Switchroom in Fertilizer Industries

04/24/2013 3:11 PM

Hi all

Now I request from your wise opinion about how do you consider the best method to protect electrical equipment (MCC & Switchroom) installed in switchroom building from hazardous explosive gas and vapor sorronding this area in a fertilizer plant.

The point is:

  1. Should I can use pressurized, air conditioning or both method to prevent switchroom gas penetration into this local.
  2. Also, how to avoid gas penetration into sitchtroom though cable trench and cable trays entries

Bye

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Marine Engineering - New Member

Join Date: Sep 2008
Location: Vancleave, Ms about 30 miles inland from Biloxi and the coast
Posts: 3197
Good Answers: 106
#1

Re: Switchroom in Fertilizer industries

04/24/2013 3:28 PM

Use explosion proof motors and switchgear. Fans should also have explosion proof motors for venting enclosures. DO NOT USE ELECTROSTATIC FILTERS. There are many wrong ways, but only one right way. Additionally, all tools used should be spark proof; flooring should be static resistant; even the clothes you wear. There are standards that must be followed for environments that may be potentially explosive.

__________________
Mr.Ron from South Ms.
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#2
In reply to #1

Re: Switchroom in Fertilizer industries

04/24/2013 6:31 PM

What, in a switchroom?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#3

Re: Switchroom in Fertilizer Industries

04/24/2013 6:33 PM

The site has a serious process materials containment problem. Solve that problem first.

Next, have a potentially explosive atmospheres zoning drawing created by a Chemical Engineer that is practised in these things.

If the switchroom is inside any hazardous area zone after that step, do not energise it. Rebuild it outside the zone instead.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
3
Guru
Canada - Member - If there is a way to screw someting up, there is someone to do so! Safety - Hazmat - New Member

Join Date: Mar 2007
Location: Iqaluit, NU. Canada
Posts: 1854
Good Answers: 140
#4

Re: Switchroom in Fertilizer Industries

04/24/2013 10:48 PM

Stop right now..

The only way to proceed is to hire a competent engineering firm to do a FULL evaluation of the situation to come to a proper and appropriate course of action that is tailored to the reality of this facility.

The ability of local maintenance staff, the access to proper spare materials, the buy in of plant management, the physical layout of the facility, the level of housekeeping employed, etc. etc, must all be analyzed to make a proper determination on not only what is the best approach but how that approach should be implemented.

Doing less than this may put you on the main page of CNN, like another recent fertilizer facility. This is not something that should be taken lightly!

__________________
Joe Contractor to Electrical Inspector, "What do you mean you are going to make me follow the code?".
Register to Reply Good Answer (Score 3)
Commentator

Join Date: Jan 2013
Posts: 70
#9
In reply to #4

Re: Switchroom in Fertilizer Industries

04/29/2013 1:10 PM

Ok friends

Thanks a lot for your comments, before close this case I would like to let you know as follow: I'm pesuaded it is a very delicated issue to be solve in a forum, but my intention was just share ideas about this matter.

The actually in fact is that I have to define a proporsal project from bidder that are considering switchrooms building placed in hazardous areas as common practice in all fertilizer plant (IEC-60079-13) just to find the load center as all of your know.

The whole hazardous zones are full evaluated as per correspond to different gases that could be present in each zone in particular (zones 1 & 2).

Referent to cable trench, my proporsal was sand filled and cable trays with ROXTEC at all cables trays entries.

The point is that bidder proposed the switchrooms only provide with pressurized, rejecting the installation of air conditionig too. I think they are making a mistake ignoring the air conditionig because this action could leads to equipment damage due to lack of humidity control therefore the condentation will damage the internal installed electrical equipment.

Bye

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#5

Re: Switchroom in Fertilizer Industries

04/25/2013 5:18 AM
__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply Score 1 for Good Answer
Power-User
India - Member - New Member

Join Date: Jul 2010
Location: India
Posts: 162
#6

Re: Switchroom in Fertilizer Industries

04/25/2013 8:12 AM

Which plant...??

NH3

__________________
When was last time you did something for first time.
Register to Reply
Guru

Join Date: Sep 2008
Posts: 706
Good Answers: 32
#7

Re: Switchroom in Fertilizer Industries

04/25/2013 10:24 AM

As a minimum bring in an air supply line/duct from outside the HAZ (hazardous air zone) and make sure the building is accessed via an airlock to maintain positive pressure in the building. I would assume it's a totally enclosed concrete block building with no windows as a starter. You can heat or cool the air as it comes in and vent it as needed through a vent stack well above roof level.

__________________
Spinco
Register to Reply
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#8

Re: Switchroom in Fertilizer Industries

04/25/2013 3:18 PM

Should I can use pressurized, air conditioning or both method to prevent switchroom gas penetration into this local.

It depends on what the switchboard room is zoned as. Get someone qualified to zone the areas of the plant first before you proceed any further. Air conditioning is not a form of hazardous area protection and neither is pressurizing an entire switchboard room to make it into a safe area.

In fact your main switchboard room should be in the safe area, with distribution switchboard(s) located in the hazardous areas being Ex ed (or similar).

Also, how to avoid gas penetration into sitchtroom though cable trench and cable trays entries

You need to seal the holes and cables to prevent gas passing from one zone to another, especially from a hazardous area zone to a safe zone. This can be done with cable glands, barrier glands, special sealing compound, etc. It depends on the cables, the zone, the application, etc.

More information can be found in the applicable IEC 60079 (or similar) standards for cable installations.

Try talking to a hazardous area equipment supplier directly like Stahl.

__________________
jack of all trades
Register to Reply
Register to Reply 9 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers: