Circuit Breaker Rating for Fire Pump Controller: Need Urgent Help

04/23/2013 5:08 AM

Hi..

I need help with determining the size of circuit breaker for my foam pump installation.

In my case , the motor load is 25 KW max and full load current not more than 45 A. The circuit breaker provided by the vendor is of 150 Amp rating and is referring to NFPA 20 10.4.2,10.4.3& 10.4.4

NFPA 10.4.4 refers to tripping time of 3 minutes at a minimum of 300 % of motor full load current.

Does that mean you will have to size the circuit breaker as 150 amps.

My electrical team is telling 115% is enough citing 10.4.3.3.1 ,so 63 amp is suffcient.

I am not an electrical guy and I am unable to decide which is correct?

Can anyone tell me the circuit breaker rating required. is it 63 amp or 150 amp?

The controller manufacturer is from US .

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Circuit breaker rating for fire pump controller: need urgent help

04/23/2013 5:18 AM

In the absence of an electrical standard to work to, play safe and install the 150A one. To hell with the additional expense.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Member

Join Date: Apr 2013
Posts: 5
#2
In reply to #1

Re: Circuit breaker rating for fire pump controller: need urgent help

04/23/2013 6:10 AM

NFPA standards are applicable.

I believe NFPA 20 & NFPA 70 is relevant in this case.

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#3
In reply to #2

Re: Circuit breaker rating for fire pump controller: need urgent help

04/23/2013 6:10 AM

Follow the standard, then. If in doubt, consult a qualified Electrician locally. Make sure a test certificate is forthcoming after installation, recording the correct nature of the installation.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Member

Join Date: Apr 2013
Posts: 5
#4
In reply to #3

Re: Circuit breaker rating for fire pump controller: need urgent help

04/23/2013 6:18 AM

Unfortunately ,I am not clear from the standard.

Whether the standard requires circuit breaker to be sized minimum 125% i.e 63 Amp or 300% ie 150 amp?

Sorry but I am not good wit these electrical terms.:(

Register to Reply
2
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#5

Re: Circuit Breaker Rating for Fire Pump Controller: Need Urgent Help

04/23/2013 8:46 AM

Go with what the manufacturer is telling you. They are the experts on the equipment, not you're electrical team.

If these pumps are for fire control you wouldn't want them to trip, would you?

__________________
The reports of my death are greatly exaggerated.
Register to Reply Good Answer (Score 2)
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#6

Re: Circuit Breaker Rating for Fire Pump Controller: Need Urgent Help

04/23/2013 11:16 AM

If this is classified as a fire pump, and built accordingly, NFPA takes precedence.

Your "electrical team" isn't correct even with regard to the NEC.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Member

Join Date: Apr 2013
Posts: 5
#7
In reply to #6

Re: Circuit Breaker Rating for Fire Pump Controller: Need Urgent Help

04/23/2013 11:24 AM

But NFPA 20 10.4.3.3.1 says circuit breaker electrical charcterstic to be minimum 115 percent of full load current only .

Is it requiring 300 percent ?

Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#12
In reply to #7

Re: Circuit Breaker Rating for Fire Pump Controller: Need Urgent Help

04/24/2013 12:41 AM

Yes. Please reread your original post, where it says that 300% for 3 minutes is required.

(The minimum of 115% does not prevent the CB from being larger, as needed to fulfill other required items.)

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Anonymous Poster #1
#17
In reply to #7

Re: Circuit Breaker Rating for Fire Pump Controller: Need Urgent Help

04/24/2013 5:22 AM

Now you're arguing. Stop it.

Register to Reply Score 2 for Off Topic
3
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#8

Re: Circuit Breaker Rating for Fire Pump Controller: Need Urgent Help

04/23/2013 11:44 AM

The rules for sizing of protective devices on fire pump systems are different from the normal rules for sizing for regular electrical equipment. The core concept on fire pumps is "Run to Destruction", meaning that there is to be as LITTLE equipment protection as is possible for them. The only thing you are attempting to do with electrical protective devices in fire pump systems is to avoid starting ANOTHER fire in the equipment room. All other considerations are forgone.

So there is a MINIMUM sizing of the device itself, to avoid someone getting too cheap, and there is a separate issue on the trip settings. Don't confuse them.

And unless your "electrical experts" have very SPECIFIC training and expertise on FIRE PUMP SYSTEMS, ignore them. Generally, anyone making a FIRE PUMP CONTROLLER will follow all of the proper rules and regulations. Here in the US (I don't know where you are) you are NOT allowed to "roll your own" fire pump controller, you must have a UL Listed Fire Pump Controller, and the UL-218 rules for them are of course very specific and different from the regular rules for electric motor controllers. Bottom line, buy something that says it is a UL-218 Listed Fire Pump Controller and you are going to be covered.

http://www.ul.com/global/documents/offerings/perspectives/regulators/technical/ul_FirePumpsControllerApplications.pdf

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply Good Answer (Score 3)
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#10
In reply to #8

Re: Circuit Breaker Rating for Fire Pump Controller: Need Urgent Help

04/23/2013 7:48 PM

I love this attitude of maintenance electricians "it might burn out without the correct protection".

So what? The buildings on fire!

BTW I've spent all my life in electrical maintenance. I've pulled some crazy tricks to get a process back under control. Motor protection? Who gives a stuff! There's going to be a very big bang if the process gets out of control.

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Participant

Join Date: Jul 2013
Posts: 1
#19
In reply to #8

Re: Circuit Breaker Rating for Fire Pump Controller: Need Urgent Help

07/25/2013 3:57 PM

Per NEC/NFPA70 695 and NFPA 20 the main breaker in the controller is rated at 300%, but the supply breaker must be 6 times FLA or locker rotor. The cable is still sized per NEC 430 @ 125% of FLA. Basically you only want short circuit protection and not over current. You do not want the controller to trip out because of amps during a fire. I do this all day every day for fire protection. Please feel free to contact me if needed.

P.S. The main breaker in the controller is considered lock rotor protection breaker. If coming off a transformer the protection is on the primary side only and rated to carry locker rotor and additional pump house loads only related to fire pumps and not the secondary. It would be too costly if on the secondary side as well.

Register to Reply
Guru

Join Date: Nov 2007
Location: Eastern Arizona mountains on Route 666 about a mile from God's country
Posts: 1676
Good Answers: 122
#9

Re: Circuit Breaker Rating for Fire Pump Controller: Need Urgent Help

04/23/2013 12:23 PM

The circuit breaker is sized to protect the motor lead conductors, not the motor.

The circuit breaker must also be capable of withstanding the high motor current "inrush" during starting which is often 3 x FLA without tripping/opening and rendering the pump unavailable.

The motor lead conductor size has been designed by the manufacturer to meet NFPA and NEC requirements.

Motor protection is is provided by the motor starter and/or motor protection relay(s).

__________________
They said; "Brain size?" I heard; "Train size?" so I said: "I'll take a small one, thank you."
Register to Reply Score 1 for Off Topic
Power-User

Join Date: Nov 2012
Posts: 142
Good Answers: 14
#13
In reply to #9

Re: Circuit Breaker Rating for Fire Pump Controller: Need Urgent Help

04/24/2013 1:40 AM

Can't see why this one got an off topic, but probably done by one of the same as usual know-alls.

The response is absolutely correct in that a circuit breaker is there only to protect the circuit conductors which should be sized to adequately carry the required circuit loading, the starter overloads are there to protect the motor.

Whilst fire protection apparatus have specific requirements regarding tripping values, the above still holds true.

Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#15
In reply to #13

Re: Circuit Breaker Rating for Fire Pump Controller: Need Urgent Help

04/24/2013 2:40 AM

Fire pump motors are not equipped with overload relays.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#11

Re: Circuit Breaker Rating for Fire Pump Controller: Need Urgent Help

04/24/2013 12:16 AM

Does NFPA mention anything about method of stating(DOL,star delta,AT,VFD etc) for 300% FLC?.

__________________
pnaban
Register to Reply
Member

Join Date: Apr 2013
Posts: 5
#14

Re: Circuit Breaker Rating for Fire Pump Controller: Need Urgent Help

04/24/2013 2:12 AM

Thanks everyone..

Its clear for me.

I am going with the 150 amp so that the electrical motor doesn't trip easily.

Thanks again..

Register to Reply
Power-User

Join Date: Jun 2012
Posts: 115
#16

Re: Circuit Breaker Rating for Fire Pump Controller: Need Urgent Help

04/24/2013 2:41 AM

Check in the panel whether the over load relay is provided or not If it is provided means we can adjust in the relay as class 5,10,20 & 30 this over load relay will help us to trip in 5,10,20 & 30 sec in the sense no need to worry about the more starting current for motor.So we can select 63A circuit breaker If the OLR relay is provided.

Register to Reply Off Topic (Score 3)
Commentator

Join Date: Jan 2013
Posts: 70
#18

Re: Circuit Breaker Rating for Fire Pump Controller: Need Urgent Help

04/24/2013 1:40 PM

Hi. all

The electrical equipment dedicated to emergency condition have a proper regulation in all kind of standard through the world.

I think JRaelf is right, you will've to adopt a limit in between, ie. not to create another fire in the equipment room but at same time not to trip the fire pump in the middle of the existing fire. The best you can do is to install the 150 A CB and an additional overload alarm, so on critical condition event someone will decide what action have to be take (as Salomonical decision)

Bye

Register to Reply Score 1 for Good Answer
Register to Reply 19 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); bwilko (1); jerine (4); JRaef (1); juan J. Isdray (1); Ken Burns (1); Muthuvel (1); pnaban (1); PWSlack (2); SHOCKHISCAN (1); TonyS (2); Tornado (3)

Previous in Forum: 20 kV Delta System   Next in Forum: Aluminum Wired Fan vs. Copper Wired Fan

Advertisement