I don't like to ask questions before I do a proper research, but I'm pressed for time and have to come with a sensible explanation for one of my clients.
It's a contour measuring station ($100k range) that perennially blew fuses in one of the power supply that provide power for two drives (1.5kW each) driving two motors of, so far, unknown specs.
After finding a magnetic break intermittent I thought I hit it, but after that the fuse kept blowing. Checked the drive, did a signature components comparison against the good one, one drives the motor moving camera on Y axis, the other turns the measured piece (the fuse was blowing when the camera was trying to move).
Didn't find anything, check the motor, no abnormalities, so I put 10A fuse (drive commissioning calls for 10A in power supply, application has 6A, and.. everything started working just fine. Lowered the fuse value to 8.5A, works fine for a month now.
There are two more machines like that blowing fuses as well just not that often, I suspect fuse value is underrated
I know without the motor spec it's difficult to rate a fuse. I just need a general good designing approach how to find a proper value. Slow blow, then what % of the max current for starters.
TIA