Inrush Current Carrying Capacity of Cable

04/18/2013 7:56 AM

Dear All

At the starting time of motor it will draw 3-6 times of full load current for certain time period hope all of you know that.Weather the cable can able to withstand that Inrush current for that certain time period?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Inrush current carrying capacity of cable

04/18/2013 8:08 AM

The answer is either yes or no. If it is over- or correctly-sized, the answer is yes. If it is under-sized, then the answer is no.

The protocol for cable sizing for all eventualities is given, once again, in good ol' British Standard 7671, the repetition of which reminder is somewhat tiresome.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Anonymous Poster #1
#2

Re: Inrush Current Carrying Capacity of Cable

04/18/2013 8:24 AM

Weather Whether

Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#3

Re: Inrush Current Carrying Capacity of Cable

04/18/2013 8:50 AM

YES.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#4

Re: Inrush Current Carrying Capacity of Cable

04/18/2013 8:54 AM

...otherwise it isn't a cable; it's a fuse.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#5

Re: Inrush Current Carrying Capacity of Cable

04/18/2013 3:38 PM

Given the information provided (no current, not time, no cable size, no cable length, no cable type, no installation information to calculate de-rating factors, no country of origin to reference local electrical standards,) my crystal ball says no.

Your a graduated Electrical Engineer (you say) and you cannot work this out or even post a question that has at least some information in it to allow someone else to give you an answer?

What did you study, Microprocessors or something?

Were you not taught during your education how to go and find the answers yourself? Books, internet, cable manufacturer websites, a simple internet search, self-learning?

You are NOT going to get a design engineer job in the oil and gas industry if you are asking questions like this. I wouldn't give you a job with peoples lives on the line based on your design decisions.

Take all this as an instructive prompt that you should perhaps re-evaluate your career and look into furthering your education and knowledge, be it self-learning (not asking us to hold your hand and teach you by the way) or an additional (and perhaps more practical) electrical course.

Jack - An actual Design Engineer working in the oil and gas industry (among other things)

__________________
jack of all trades
Register to Reply Score 1 for Off Topic
2
Guru

Join Date: Oct 2012
Location: 100 miles North from the World Center
Posts: 879
Good Answers: 42
#6

Re: Inrush Current Carrying Capacity of Cable

04/19/2013 4:05 AM

I agree with jack of all trades, of course. Let's take an example:

Allowable Ampacities of a cable -of 3*250 MCM; copper conductor; 90 dgr.C insulation; 30 dgr.C ambient- according to NEC Table 10.15(B)(16) it is 290 A.

If a motor of 290 A rated will start DOL- start current 8*Irated for 10 sec- the cable conductor will reach 89-84 dgr.C in three consecutive starts [no cooling] first start

from ambient [30dgrC.] (89 dgr.C calculated as adiabatic phenomenon and 83 dgr.C taking into consideration heat evacuation).

Formulae:

TF=TI+J^2*ts*(2TI+2*Ko)/(KR-J^2*ts) adiabatic [See: IEC 60076-5 4.1.5 Calculation of temperature θ1]. And for heat evacuated:

Tc(t)=Tc(0)+[Tc(f)-Tc(0)]*(1-exp(-t/K) eq.4-23 from:

EPRI- POWER PLANT ELECTRICAL REFERENCE SERIES VOL.4 Evaluation of Conductor Temperature under Transient Conditions.

K=0.5-4 hr. [I took K=0.6 hr.].

If the conductor temperature will be 90 dgr.C [rated] at start, the final temperature after first start will be 122-126 dgr.C [no second start permitted!]

Permissible temperature for short-time[Emerging Rating] is 140 dgr.C.[XLPE for instance].

__________________
Julius
Register to Reply Good Answer (Score 2)
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#7
In reply to #6

Re: Inrush Current Carrying Capacity of Cable

04/19/2013 4:12 AM

GA. This is the sort of stuff to be found in BS7671.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#8

Re: Inrush Current Carrying Capacity of Cable

04/19/2013 4:28 AM

Oops! It has - time and again - been mentioned in this forum - by experts, that there is a huge difference between the starting current and the (magnetising) inrush current in motors.

The magnetising inrush current is necessary for excitation of the motor core & its magnitude can be as high as 10 to 12 times the rated motor current. And, its duration would typically be about 10 to 100 milli-seconds only (more for larger motors). Whereas, the starting current is the current required to accelerate the connected load from zero speed to rated speed,. Its magnitude would be between 5 to 8 times the rated motor current (when started direct-on-line). Its duration would depend upon the inertia of the motor's rotor and that of the driven equipment. It may vary from about 4 milliseconds for a small centrifugal pump to about 30 to 40 seconds for centrifugal blowers.

Now, coming to the short time withstand capacity of cables to tolerate this high current (either starting current or even the magnetising inrush current), the same may be verified by the adiabatic equation:

K2S2 = I2t

where

K = Adiabatic Constant, depends upon the conductor & the insulation of the cable

S = Cross sectional area of the cable conductor, in sq.mm

I = Current, in Amps

t = Duration, in seconds

Now, for your expected high current, for the given cable, you may very well verify the withstand time.

Hope the above is clear!

Register to Reply
Guru

Join Date: Oct 2012
Location: 100 miles North from the World Center
Posts: 879
Good Answers: 42
#9

Re: Inrush Current Carrying Capacity of Cable

04/20/2013 11:49 PM

Almost I forgot it:

See also:

IEEE-242/2001

Ch.9.5 Overload protection of cables

__________________
Julius
Register to Reply
Member

Join Date: Jul 2012
Location: Hanoi, Vietnam
Posts: 7
#10
In reply to #9

Re: Inrush Current Carrying Capacity of Cable

03/01/2014 3:56 AM

Dear 7anoter4!

Can u please shared to me IEEE std 242-2001 file. I'm looking for this std on internet long time but difficulty to get it.

Now i'm working in Mong duong II power plant project (located in Vietnam), in-charge protection relay system. So i need this file for studying.

If you're possible, please send to me via email address: dinhbka51@gmail.com

Thanks a lot!

Register to Reply Score 1 for Off Topic
Register to Reply 10 comments