Drain Pipe Line Routing

04/05/2013 4:36 AM

Dear CR4 members Can you please advise whether drain line (flow by gravity) has to run straight or i can run the line with bends?? Note this line is for sewer water treatment plant. Thanks

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Drain pipe line routing

04/05/2013 4:40 AM

This pipe has bends:

and will need more bends to connect it to the sewage treatment works.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Commentator

Join Date: Sep 2009
Location: Bahrain
Posts: 62
#2
In reply to #1

Re: Drain pipe line routing

04/05/2013 4:59 AM

'PWSlack' I fully agree with you but i presume that static head is the deciding factor here. But i cannot find out this relation between min static head required for x numbers of bends in the drain line.

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#3
In reply to #2

Re: Drain pipe line routing

04/05/2013 5:06 AM

As drain lines never run full, the concept of a static head for the number of bends is meaningless.

One needs to ensure a fall between the source and the destination. There is a minimum gradient for the invert of the pipe. If bends are needed, as they usually are, then so be it.

Is this a case of a Civil Engineering installation being over-specified by a Process Engineer?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#4

Re: Drain pipe line routing

04/05/2013 5:48 AM

Provided correct grade is maintained, there is no particular limit on the number of bends. They should be "sweep" elbows rather than sharp turns; or 45° elbows.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Commentator

Join Date: Sep 2009
Location: Bahrain
Posts: 62
#5

Re: Drain pipe line routing

04/05/2013 6:41 AM

Do i need to provide a concrete pit where there will be change in the drain line direction? and what is the standard pit size in case we need access for maintenance?

Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#6
In reply to #5

Re: Drain pipe line routing

04/05/2013 6:53 AM

No.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Power-User

Join Date: Jul 2010
Location: Virginia, USA
Posts: 227
Good Answers: 4
#16
In reply to #6

Re: Drain pipe line routing

04/06/2013 1:38 PM

Depends on local codes. In New York City, Every time a sewer changed direction, a manhole was required. (This was 1980, it may have changed since then.)

__________________
Robert A. Heinlein (1907-1988) "There is no worse tyranny than to force a man to pay for what he does not want merely because you think it would be good for him."
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#7
In reply to #5

Re: Drain pipe line routing

04/05/2013 7:04 AM

...because that is where the flow will slow-up leading to deposition of suspended solids, which is exactly what is not wanted.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
2
Guru
Engineering Fields - Mechanical Engineering -

Join Date: Sep 2009
Posts: 1651
Good Answers: 71
#8

Re: Drain Pipe Line Routing

04/05/2013 9:54 AM

What size line are you talking about?

As described below, this is considered open channel flow. When considering solids in your flow the most important things are rate of flow, volumetric flow and the slope of the pipe. Sweeping bends are necessary to prevent the solids from being left behind the flow. The slope cannot be excessively steep or shallow.

If you are working on a city sewage that has pretty much constant flow from the numerous houses you can get away with a steeper slope because of the near constant flow that will keep solids moving (they tend to drag and fall behind the liquids). If you are working on a home sewage line, it is actually more critical to get the precise slope. When I was a young man working on new construction we installed our pipes using a spirit level that was marked at 1/4 bubble and that is the slope we used, I am certain that you can find the value of that slope with a quick google.

For city sewage systems, many of the manholes cover a large concrete chamber that has a channel cut into the bottom with sloped sides. This allows some area for water and solids to accumulate and develope some head pressure if there is a blockage or just excessive flow. Once the water rises high enough it will push the blockage or increase flow until it is sufficent to prevent backup. These manholes also provide a place to insert tools to clear blockages or perform inspections.

My best advice would be to get a civil engineer to have a look at your system so you don't engineer in something that will cost you later...pay now or gamble to pay nothing or more later...just think about how much a problem will cost in the future.

Drew K

__________________
Question: What is going on with the American's Government? Response: Who is John Galt?
Register to Reply Good Answer (Score 2)
Guru

Join Date: Feb 2009
Location: West Coxsackie, NY
Posts: 533
Good Answers: 10
#9

Re: Drain Pipe Line Routing

04/05/2013 10:24 PM

As long as it has 1/8" per foot drop in elevation you can have as many twists and turns as you need as long as it is properly vented. All Sh$t will continue downhill to the treatment plant or septic tank.

__________________
"Real Bass Players" do not use picks
Register to Reply
Guru
Safety - Hazmat - New Member Engineering Fields - Retired Engineers / Mentors - New Member Engineering Fields - Piping Design Engineering - New Member Hobbies - DIY Welding - New Member Fans of Old Computers - PDP 11 - New Member

Join Date: Feb 2007
Location: Stronger Than The Storm
Posts: 2394
Good Answers: 203
#18
In reply to #9

Re: Drain Pipe Line Routing

04/07/2013 10:16 AM

In most of the USA a pitch of 1/4" per foot of run is required for for drain (sewer) lines. This is to maintain a minimum velocity of the fluid/solids and as previously stated by others, keep things moving. An easy way to install piping at this pitch is to take a 9" torpedo level and tape a #10 (dia. of approx. 3/16") machine screw to the bottom of one end or a 1/2" piece of wood to one end of a 2-foot level. By putting the raised end of the level on the down-stream direction of the pipe you simply pitch the pipe until the level indicates the bubble is in the level state. This is much easier than having to "think too much" each time the pitch is check or an another section of pipe is installed.

I have used this method (taught to me by my father, who felt that "laziness was the mother of invention") for many years and have taught it to many plumbers and pipe-fitters, all of whom adopted this method because of its ease.

Good Luck, Old Salt

__________________
Any day on the green side of the grass is a GREAT DAY!, --- me +++++++++. I believe creativity is an inherent part of everyone. --- Kermit T. Frog
Register to Reply
Commentator

Join Date: May 2012
Location: Sutter buttes - East 50 miles you found me
Posts: 59
Good Answers: 3
#10

Re: Drain Pipe Line Routing

04/05/2013 10:27 PM

Always remember turds float. Maintain a 1/4 inch to the foot down hill grade and the turds will float the bends with a minimal static head push.

__________________
Lurking Always Lurking.........................in the Shadows
Register to Reply
Commentator

Join Date: Oct 2012
Posts: 75
Good Answers: 7
#11

Re: Drain Pipe Line Routing

04/05/2013 11:31 PM

Now you learn something new every day, Americans don't use simple ratios for fall.

1:50 Fall in the pipe.

No pockets.

As many bends as you like as long as you put in plenty of rodding points or inspection chambers (pits) I would want to have a minimum of one rodding point/inspection chamber for every 3 bends. Hard to get a drain rod round anymore than 3 and hard to get a retrojet hose back after anymore than 3 bends.

Register to Reply
Power-User

Join Date: Feb 2008
Location: Cleveland, OH
Posts: 135
Good Answers: 6
#12

Re: Drain Pipe Line Routing

04/06/2013 4:46 AM

I don't know if have something similar to this in Bahrain:

http://10statesstandards.com/wastewaterstandards.html

but it might be a good reference point.

__________________
If you want to know what God thinks of money, just look at the people he gave it to. - Dorothy Parker
Register to Reply
Commentator

Join Date: Sep 2009
Location: Bahrain
Posts: 62
#13
In reply to #12

Re: Drain Pipe Line Routing

04/06/2013 5:24 AM

Thanks alot for the reference you have posted. It has some good info that might help. The reference states different slope of of sewer line sizes starting from 8 inch. In my case the line is smaller it is 6 inch, i may assume that slope i need will be not more than 0.4 which is min for 8 inch.

Register to Reply
Commentator

Join Date: Oct 2012
Location: Located in South eastern North Carolina, I am a retired Supt of Public Works. also I am wheelchair confined due to an INdustrial accident of the Bends (Caissone Disease) from a construction Diver/underwater mechanic.
Posts: 64
Good Answers: 2
#14

Re: Drain Pipe Line Routing

04/06/2013 9:09 AM

You will never regret using the 10 States Standards, as was presented to you, when constructing a municipal like system and Treatment Plant.

Register to Reply
Guru

Join Date: Apr 2006
Location: Cincinnati, Ohio, USA
Posts: 662
Good Answers: 49
#15

Re: Drain Pipe Line Routing

04/06/2013 9:32 AM

One item not yet mentioned is the need for reasonably spaced clean-outs, especially at all bends.

Due to "normal" limits on equipment, clean-outs should be spaced no more than about 75-80 feet (25 meters).

Obviously, if the change in direction occurs at a manhole, you have the clean-out.

__________________
NO MATTER HOW WELL YOU HAVE DONE SO FAR, ALWAYS TRY TO BE BETTER TOMORROW.
Register to Reply
Guru
Hobbies - DIY Welding - New Member Hobbies - Target Shooting - New Member Engineering Fields - Civil Engineering - New Member United States - Member - New Member

Join Date: May 2009
Location: Red Hook, New York (Mid-Hudson River Valley)
Posts: 4362
Good Answers: 179
#17

Re: Drain Pipe Line Routing

04/06/2013 7:25 PM

It's been my experience designing WWTP's (pursuant to USEPA, NYSDEC, and 10-State Standards), that whenever you have gravity sewer line or waste line that makes a directional turn that you should provide a manhole of some type that features a concrete trough and side benches. The minimum depth of the concrete trough must be 0.80 x the pipe diameter. the side benches must have a minimum 2" per foot slope from the interior manhole wall to toward the trough so that they drain adequately.

The reason why is quite simple: Sludge and other debris sometimes accumulates in the pipeline and you need to provide an easy enough access point to rout or pressure flush the line in order to clean it. Providing a cleanout along the line just won't do because you need to visually verify that the maintenance work was sufficiently done.

__________________
"Veni, Vidi, Vici"; hendiatris attributed to Gaius Julius Caesar, 47 B.C.
Register to Reply
Register to Reply 18 comments

Good Answers:

These comments received enough positive votes to make them "good answers".
Copy to Clipboard

Users who posted comments:

bluebelly (1); Bob Sullivan (1); CaptMoosie (1); d_m_rosenberg (1); Drew K (1); energygod (1); HeHound (1); Jimh77 (1); old salt (1); power engine (3); PWSlack (3); The Shadow (1); Tornado (2)

Previous in Forum: SAE Equivalent Steel   Next in Forum: Oddball Thread Designation

Advertisement