HT Room No Ventilation

03/25/2013 5:33 AM

Hi, I'm doing maintanance of old school building and noticed in the HT room, there is no ventilation fan. HT room totally no air circulation too. Once check find out there is a window opening but it permanently sealed by glass about 15 year ago according to the one of the engineer(PE) instruction. Recently i had a audit and they questioning me about this but i do not have clear idea why HT room cannot be have air circulation. According to my knowledge must have air in & out window at least. I'm planing to propose to open up the closed window openings but just worried is it make any impact to the system. Any of you have experience about HT rooms can you share with me? Is it really necessary to seal the HT room without air circulation. Please take a note this school located near the sea. but rest all the room got ventilation. Thanks.

__________________
Improvement makes strait roads: but the crooked roads without Improvement are roads of Genius.
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#1

Re: HT room no ventilation

03/25/2013 5:38 AM

HT = ??

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Active Contributor

Join Date: Oct 2009
Posts: 16
#4
In reply to #1

Re: HT room no ventilation

03/25/2013 5:52 AM

HT means high trannsmission having range 132 to 400 KV

__________________
Improvement makes strait roads: but the crooked roads without Improvement are roads of Genius.
Register to Reply
Active Contributor

Join Date: Oct 2009
Posts: 16
#2

Re: HT room no ventilation

03/25/2013 5:48 AM

Sorry for short term. HT i'm referring to High voltage Transmission line

__________________
Improvement makes strait roads: but the crooked roads without Improvement are roads of Genius.
Register to Reply Off Topic (Score 5)
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#3

Re: HT room no ventilation

03/25/2013 5:51 AM

Go back to the Engineer that issued the instruction, and ask.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Active Contributor

Join Date: Oct 2009
Posts: 16
#5
In reply to #3

Re: HT room no ventilation

03/25/2013 5:58 AM

I'm just take over this place and frankly speaking i do not have much more experience. Thats why i'm looking for your opinions. i try to contact the engineer, closed this windows 15 years ago but his contacts no more in use.

__________________
Improvement makes strait roads: but the crooked roads without Improvement are roads of Genius.
Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#6

Re: HT room no ventilation

03/25/2013 6:01 AM

I think you need to describe your situation in more detail. Somewhere your HT must be transformed to LT; where does that happen? Is the transformer actually in the HT room, or does it have a separate room with only the infeed cables in the HT room? Or some other combination?

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Active Contributor

Join Date: Oct 2009
Posts: 16
#7
In reply to #6

Re: HT room no ventilation

03/25/2013 8:48 AM

Sorry for the less info. There is a transformer room beside the HT room.(Transformer room got well air circulation system with ventilation fans). HT room inside only switchboards. Below the HT room there is a cable chamber also.( infeed cables to transformer room)

HT room located ground floor.

Below the under ground cable chamber.

just beside the HT room is transformer room.

Do you think air floor in HT room causing any damage by humidity? Please take a note this HT room opposite is sea. its about 100m away.

__________________
Improvement makes strait roads: but the crooked roads without Improvement are roads of Genius.
Register to Reply
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#8

Re: HT Room No Ventilation

03/25/2013 3:52 PM

Hang on, are you saying you have a school building with a 132 to 400 KV indoor transformer on site?

Surely this transformer is not just for powering the school site (the normal procedure is to step the transmission level voltage down to a lower 11-33kV distribution level voltage at a substation).

Is this some sort of University with VERY high power requirements for test or research labs or something? Or perhaps the HT transformer feeds the old school and then loops out to feed the local area at the lower voltage also.

What's the transformer type, construction, output voltage and power rating?

Can you please provide more information (including country location, transformer details and even school details if possible) on this rather interesting nightmare (I mean application).

In the end the answer is likely in your local electrical and transmission transformer standards and codes, but they are country and application specific and what you describe is very uncommon from my point of view.

__________________
jack of all trades
Register to Reply
Commentator

Join Date: May 2011
Posts: 61
Good Answers: 1
#9

Re: HT Room No Ventilation

03/25/2013 11:57 PM

Last week a small Civic Cat entered in HT room of Electricity board. He found a path to enter inside the panel (through gap with cable entry). he want to warm herself as there was severing cold outside. But unfortunately she came in contact with live bus and the result was complete blackout for 12 hrs.

Now the ENGINEERS are busy to close/seal all openings to panels & HT room.

Believe me, it is a true story.

Register to Reply
Guru

Join Date: Feb 2012
Posts: 595
#11
In reply to #9

Re: HT Room No Ventilation

03/26/2013 5:53 AM

whats the fuss about cat havong a 12 h blackout

__________________
ci139
Register to Reply Score 1 for Off Topic
Guru

Join Date: Feb 2013
Posts: 2004
Good Answers: 31
#12
In reply to #11

Re: HT Room No Ventilation

03/26/2013 6:59 AM

I just put my cat out..................It was on fire!

Register to Reply
Guru

Join Date: Feb 2013
Posts: 2004
Good Answers: 31
#10

Re: HT Room No Ventilation

03/26/2013 2:24 AM

This may help you. Normally an HT room, (HT/HV-132kv and above, MV/MT 1kv to 132kV), is positive air pressured with air flow. So a flow in and a vent out. It helps to keep the room 'dust free', and free of fumes which may build up over time. The dust can cause a potential flash over of phases and tracking on conductors. Their would be a filter on each in flow and out flow. If you have cable trenches in the room, the air flow helps keep the trenches clear of any heavy gas which may, be present in the room. An air flow will also help keep the heating from the equipment down slightly. And before anyone jumps down my throat here, everytime a switch is operated or trippped out, gases will be present in the room and they need to be vented off. They usually end up in the trench or the lowest part of the room. If there are batteries present in the room, which there should not be, the ventilation will help keep the gases from the charging batteries at a minimum level. (Old school building!). But, you do need to calrify if you have HT or LV equipment in the room as well as any tranformers. I have doubts that in a school you have 132kV. Perhaps 11kV or lower transformed down to 440V, so please make sure you know what voltage you have. It is marked on the switchgear or transformer for easy reference. If you have LV, 440V, the room should still have some sort of ventilation and fliters to keep dust out the room. Hope this helps you.

Register to Reply
Commentator

Join Date: May 2011
Posts: 61
Good Answers: 1
#13

Re: HT Room No Ventilation

03/26/2013 8:52 AM

Actually my English is poor.

I mean to say that, based on our past experience, sometimes we keep all windows and ventilators closed to prevent entry of lizards, dove etc in the HT room.

Register to Reply
Guru

Join Date: Feb 2013
Posts: 2004
Good Answers: 31
#14
In reply to #13

Re: HT Room No Ventilation

03/26/2013 1:05 PM

In all honesty this is a simple issue to solve. Pull out the window, install an expanded metal mesh in a frame. The frame has a nylon 66 filter, about 50mm thick. Another expanded metal mesh is installed, sandwiching the filter material. Make a second one for the door of the switch room. Install rodent protection mesh on the switchgear, normally a fly screen type mesh. (around the cable entries and gland plates), or use a sheet metal to fill in the gaps around the cable entries. Rodent proofing is not new and not rocket science, neither is installing a vent system for HV/LV rooms. Even use acrylic, bakelite sheeting if need be to rodent proof the gear. It works in Africa, I see no reason it wont work where you may be. If it wants in, it will get in and it will cook, no matter what you do. Try having a large bird fly over, and close to your OH Lines and see what happens to it when it craps mid-flight, between phases. The last thing going through its mind is indeed, its arse. You still have not stated your whereabouts nor actual voltage you are working with. If in doubt, employ me. Cheers.

Register to Reply Score 1 for Good Answer
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#15

Re: HT Room No Ventilation

03/26/2013 5:38 PM

Everything is relative. HT is short for High Tension, not Transmission, because "tension" is a literal translation to English of the term for "voltage" in some languages.

In same said countries, "High" with regards to voltage is also not the same as the IEEEE definition of "High Voltage". In general, the use of the term "HT" with regards to switchgear and motors etc. in places that regularly use that term is what the rest of us refer to as "Medium Voltage", meaning above 1000V and below 100kV. This is most likely 3.3kV switchgear.

Without knowing the original justification for sealing the windows, it is not necessarily a good idea to introduce outside unconditioned air to MV switchgear rooms. You will also introduce humidity and the possible deadly combination of high humidity, cold air and warm bus bars, which can cause flash-over.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Guru

Join Date: Feb 2011
Posts: 7025
Good Answers: 207
#16

Re: HT Room No Ventilation

03/27/2013 8:46 PM

I must know this room by a different name..........ht??

Register to Reply
Register to Reply 16 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

ci139 (1); Fredski (1); hasantha84 (4); IQ (3); jack of all trades (1); JRaef (1); PWSlack (1); satendrakumart (2); Tornado (2)

Previous in Forum: Emergency Stop Circuit at a Diesel/Petrol Service Station   Next in Forum: ETAP 7.0

Advertisement