have flammable PAH additives in small amounts to assist ignition/combustion enhancements to ensure NOX/SOX reductions in the exhaust. Plus not all diesel is CLEAN diesel-can be corrupted (like NY had PCB's mixed in the fuel oils sold to homes and apartments for YEARS) and in winter they add Kerosene or Propane/Kerosene to stop gelling if the tank is not heated.
Lastly as I stated in my thread below (50), need the day tank BERMED.
Geoff Daly Nashua NH
Good Answers: 125
02/03/2013 10:36 AM
I had no idea that diesel was sometimes corrupted for residential sale.
Thanks for that info.
02/07/2013 10:49 AM
Wjmfire,
dilution and corruption of fuels has gone on for years and is not only Diesel type fuels. Recently in south America someone mixed waste contaminated oils used in cars, trucks and hydraulic systems into residential heating oil about 20 to 30 % by volume (all the stuff they mixed was free except for the transport/pick-up aspect) so they did not get a clean burn and many burners had to be constantly adjusted for the fuel/air ratio. Was eventually investigated/stopped when a major Hospital had a full burner failure and huge emissions from the stack - constant haze, NOX & SOX # off the chart; same occurred in NY in the 70's and 80's by some rogue fuel dealers with PCB's and other waste oils.
So any fuel area should conform to the highest standard within the NFPA 497 and NEC Article 500 for the maximum safety- does not add much cost, maybe $185.00 extra.
Australia - Member - New Member Engineering Fields - Mechanical Engineering - New Member Engineering Fields - Marine Engineering - New Member
Good Answers: 16
01/30/2013 11:11 PM
Greetings fellow Posters.
I see a lot of good information here and lots of useful standards alluded to and great terminology.
What I don't see is where the original poster is located and there is no indication of where in the world the diesel and day tank are. Surely that should be a major consideration as to what the appropriate standard should be?
I like sight glasses for day tanks. No moving parts, little to no maintenance required and like everything else it is only as safe as the plant operator.
BAB
Make it so.
01/31/2013 12:32 PM
Great, BlueAussieBoy,
Thanks for asking that very pertinent and fundamental question!
I too am here down under like yourself, in NZ though, and I have in front of me Standards AS/NZS 60079.10 and AS/NZS 60079.14 among others.
I was just trying to get a second expert opinion. Among all the replies I spotted a few that answered my basic doubt regardless of their geographical location.
Thanks.
Good Answers: 444
01/30/2013 11:24 PM
It seems odd that nobody has made the distinction between "flammable" and "combustible" liquids. Diesel fuel is a "combustible" liquid which means that it does not fall under NEC 500 which covers "flammable" liquids. Gasoline is a "flammable" liquid (as are its vapors) and requires Division 1 or 2 treatment depending upon the proximity to the source.
Q. How does the Code address diesel fuel dispensers as they relate to hazardous locations?
A. The hazardous Class I location requirements contained in Art. 514 only apply where a flammable liquid having a flash point below 100°F [Art. 100 Volatile Flammable Liquid] is stored, handled, or dispensed [514.3(B)]. The flash point of diesel fuel is 100°F or above; thus, the area involving diesel fuel is typically not a classified location. But if the conduit for the diesel dispenser passes through the Class I area around the gasoline dispenser, then the installation must comply with the sealing and wiring method requirements of Art. 501 ( Figure )..."
From http://ecmweb.com/qampa/code-quandaries-6
The answer to the OP's question is "No".
Good Answers: 125
01/31/2013 6:33 PM
You are exactly right.
With all of the off topic comments on this thread, my brain went to sleep. A good example of why engineering (for me at least) should not be exercised under distraction.
My brain said fuel and that was all I saw.
Diesel has a flash point of approximately 126 F and above, making it a non-issue here.
Even if atomized from a pinhole leak, an explosion won't occur, only fire.
GA from me.
01/30/2013 11:37 PM
In response to the general nonsense going on in this thread. I have had the misfortune of dealing with highly educated certified mechanical engineers who did not know how to operate a screwdriver! (fresh out of college) I have also been subjected to highly educated AND experienced mechanical engineers who specified on plans that a 6" pipe be routed through a 3" hole in a concrete wall. Worse, when same was questioned, they commented that "if I put it on the plan, that's the way it is!" We ended up drilling the hole out to size AFTER the concrete was cured. All nine feet of it, at a cost of thirteen thousand dollars! I have worked with guys who had more than 20 years of experience who had learned absolutely nothing new in all that time. And with guys who never graduated high-school that had 20 years of plant experience who could hold their own with any mechanical or electrical engineer. My point is this....we were all dumb once upon a time....some of us are determined to stay that way....some of us will do whatever it takes to learn something new. Degrees and certifications are nice and often required by law....buy they don't mean you know anything except how to pass a test, or pay the fees for a license, or maybe that you have a good friend in the right place. What says something about our ability in the end is how we behave professionally and how successful we are at executing our jobs and solving real world problems while keeping things as safe for everyone as is humanly possible. The old school was always based on intimidation, the master verses apprentice system who's names we still use. In the old days engineers had years to develop their skills and education was minimal. Now days an engineer gains most of their skills in college and often only has a couple of years to "hone" that knowledge into skills that work. There just isn't time for the old way anymore. There is too much to learn, too many disciplines for one person to master them all! The result is what we have now...and we have to deal with it. We know that these guys probably are neither educated or certified for what they are doing..they might be..who knows? But, what we do know is this; They will be doing the work, or they are doing the work NOW. We know that they are not going to stop just because we tell them to, or because we refuse to help them. So don't we have an obligation to at least TRY to insure that they do it right?
Good Answers: 7
01/31/2013 3:05 AM
ohhh full moon or something? chill people!
I would say that a diesel tank, diesel piping or anything associated with it is not a hazardous area. Certainly in offshore oil & gas it isn't, it's a utility.
Flowmeter? I would just go for a manual turbine one and just go and get a reading as often as you want. Why put a flowmeter in at all? A 'day tank' should be of a size where you can take a level gauge reading and then take another an hour or 3 later and work out the difference and the volume used for that period. Easy as long as it is a square tank or a vertical cylinder.
Good Answers: 117
01/31/2013 4:22 AM
off shore North Sea diesel is considered hazardous... FYI
Good Answers: 7
02/02/2013 11:00 PM
you might consider it hazardous but the operators, the MSDS and the Zoning classification doesnt.
Diesel isn't considered as flammable on a European MSDS, just 'harmful' and "Dangerous for the environment"
Zoning or hazardous area classifications offshore north sea are based on the probability and size of a gas release and the likelihood of ignition. They are governed by the DSEAR / ATEX 137 Regulations and there is no mention of diesel in there.
Sorry your wrong. Diesel isn't and has never been considered as a Hazardous process fluid offshore north sea and it doesnt make an area a Hazardous / zoned area.
01/31/2013 9:14 AM
First, to all of you "engineers" that get offended because someone asks a question, just remember that the person asking the question might only be some one at a lower level of a company with no technical backup, no engineering department to turn to for drawings or technical advice. To have the sense to ask a question about something you don't know should be commended not condemned.
Second, for all you "engineers" would respond with off the cuff comments, know what you are talking about, do your research, or keep your mouth shut.
Lastly, diesel fuel is not a FLAMMABLE fuel, DOES NOT emit hazardous vapors and is in fact a COMBUSTIBLE material. The facts and only the facts should be used in making a determination of hazard classification
01/31/2013 10:30 AM
There are conditions where diesel is considered flammable due to the surrounding environment. Engineered controls are utilized to keep this at a minimum but sometimes you have fuel in an environment that has parts of a fuel system exposed to temperatures above 150°F can cause even diesel to have vapors in sufficient quantities to flash.
Which is why it is important as many have suggested that an evaluation on site be conducted by their site safety personnel or competent persons.
(oh...and i support your first paragraph)
Drew K
01/31/2013 1:03 PM
Thanks for such sensible response, Daveset!
Good Answers: 25
02/03/2013 8:03 AM
I fully agree with you.
01/31/2013 12:29 PM
I don't know what legally comprises a "Hazardous Area" but I do have considerable experience with diesel fuel on my vessel.
Diesel fuel is impossible to ignite in liquid form. In fact, all combustibles must be in a vapor form to ignite (see: Flash Point [not to be confused with Ignition Point]) In a diesel engine fuel is sprayed into the cylinders in a fine mist into air that has been compressed so that it is above the Ignition Point.
I personally have sat inside my diesel fuel tanks with an inch or so of diesel oil in the bottom and a propane torch in my hand sweating copper fuel pipes together. Fuel on occasion was dripping from the pipes I was working on. The only time the fuel would burn was when I overheated a pipe. I simply blew out the flame and started over. If there had been a paper towel involved it would have been a wick which would have thinned out the oil so much so as to be easily vaporized and ignited but that couldn't happen because I didn't let it happen.
There has been an occasion when the need to operate with the engine room bilge filled with diesel oil arose. (and no, no oil went overboard!) This was not a problem as there was no way that fuel could have been ignited. Nothing could have heated any part of that fuel up to its Flash Point, nor was there any source of ignition. In due time the fuel storage problem was resolved and the fuel pumped back to its proper place.
As for your genset. I consider a consumption measuring device to be an unnecessary and unreliable gadget compared to sounding a tank with a tape measure. I measure the air space above the fuel, called the "Ullage" (the depth of the liquid in the tank is called the "Innage"), and consult a chart previously created to tell me how much fuel is in the tank. This is how it was done on oil tankers prior to radar gauging and is very reliable.
I am wondering: why do you have the day tank on the roof, what is the height between the genset and the day tank, where is the supply tank, how do you fill the day tank from the supply tank and how do you fill the supply tank?
95% of all diesel engine problems stem from failure to supply the engine with an adequate supply of clean fuel. There are several steps to prevent this problem
If a vessel loses its propulsion engine, say because heavy weather stirred up the water and glop in the bottom of the tank overwhelming the filters and stopping the engine, disaster could follow. (See: HMS Bounty sinking among many others) Therefore I have taken steps to prevent this from happening on my own vessel.
All tanks should have a way of removing foreign matter (water and glop) that settles to the bottom of the tank. A drain valve is obvious. This is how it is done on light aircraft. I would suggest a ball valve with plug and a conscientious maintenance program. Second best is to withdraw the fuel for use routinely from the very bottom of the tank, not an inch or three above the bottom as is commonly done which virtually guarantees collecting an inch or three of water and glop (asphaltenes) in the tank. Withdrawing the fuel from the very bottom will insure that ALL sinking debris, especially water, is removed from the tank and deposited in the filters with normal operation. The concept here is that your fuel tanks should contain nothing but fuel.
Also needed is an electric pump (I got mine from NAPA, a 7psi diesel Balkamp impulse pump) to draw fuel from the day tank to pressurize the system to check for leaks (a leak sucking in air during engine operation is impossible to find), to re-prime the system after changing filters, as well as compound gauges (15psi-0-15psi) downstream of each filter (primary and secondary) to determine the degree of plugging of each filter so one knows when to change them. Simply changing them on a regular basis is not enough.
Personally I would have the day tank in the genset room where I could deal with it, (check the level and drain the glop) mounted well above the genset engine for gravity feed the engine. Fuel lift pumps, the on-engine pump that supplies the injector pump, are a common point of failure.
Equip the supply tank with an electric pump (check out Gear Puppy)(switch at day tank) to refill the day tank as needed.
I am not convinced that the roof is a good place for a diesel tank. In the case of a fire a tank of diesel fuel on the roof makes a nifty source of accelerator.
The building insurance company might be a good source of information about how to make a safe system as they are familiar with failures and probably would not cover any damage to a building that didn't meet code; but they may not be so knowledgeable about ways to keep the genset operating reliably.
BTW, Mr Diesel's first name was Rudolph. He developed his engine using peanut oil, and he was very likely murdered while on an English Channel ferry.
Bandership
02/01/2013 8:21 AM
What does it matter the rating??? For even the worst scenario, Class I Div.1 the required installation is not much more expensive than what you will be doing for standard atmospheres.
You have one instrument, and apparently the controls in a non-hazardous area. You have a roof mount, so conduit is going to be used. Add the seals as required for Class I Div.1 and fill them with the new injectable epoxy. Covered. Cost above that for the conduit, assuming 1/2" rigid - about $125 or so and 1/2 hour more labor.
If you aren't sure where the seals are needed, just ask.
Only time it pays to fret over the ratings is when you have myriads of instruments and motors, with the control panel mounted there as well. Then the costs of being "overly safe" become possibly much more than required.
02/01/2013 12:14 PM
Wheel,
You ask a good question and is actually covered in the NFPA 497 and also within NFPA 70 Article 500.
If you follow the recommendations and ask your local NFPA rep and Fire Marshall to ensure you have interpreted the Code Articles correctly, you cannot go wrong with there advice/response-ensure it is in WRITING.
You should also ensure the area around the day tank is bermed and shrouded from rain; to take the FULL tank load if it spills and is fully sealed- need also a liquid sensor alarm in the berm-Turck make a nice one (to drain use an air-operated diaphragm pump, safer and EXP any way-plus place catchment pans under each hose connection with dry-spill powder or PIG rags to absorb leaks and dismantling of the hoses)
02/03/2013 12:38 AM
I'm just guessing here, but it sounds like you are trying to get a handle on diesel usage for accounting/reordering.
If that is the case, I suggest using an ultrasonic on the day tank. It won't give you a good instantaneous reading of fuel flow, but will give a good average usage rate. You will also have the ability to have (software) low and high alarm points.
If you have a decent historical trending package, that will give you information on daily through yearly usage patterns.
Just a thought...
02/07/2013 3:19 PM
Thanks for that suggestion, but only problem would be while the diesel engine is running at some stage the day tank will get filled by the fuel oil transfer pump automatically running to top up. This event will corrupt, distort and mislead ultrasonic's level readings of the day tank.
02/21/2024 3:21 AM
<...have to...>
Question the need for knowing the instantaneous flowrate of <...Diesel...> at any moment. Flowrate can be averaged by the change in level over time:
  • How about using a dipstick and a clock or a calendar?
  • The other way of doing it is to average the amount of <...Diesel...> fuel purchased over time from the purchase orders needed and records produced for replenishing the <...day tank...>.
  • How about adding a sight glass or magnetic follower type of level indicator to the side of the tank?
All of these techniques are intrinsically safe in the context of hazardous area electrical equipment. Other techniques may be had by making a simple telephone call to the <...Diesel...> fuel supplier, as this isn't exactly the proverbial "rocket science".
<...Diesel...> fuel is not known for needing hazardous area equipment, as its flashpoint is so high at ambient pressure. Its vapour in air will self-ignite if compressed, which raises both its temperature and pressure, which of course is the principle of operation of a compression-ignition engine.
02/27/2024 7:32 AM
Diesel vapors are heavier than air.The hazardous zone normally extends from approximately 4 feet above the source,and extends downward without limit.
If it is in an enclosed area,the whole enclosure is hazardous.All conduits leaving and entering must be sealed,including at the power source panel and all power and neutral conductors must be opened by a common circuit breaker.Installing a meter that requires a flange creates a possible leak scenario.I suggest using an ultrasonic flow meter which can be mounted externally without cutting the pipe.It works by detecting the deflection of the sound waves by flow.
Like an ultrasound medical device.
A typical example:Not cheap,but what price safety?
https://www.zoro.com/pce-instruments-ultrasonic-flow-meter-32-to-32-ms-pce-tds-100hsh/i/G104853882/
Register to Reply 60 comments
Anonymous Poster (4); bandership (1); BlueAussieBoy (1); brich (2); claritysable (1); Davesets (1); DogOfWar (1); Drew K (4); Drew85205 (1); Geoff Daly (3); HeHound (2); HiTekRedNek (2); hopalongcasualty (1); JPool (6); Kilowatt0 (1); lyn (7); PFR (1); Phys (3); PWSlack (2); RAMConsult (1); SHOCKHISCAN (1); suresh sharma (3); The.Tinkerer (4); wheel (3); WJMFIRE (4)