Unbalance Current in 3 Phase System

03/25/2013 12:07 AM

Hi

could someone please explain what happens to the unbalance current carried by the neutral conductor from a 3 phase switchboard with mulitple loads to a the 3 phase utility transformer( WYE connected secondary).

1. i would like to know what happens to the "unbalance current" in the neutral conductor?

thanks for answering

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#1

Re: Unbalance current in 3 phase system

03/25/2013 12:13 AM
Register to Reply Score 1 for Good Answer
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#2

Re: Unbalance current in 3 phase system

03/25/2013 1:26 AM

It goes wherever the neutral goes, which ordinarily is the star (wye) point of the transformer.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Participant

Join Date: Mar 2013
Posts: 4
#3
In reply to #2

Re: Unbalance current in 3 phase system

03/25/2013 2:19 AM

correct but what happens to the unbalance cuurent at the tansformer star point?

Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#4
In reply to #3

Re: Unbalance current in 3 phase system

03/25/2013 2:30 AM

It distributes itself into the windings and goes around again.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Participant

Join Date: Mar 2013
Posts: 4
#6
In reply to #4

Re: Unbalance current in 3 phase system

03/25/2013 3:07 AM

thanks for the reply. but the unbalance current can still be distributed at the load side instead of returning back to the source. Hence why there is a neutral conductor returning to the source. what i understand is that if the neutral conductor is not provided at the load side the unbalance current will flow from one phase to the other phases causing distortion in terms of voltage drop across and increase in current magnitude inthe phases. Thats is why the unbalance current gets passed to source via the neutral conductor.

Register to Reply Score 1 for Off Topic
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#7
In reply to #6

Re: Unbalance current in 3 phase system

03/25/2013 3:13 AM

You are completely confused.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply Score 1 for Good Answer
Member

Join Date: Feb 2012
Posts: 7
#11
In reply to #6

Re: Unbalance current in 3 phase system

03/25/2013 2:49 PM

If I understand your question well,there are two Different cases:

first case if this unbalance caused by open in one phase and another two phases are loaded then the current in one phase will flow in other phase and there is no zero sequence component to flow in the neutral

but if unbalance caused by phase to phase to earth, here zero seq. component will appear and you need neutral pass to source

Register to Reply
Anonymous Poster #1
#13
In reply to #6

Re: Unbalance current in 3 phase system

04/09/2013 6:11 AM

May be you must draw us a picture and show were is the neutral conductor

greetings

Register to Reply
Power-User

Join Date: Jun 2012
Posts: 115
#5

Re: Unbalance current in 3 phase system

03/25/2013 2:57 AM

If the unbalance current carried by the neutral conductor there will be Power loss,If it is exceeding 50% of line current means power line will be undergoing to overload trip.

Register to Reply Off Topic (Score 3)
Participant

Join Date: Mar 2013
Posts: 4
#8
In reply to #5

Re: Unbalance current in 3 phase system

03/25/2013 6:17 AM

sorry this is not what im asking for

Register to Reply Score 1 for Off Topic
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#9
In reply to #8

Re: Unbalance current in 3 phase system

03/25/2013 6:29 AM

If you are familiar with "phasor diagrams", you can draw a triangular outer diagram with a neutral anywhere within that triangle. When you connect up all the lines, the electrical phase angles will match the geometric angles in the diagram, and the voltages/currents will match the lengths of the lines.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#12
In reply to #5

Re: Unbalance current in 3 phase system

04/05/2013 6:21 AM

Nonsense.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Power-User

Join Date: Nov 2011
Posts: 171
Good Answers: 1
#10

Re: Unbalance current in 3 phase system

03/25/2013 7:42 AM
Register to Reply
Register to Reply 13 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); lyn (1); Muthuvel (1); nobodysomebody47 (1); Perth6000 (3); PWSlack (1); Tornado (4); wg (1)

Previous in Forum: What's the Meaning of Fast Phase Back?   Next in Forum: Earth to Neutral Voltage Safe Value

Advertisement