Secondary Y-ph Earthing of Potential Transformer

04/17/2013 4:30 PM

It is a long unsolved question in my mind,hoping that I will get the answer here.

The secondary Y-ph of 11Kv/110v potential transformer is earthed after the fuse as per the drawing by M/s Siemens.But the star is not gruonded.Why it is so.?

Thanks.

__________________
"Know something about everything and everything about something"
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#1

Re: Secondary Y-ph Earthing of Potential Transformer

04/17/2013 7:20 PM

Something sounds inconsistent about this. There are such things as "corner grounded" configurations, but I'm unsure why there would be a fuse in the grounded phase.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply Score 1 for Good Answer
Guru

Join Date: Feb 2010
Posts: 1013
Good Answers: 36
#2

Re: Secondary Y-ph Earthing of Potential Transformer

04/18/2013 5:36 AM

In addition to #1,

The Why: because, if the star point is grounded, with the Y-phase also grounded, you will get a short circuit through the ground !

Register to Reply Score 1 for Good Answer
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#3

Re: Secondary Y-ph Earthing of Potential Transformer

04/18/2013 6:44 AM

Er, because the drawing is wrong?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#4

Re: Secondary Y-ph Earthing of Potential Transformer

04/18/2013 7:35 AM

Mr. Giri, try the Instrument Transformers - A Reference Manual by Kappa Electric.

Register to Reply
Power-User

Join Date: May 2009
Location: Some where on Earth !!!.
Posts: 243
Good Answers: 2
#5

Re: Secondary Y-ph Earthing of Potential Transformer

04/18/2013 9:00 AM

For clarity,the picture is posted here with the grounded part part is clouded.

Mistakenly I have written that ground is given after the fuse.Its actually before the secondary side MCB.

Pls help!!!

__________________
"Know something about everything and everything about something"
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#6
In reply to #5

Re: Secondary Y-ph Earthing of Potential Transformer

04/18/2013 10:08 AM

Does this drawing depict accurately the actual installation at site?

Has the question been asked of the individuals and organisation that produced it?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Power-User

Join Date: May 2009
Location: Some where on Earth !!!.
Posts: 243
Good Answers: 2
#7
In reply to #6

Re: Secondary Y-ph Earthing of Potential Transformer

04/18/2013 1:48 PM

Dear PWSlack...I didn't get the answer from any corner,neither able to ask the manufacturer.So thought of getting help here.:)

__________________
"Know something about everything and everything about something"
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#8
In reply to #7

Re: Secondary Y-ph Earthing of Potential Transformer

04/19/2013 4:15 AM

Does this drawing depict accurately the actual installation at site? Please check, then answer either yes or no, as either response will enable the forum to help with the query appropriately.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Power-User

Join Date: May 2009
Location: Some where on Earth !!!.
Posts: 243
Good Answers: 2
#9
In reply to #8

Re: Secondary Y-ph Earthing of Potential Transformer

04/20/2013 10:04 PM

The actual wiring can only be checked during the panel shutdown,by drawing out the PT module.This kind of wiring is shown in HT & LT panels.If anybody aware of this pls help...

__________________
"Know something about everything and everything about something"
Register to Reply
Power-User

Join Date: Jun 2010
Location: Kolkata, West Bengal, India
Posts: 172
Good Answers: 1
#10
In reply to #9

Re: Secondary Y-ph Earthing of Potential Transformer

04/22/2013 8:09 AM

Dear,

Giri,

Usually, Y-phase of the secondary side is grounded(intentional ground) and copper link(not fuse) is used.In case of any earth fault in the secondary circuit of the of the PT, the short circuit current flows thro' the circuit , completed the current loop thro' the two ground points(one in Y-phase and other grounded point) and blowing up the fuse to protect the PT.

Thanks,

Manindra.

__________________
Manindra
Register to Reply
Power-User

Join Date: May 2009
Location: Some where on Earth !!!.
Posts: 243
Good Answers: 2
#11
In reply to #10

Re: Secondary Y-ph Earthing of Potential Transformer

05/04/2013 6:45 AM

Dear Manindra,

What I am not able to understand is that ,if we ground any phase directly,the protection equipment will trip/must trip,in this case its primary side fuse.(HT fuse).why this is not happening.

The above answer by you doesnt solve my question fully.

(No,its not grounded after fuse.I wrongly told this.Primary side fuse provided.Secondary side MCB provided & the grounding is provided at secondary before MCB)

Thanks for your interest though:)

__________________
"Know something about everything and everything about something"
Register to Reply
Participant

Join Date: Jun 2013
Posts: 1
#12

Re: Secondary Y-ph Earthing of Potential Transformer

06/01/2013 5:46 AM

Unfortunately I don't have the answer to your query, but am writing this to confirm your observation. In some of our installations which are more than 40 years old, 110V PT secondary is connected like this. Y-ph is solidly earthed and neutral kept floating. I am also confused about this. This seems to be the old practice as I see the same configuration repeating in panels supplied by Brown Boveri and Reyrolle.

Newer panels come with neutral grounded pt secondary.

Register to Reply
Power-User

Join Date: Jun 2010
Location: Kolkata, West Bengal, India
Posts: 172
Good Answers: 1
#13
In reply to #12

Re: Secondary Y-ph Earthing of Potential Transformer

06/06/2013 5:50 AM

In old installation, in various panels, instead of neutral point earthing of secondary of P.T., Y-Phase( middlle phase) is earthed (intentional earth ), so that, in case of any earth fault in secondary circuit, fuse provided in the secondary circuit(in other two phases of P.T.) is blown off to protect the circuit and various instruments connected in the secondary circuit.

Manindra.

__________________
Manindra
Register to Reply
Register to Reply 13 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

electricalexpert65 (1); giri (4); LAA_Lucke (1); manindra (2); PWSlack (3); sajkumar (1); Tornado (1)

Previous in Forum: Forklift Operators Get Static Shock at Elevator Pendant   Next in Forum: Earthing Electrode No. Calculation

Advertisement