Circuit Breaker Selection

04/09/2013 9:42 PM

After getting the value for the short circuit current for a certai single line diagram, what is the next step in order to choose the appropriate circuit breaker for a certain load feeder?

for example: i want to select a circuit breaker for a load feeder where i calculated the Max Isc = 30 KA. What are the correct ratings of the CB to protect that load? What are the other factors that i should take into account when selecting the right CB??

__________________
vandie
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#1

Re: Circuit breaker selection

04/09/2013 9:59 PM

It depends on your local electrical regulations, and is likely to be something along the lines of FLC of all loads on the feeder plus 1.5 times the FLC of the largest motor.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply Score 1 for Good Answer
Associate

Join Date: Mar 2013
Posts: 39
#2
In reply to #1

Re: Circuit breaker selection

04/10/2013 12:10 AM

To be clear, can you give an example? what is the specific parameter to look in a CB for this purpose? (Icu, Ics, Icw, etc..)

__________________
vandie
Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#4
In reply to #2

Re: Circuit breaker selection

04/10/2013 3:41 AM

The nominal rating of a CB should be somewhat larger than the current it will normally handle, and will allow for the brief starting current of motors. The formula I gave is based on the United States National Electrical Code; your local regulations may differ somewhat.

In addition to the nominal rating, a CB or fuse has a maximum interrupting rating, such as 10kA, 22kA, 50kA, etc. In the event of a large fault, the CB/fuse must be able to successfully interrupt this large current, which is different from the nominal rating.

You can search the Web or IEC literature for the meanings of Icu, Ics, Icw, etc.... Many of these numbers will be fairly close to each other.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply Score 1 for Good Answer
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#3
In reply to #1

Re: Circuit breaker selection

04/10/2013 3:30 AM

That was perfectly on topic. What worthless idiot voted otherwise?

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply Score 1 for Off Topic
Guru

Join Date: Mar 2011
Location: Sebastopol, California
Posts: 1205
Good Answers: 54
#7
In reply to #3

Re: Circuit breaker selection

04/10/2013 11:20 PM

It was probably somebody's cat, don't sweat it.

__________________
Most people are mostly good most of the time.
Register to Reply Off Topic (Score 6)
Guru

Join Date: Jul 2006
Location: CA (Central Arkansas, USA)
Posts: 599
Good Answers: 10
#12
In reply to #3

Re: Circuit breaker selection

04/11/2013 12:41 PM

It was off topic because you gave the answer. You were supposted to do the whole homework page for him. -- JHF PS GA!

__________________
If it's too good to be true, it probably isn't
Register to Reply Score 1 for Good Answer
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#5

Re: Circuit breaker selection

04/10/2013 3:42 AM

The next step is to get a copy of British Standard 7671, and digest and apply the contents.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
2
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#6

Re: Circuit Breaker Selection

04/10/2013 9:38 AM

Circuit Breaker Selection parameters:

i) Rated Operational Voltage

ii) Rated Insulation Withstand Voltage

iii) Rated Impulse Withstand Voltage

iv) Rated Operational Current

v) Rated Ultimate Short Circuit Breaking Current

vi) Rated Service Short Circuit Breaking Current

vii) Rated Short Circuit Making Current

viii) Rated Short Time Withstand Current

ix) Utilisation Category

x) Discrimination

Register to Reply Good Answer (Score 2)
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#8
In reply to #6

Re: Circuit Breaker Selection

04/11/2013 5:53 AM

Rated operational current to be calculated properly considering the type of load (continuous, fluctuating,periodical,duty-AC1,2,3 etc and S1,S2,S3 etc)

__________________
pnaban
Register to Reply Score 1 for Good Answer
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#9
In reply to #8

Re: Circuit Breaker Selection

04/11/2013 6:05 AM

Vide IEc 60947-2, for circuit breakers, the rated operational current (In) should be equal to the rated uniterrupted current (Iu) which again should be equal to the rated free air thermal current (Ith). The Standard does not specify anything about Utilisation Categories like AC1, AC2, AC3, etc. for circuit breakers. They are applicable for contactors only.

Register to Reply Score 1 for Good Answer
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#10
In reply to #9

Re: Circuit Breaker Selection

04/11/2013 6:56 AM

The number of times/frequency of switching on/off,time interval between them,duration, reversing,loads like elevator(lift) increases the current/heat generated in the CB,which will influence its rated current.

__________________
pnaban
Register to Reply Score 1 for Good Answer
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#11
In reply to #10

Re: Circuit Breaker Selection

04/11/2013 7:46 AM

The frequency of swithing, the electrical life and the mechanical life are given as Standard for the given breaker in the manufacturers' catalogues. And, the CB current rating does not vary much on these parameters.

For reversing loads like elevators, contactors are normally employed with AC-4 Utilisation Category ratings. It is highly unlikely that one would go for a circuit breaker for reversing motor applications.

Register to Reply Score 1 for Good Answer
Associate

Join Date: Mar 2013
Posts: 39
#13
In reply to #6

Re: Circuit Breaker Selection

04/14/2013 10:14 PM

Am I correct to say, that the CB ratings selection is based upon these circuit parameters:

a) Maximum and minimum momentary (first cycle) single- and three-phase short-circuit current.

b) Maximum and minimum interrupting duty (1.5 cycles to 8 cycles) three-phase short circuit current.

c) Maximum and minimum 30-cycle three-phase short-circuit current.

d) Maximum and minimum ground-fault current.

Is it the Icu (Rated Ultimate Short Circuit Breaking Current) or the Ics (Rated Service Short Circuit Breaking Current) of the CB that should be higher than the max momentary three-phase short circuit ?

And the rated operational current and voltage of the CB (Ie & Ue) should be higher than the rated operational current and voltage of the circuit within which the CB is to be placed? please correct me if i'm wrong..

__________________
vandie
Register to Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#14
In reply to #13

Re: Circuit Breaker Selection

04/14/2013 11:23 PM

Pl. note my comments itemwise:

a) This is to be checked with the rated short circuit making capacity or short circuitmaking current of the CB. The capacity of the CB shall be more than actual, obviously.

b) This is to be checked with the rated short circuit breaking capacity (either ultimate or service) of the CB. Again, the CB capacity shall be more than actual.

c) This is to be checked with the rated short time withstand current of the CB. The CB has to withstand carrying the maximum aniticipated short circuit current for the maximum anticipated duration.

d) If the source is a transformer with the LV system neutral solidly grounded, then the single-line-to-ground fault current would be equal to the initial symmetrical three phase short circuit current, which however, the CB is designed to break. In any other method of earthing, the earth fault current would only be lesser; hence, the CB would very well break such ground fault currents comfortably.

In case the source is a generator, then maybe, if the fault is very close to the generator and if the neutral is solidly grounded, the single-line-to-ground fault current may exceed the three phase fault current. A detailed analysis is needed in such cases.

e) The duty cycle for Icu is O-t-CO and for Ics is O-t-CO-t-CO; as can be seen if you want more life then have Ics more than the three phase short circuit current. Else, have Icu more. Choice is yours.

Hope the above is clear.

Register to Reply Score 1 for Good Answer
Associate

Join Date: Mar 2013
Posts: 39
#15
In reply to #14

Re: Circuit Breaker Selection

04/15/2013 3:12 AM

Thank you for the clear explanation. Do you have any reference for this, so that i can cite it based on your reference...?

__________________
vandie
Register to Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#16
In reply to #15

Re: Circuit Breaker Selection

04/15/2013 3:16 AM

IEC 60947-2

Register to Reply
Associate

Join Date: Mar 2013
Posts: 39
#17
In reply to #16

Re: Circuit Breaker Selection

04/15/2013 3:49 AM

Thanks again for your help.

__________________
vandie
Register to Reply
Register to Reply 17 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard