20 kV Delta System

04/23/2013 2:59 AM

I found a strange thing when I went to site.

On the 20 kV Delta system, I found the Zigzag transformer + NGR connected to the main 20 kV busbar. But they also have 5 units of step-up transformer (0.38/20kV) that is connected to the LV generator (Y - floating) with Delta on the 0.38 kV side, and Y on the 20 kV side. Now, all of the the neutral of the transformers is solidly grounded. Should I take out the solid ground, and left the 20 kV to be Y-floating?

Register to Reply
Pathfinder Tags: 20 kV Delta System
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: 20 kV Delta System

04/23/2013 3:16 AM

Why would one want to do that?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#2

Re: 20 kV Delta System

04/23/2013 4:58 AM

The zingzag Trafo + NGR is for the bus earthing, by creating an artificial neutral on the 20kV Delta side, to avail the benefits of an earthed system.

The 380V LV generator neutral is solidly grounded for human safety reasons. For, only when solidly grounded, the single-line-to-earth fault current would be equal to the three phase symmetrical short circuit current and even any short circuit protective device would isolate the faulty portion without the ned for any special earth leakage protective device.

Register to Reply
Guru

Join Date: Nov 2007
Location: Eastern Arizona mountains on Route 666 about a mile from God's country
Posts: 1676
Good Answers: 122
#3

Re: 20 kV Delta System

04/23/2013 12:30 PM

No.

It is very important that you maintain low impedance, common neutral bussing connected to ground on all the transformer "Y" star-points.

If you interrupt/disconnect the ground continuity the "B" phase voltage will become unstable and significantly higher than the other two phases. (A, C)

This will severely disrupt the system protection and will cause circuit differential voltage tripping.

__________________
They said; "Brain size?" I heard; "Train size?" so I said: "I'll take a small one, thank you."
Register to Reply
Commentator

Join Date: May 2011
Posts: 80
#4

Re: 20 kV Delta System

04/23/2013 11:53 PM

Thanks electricalexpert65 and SHOCKHISCAN for your comments.

To summarize all, the neutral of the Y generator should be solidly grounded for personel protection, and the phase of the Y generator can be connected to the LV Delta transformer, while the neutral of the MV Y transformer should be bussing connected to ground?

But what should I do with the ZZ transformer then?

And bussing to ground the MV side of the transformers would create higher fault rate?

Register to Reply