High Leakage Transformer

04/21/2013 12:25 AM

For high leakage transformer:

If the secondary coil will be short-circuited , then the flux in the portion of the core under the secondary will be nearly zero.

Can some one confirm the above statment !!

How come zero flux under a coil carrying a short circuited current ???

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Power-User

Join Date: Jun 2009
Posts: 134
Good Answers: 11
#1

Re: High Leakage Transformer .

04/21/2013 12:49 AM

Not true.
If the secondary is short circuited, there will be current in the secondary and in most cases, the magnitude of the flux caused by the current in the secondary will be only slightly less than the magnitude of the flux caused by the current in the primary.

Register to Reply
Guru

Join Date: Apr 2011
Posts: 8006
Good Answers: 286
#2
In reply to #1

Re: High Leakage Transformer .

04/21/2013 1:47 AM

'...the magnitude of the flux caused by the current in the secondary will be only slightly less than the magnitude of the flux caused by the current in the primary....'

.

But, of course the flux will not be nearly twice magnitude of the flux that would occur if the secondary were not there.... .....because the current in the short circuited secondary is in the direction such that it opposes changes in flux.

In short the magnitude at a certain time may only be slightly less, but in the opposite direction. Which, I think, is what the OP is after.

__________________
Eternal vigilance is the price of knowledge. - George Santayana
Register to Reply
Guru

Join Date: Apr 2011
Posts: 8006
Good Answers: 286
#3

Re: High Leakage Transformer .

04/21/2013 1:54 AM

I'll confirm that the statement is valid with the right conditions.

Further:

All other things being equal, the flux in the portion of the core under the shorted secondary is closer to zero when:

-the secondary is a better conductor (frequency dependent)

-the transformer is has more leakage especially between the primary and secondary.

-the frequency is higher (with a caveat related to the better conductor condition above)

__________________
Eternal vigilance is the price of knowledge. - George Santayana
Register to Reply
Associate

Join Date: Jun 2012
Posts: 49
#4

Re: High Leakage Transformer .

04/21/2013 10:11 AM

Actually the transformer works at 60 HZ frequency - Is a ferroresonance transformer with high leakage inductance.

Register to Reply
Guru

Join Date: Apr 2011
Posts: 8006
Good Answers: 286
#7
In reply to #4

Re: High Leakage Transformer .

04/22/2013 1:49 AM

....and this changes the scenario, how exactly?

.

oh, wait.

What is the thickness of a lamination in the core? Also, what it the effective cross sectional area and the length of the path through the core?

__________________
Eternal vigilance is the price of knowledge. - George Santayana
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#5

Re: High Leakage Transformer .

04/21/2013 10:40 AM

What is the point of operating a transformer in short circuit without its protective devices operating to stop it happening? Is this some kind of joke? Does the individual doing it have some sort of unfulfilled death wish?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Associate

Join Date: Jun 2012
Posts: 49
#6
In reply to #5

Re: High Leakage Transformer .

04/21/2013 10:59 AM

Actually ferroresonant transformer works as a "Constant Voltage Transformer" - It is self protected against short circuit at its output - It passes only 1.2 -1.6 of its rated current at short circuit - and it can run short circuited for years without damage.

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#8
In reply to #6

Re: High Leakage Transformer .

04/22/2013 4:20 AM

And why would one want to operate a transformer that isn't supplying power to its downstream load?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Power-User

Join Date: Jun 2009
Posts: 134
Good Answers: 11
#9

Re: High Leakage Transformer

04/22/2013 10:05 AM

Actually I designed a transformer for 100% impedance per the customer's specification.

The customer wanted to hipot cable and he wanted the current to continue after the cable failed. Customer never said if he wanted to make sure the cable had a positive failure or if he was trying to locate the failure.

Register to Reply
Associate

Join Date: Jun 2012
Posts: 49
#10
In reply to #9

Re: High Leakage Transformer

04/22/2013 10:21 AM

Actually I want to design a Constant Voltage Transformer (CVT) 120V, 500VA - FERRORESONANT

Any special design equations or procedurs are available for that ?

Register to Reply