Anonymous Poster #1

Earth to Neutral Voltage Safe Value

03/25/2013 2:25 AM

Dear friends,

When there is no voltage between earth to neutral the system is said to be healthy.

But what is the allowable/acceptable limit for the voltage between earth and neutral.?

Is there any standards to support the acceptable limit.?

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Power-User

Join Date: Jun 2012
Posts: 115
#1

Re: Earth to neutral voltage safe value.

03/25/2013 2:43 AM

For Human safety concern voltage between neutral to ground should be less than 50 V.

It can be achieved only in the healthy balanced power system.

Reply Score 1 for Off Topic
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#2

Re: Earth to neutral voltage safe value.

03/25/2013 4:27 AM

The voltage in the neutral relative to the earth conductor is a function of the neutral current and the earth loop impedance, as has been indicated in this forum countless times before. For a 3-phase system that is perfectly balanced, the voltage difference will be zero, as there is no neutral current. However, the perfectly-balanced system is a hypothetical concept and rarely if ever achieved in practice.

If the voltage on the neutral conductor is perceived to be high, then increasing the area of the neutral conductor will help. British Standard 7671 gives full protocols for conductor sizing.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Guru
Engineering Fields - Mechanical Engineering - New Member

Join Date: May 2008
Location: CHENNAI, TAMIL NADU, INDIA.
Posts: 1851
Good Answers: 65
#3

Re: Earth to neutral voltage safe value.

03/25/2013 5:00 AM

Dear Friend,

Upto 2 Volts is VERY GOOD, 2 to 5 Volts is GOOD, 5 to 8 is OK.

Pl. refer ELECTRICAL ENGINEERING PORTAL. The above Values are taken from there.

DHAYANANDHAN.S

Reply
Reply to Forum Thread 3 comments
Copy to Clipboard

Users who posted comments:

dhayanandhan (1); Muthuvel (1); PWSlack (1)