Earthing Cable with the Armoured Power Cable (Hv/Lv)

05/12/2013 8:37 AM

Hi friends do we need to lay additional Earthing cable with the armoured power cable (Hv/Lv) system. Is there any international standard?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#1

Re: Earthing Cable with the Armoured Power Cable (Hv/Lv)

05/12/2013 10:20 AM

You might try searching, before asking someone else to do your work for you!!

ISO - International Organization for Standardization

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#2

Re: Earthing Cable with the Armoured Power Cable (Hv/Lv)

05/12/2013 4:47 PM

Not if one of the conductors inside the armour were an earth conductor.

There are very few international electrical standards, as there are so many countries, each of which has a slightly different way of doiing things.

In the absence of an international standard, some countries use British Standard 7671, particularly where the suply is 230VAC 50Hz.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Feb 2013
Posts: 2004
Good Answers: 31
#8
In reply to #2

Re: Earthing Cable with the Armoured Power Cable (Hv/Lv)

05/13/2013 2:24 AM

Not quite true as you know nothing of the system voltage, cable type, (3 or single core), earth fault currents for the area and if this is in a sub station, duct, trench or cable rack. This lad has offered no details, so your inofrmation is totally irrelevant, either in the UK or USA or anywhere. He needs to check his own regs and know what he is working with. And, all steel wired armour cables should be mechanically glanded off, to a steel gland plate, which is earthed. Standard practise incase the cable is struck by a digger machine, pick or shovel. Even short run lengths need the armour earthed solidy. (At one end for the least). Personnel protection.

Register to Reply Score 1 for Good Answer
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#10
In reply to #8

Re: Earthing Cable with the Armoured Power Cable (Hv/Lv)

05/13/2013 3:35 AM

<...nothing of the system voltage, cable type, (3 or single core), earth fault currents for the area and if this is in a sub station, duct, trench or cable rack..>

- a situation shared with the whole of the rest of the forum at this time.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#3

Re: Earthing Cable with the Armoured Power Cable (Hv/Lv)

05/12/2013 11:06 PM

If the cross section and material of armour is sufficient/satisfactory to carry the fault current till it is interrupted why don't you use it for earth continuity?. Check standards/codes.

__________________
pnaban
Register to Reply
Guru

Join Date: Oct 2009
Location: sometimes Wales,UK.. was Libya, now Oman!
Posts: 1715
Good Answers: 117
#4

Re: Earthing Cable with the Armoured Power Cable (Hv/Lv)

05/13/2013 12:18 AM

Yes there are standards, and yes you should run a earth cable.

Standards... you need to find the one that applies to where you are, or adopt a known standard.

Why run a earth core? Depends on if you armour has the csa to carry the fault current. It was common practice many years ago, however the armour is just that... armour to protect the cable against mechanical damage. Furthermore, as in many cables the armour is some sort of lightly protected metal , and the SWA cable gland was brass, in a right conditions corrosion would occur where the gland gripped the armour, rendering your earth path to almost nothing. So to be sure you have your item earthed.. run a earth conductor

__________________
The square root of nothing is what you make it!
Register to Reply
Participant

Join Date: Dec 2011
Posts: 3
#5
In reply to #4

Re: Earthing Cable with the Armoured Power Cable (Hv/Lv)

05/13/2013 1:06 AM

Thanks brich

Can you give me the standard reference as it is in IEC or IEEE/NEC with reference number.

Register to Reply
Guru

Join Date: Oct 2009
Location: sometimes Wales,UK.. was Libya, now Oman!
Posts: 1715
Good Answers: 117
#17
In reply to #5

Re: Earthing Cable with the Armoured Power Cable (Hv/Lv)

05/13/2013 11:23 AM

My friend.. the short answer is NO!

Why?

Because if you can find CR4, then you are clever enough to find the standards, and you will remember.

If you need help with those standards, yes I will if possible help, but I refuse to do your work for you!

__________________
The square root of nothing is what you make it!
Register to Reply
Guru

Join Date: Feb 2013
Posts: 2004
Good Answers: 31
#20
In reply to #17

Re: Earthing Cable with the Armoured Power Cable (Hv/Lv)

05/13/2013 1:22 PM

Are you on the same grumpy pills I am on?

Register to Reply
Guru

Join Date: Oct 2009
Location: sometimes Wales,UK.. was Libya, now Oman!
Posts: 1715
Good Answers: 117
#21
In reply to #20

Re: Earthing Cable with the Armoured Power Cable (Hv/Lv)

05/13/2013 10:23 PM

sure am!! 1000mg twice a day!! makes me grumpier than a water buffalo with a tick up its butt!!

__________________
The square root of nothing is what you make it!
Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#22
In reply to #21

Re: Earthing Cable with the Armoured Power Cable (Hv/Lv)

05/13/2013 10:43 PM

Clarification please.

Is it tick?

Register to Reply
Guru

Join Date: Oct 2009
Location: sometimes Wales,UK.. was Libya, now Oman!
Posts: 1715
Good Answers: 117
#24
In reply to #22

Re: Earthing Cable with the Armoured Power Cable (Hv/Lv)

05/14/2013 12:03 AM

Tick!

Small biting insect, that can leave an infection, or pass on infections.. Hence grumpiness of water buffalo and Welshmen stuck in a hot, dry Libyan desert.

for further explanation please go to Wikipedia!

__________________
The square root of nothing is what you make it!
Register to Reply
Guru

Join Date: Feb 2013
Posts: 2004
Good Answers: 31
#9
In reply to #4

Re: Earthing Cable with the Armoured Power Cable (Hv/Lv)

05/13/2013 2:42 AM

Agreed, the SWA is for protection, but if it is NOT earthed and the SWA is damaged by a JCB bucket, and the bucket tooth hits a live core, the system does not trip! One live JCB, one fried operator. Fact! The armour gets earthed by some means and a mechanical gland is best, if you know how to install it properly. Old days we used lead wipe glands, Armour and lead connected to the gland. I wonder why we went to so much hassle? Did we know something then, we dont know now?

Register to Reply
Guru

Join Date: Oct 2009
Location: sometimes Wales,UK.. was Libya, now Oman!
Posts: 1715
Good Answers: 117
#11
In reply to #9

Re: Earthing Cable with the Armoured Power Cable (Hv/Lv)

05/13/2013 5:28 AM

As most SWA glands are metal (brass or S/S) and usually fixed to a metal box and the metal box would hopefully be earthed, the armour would be earthed. In the case of the box being made of a non-conducting material such as fibreglass then a earth washer would be used and the armour would be bonded to the most suitable earth point, using an earth cable with a suitable csa. That would be sufficent to earth the armour and prevent your fatal accident, would you not agree?

I did not say that the gland was not earthed, did I?

The SWA is looked upon as a supplimentary earthing and not to be confused with the main earth of any cable or supply. Previously before gland earth washers for SWA cables, a small section of the outer insulation was removed and an external earth clamp was connected to the armour, and if jointing a large "pilcswa" cable, the cast iron joint box was also earthed.. but I digress..

__________________
The square root of nothing is what you make it!
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#12
In reply to #11

Re: Earthing Cable with the Armoured Power Cable (Hv/Lv)

05/13/2013 5:54 AM

Quite.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Feb 2013
Posts: 2004
Good Answers: 31
#13
In reply to #11

Re: Earthing Cable with the Armoured Power Cable (Hv/Lv)

05/13/2013 7:50 AM

No, you are correct, you stated; ...metal box would hopefully be earthed.. I think this was what you stated. It either is earthed, or it is not earthed. There are no half measure when earthing a system. Won't argue a meaningless point but will agree with you, 'the armour would be bonded to the most suitable earth point, using an earth cable with a suitable csa'. Cheers.

Register to Reply
Guru

Join Date: Oct 2009
Location: sometimes Wales,UK.. was Libya, now Oman!
Posts: 1715
Good Answers: 117
#16
In reply to #13

Re: Earthing Cable with the Armoured Power Cable (Hv/Lv)

05/13/2013 11:20 AM

like I said.. 'hopefully be earthed'.... but that really depends on who has installed the box, cable...etc.

Having worked all over the world.. I cannot begin to describe what I have seen as a 'safe' electrical installation.... hence the word.. 'hopefully'..

One can only hope!

__________________
The square root of nothing is what you make it!
Register to Reply
Guru

Join Date: Feb 2013
Posts: 2004
Good Answers: 31
#6

Re: Earthing Cable with the Armoured Power Cable (Hv/Lv)

05/13/2013 1:57 AM

It seems there are many lazy folks out there waiting for others to do alltheir work. Have you tired checking any standard? Do you even know what your earth fault currents are for the installion? If you knew these simple facts you might calculate the armour wire size, armour wire type, Galv versus copper and you might add details of your system voltage, cable type, soil type, run lengths, before asking for miracles. Perhaps we should charge for services rendered or issue certificates. Did anyone teach anything at college or Uni. Did you listen to what was informed to you. First stop; check your own requirements, 2nd stop;know what standards you utilise, 3rd stop; check your current standards, 4th stop; know the system you are working on.

Good advice is found here, but only you can stop yourself being killed. Lyn may be sarcastic, but he has a valid point.

Register to Reply
Guru

Join Date: Feb 2013
Posts: 2004
Good Answers: 31
#7

Re: Earthing Cable with the Armoured Power Cable (Hv/Lv)

05/13/2013 2:11 AM

And I forgot, what gland type are you using? Are you even glanding the cable off, or using wood blocks, earth starp and connection? Details my son, b*llsh*t is everywhere, facts are rare. Facts keep you alive, b*llsh*t kills. I make no apology to be so to the point, happy to help. But if you cany give detail you could end up injuring another or even wrse, you geting injured or even ....You are adding safety to a system, personnel and equipment. How can you get remedial facts if you dont know what you are doing or what you have existing. Done, Do it right First Time!!!

Register to Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#14

Re: Earthing Cable with the Armoured Power Cable (Hv/Lv)

05/13/2013 8:06 AM

Not necessary as long as the armour cross section has the sufficient short time withstand current rating and is earthed properly.

Register to Reply
Guru

Join Date: Oct 2009
Location: sometimes Wales,UK.. was Libya, now Oman!
Posts: 1715
Good Answers: 117
#18
In reply to #14

Re: Earthing Cable with the Armoured Power Cable (Hv/Lv)

05/13/2013 11:26 AM

Wrong!

__________________
The square root of nothing is what you make it!
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#15

Re: Earthing Cable with the Armoured Power Cable (Hv/Lv)

05/13/2013 10:53 AM

...however, it is necessary if it is required by the end Client's electrical specifications, whoever "we" might be. Those documents cannot be seen from here.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Feb 2013
Posts: 2004
Good Answers: 31
#19
In reply to #15

Re: Earthing Cable with the Armoured Power Cable (Hv/Lv)

05/13/2013 1:16 PM

Well dont worry to put your glasses on, I put mine on and I still could not see the documents. (I did see the naked lady next door though).

Register to Reply
Active Contributor

Join Date: Jan 2013
Posts: 18
Good Answers: 2
#23

Re: Earthing Cable with the Armoured Power Cable (Hv/Lv)

05/13/2013 10:52 PM

It has been my experience and also a code standard, that armor on cabling may not be used as an earth or common ground, as it would then be considered a conductor in the system. Use a separate cable, sized appropriately to handle the current and resulting temperature rise of a ground fault or short.That said, armor may be used as an RF shield if connected to earth on one end only, very handy if a VFD is used to control a motor in the circuit.

Register to Reply Score 1 for Off Topic
Guru

Join Date: Oct 2009
Location: sometimes Wales,UK.. was Libya, now Oman!
Posts: 1715
Good Answers: 117
#25
In reply to #23

Re: Earthing Cable with the Armoured Power Cable (Hv/Lv)

05/14/2013 12:14 AM

The armour cannot be used as a RF shield as it does not have the qualities or properties to perform that task. further to your statement I have installed many VSD's WITHOUT armoured cable

And to clarify to one and all, a separate earth conductor means a core within the cable itself and that core is dedicated for the function of earthing and NOT another single core cable OUTSIDE the cable you need earth protection for.

In many large power cables 50mm csa and above the cable could be 4 or 5 core. 4 core= 3phase plus earth, 5 core= 3phase, neutral and earth. These cores are either numbered or colour coded and the earth core depending on the electrical code of the country, could contain green plus another colour.

__________________
The square root of nothing is what you make it!
Register to Reply
Active Contributor

Join Date: Jan 2013
Posts: 18
Good Answers: 2
#26
In reply to #25

Re: Earthing Cable with the Armoured Power Cable (Hv/Lv)

05/14/2013 4:36 AM

Since the OP did not specify the cable type, we are all making assumptions.

Look up IEEE 1580 Type P or Type E, Type E is purpose built for VFDs, each major conductor is individually shielded, and the metal armor is also a shield with 88% covering.

Most newer VFDs operate in the the 3-30 KhZ range and higher, which is well into the RF, and should be shielded to prevent harmonics on other system cabling, and standing wave problems on its own cabling.

If the OP was referring to common off the shelf, single phase triplex direct burial armored cable cable? They do not normally come with a 4th grounding lay, and it must be layed separately, you can order a quad lay cable but it would be special order from most cable suppliers.

Register to Reply Score 1 for Off Topic
Guru

Join Date: Oct 2009
Location: sometimes Wales,UK.. was Libya, now Oman!
Posts: 1715
Good Answers: 117
#27
In reply to #26

Re: Earthing Cable with the Armoured Power Cable (Hv/Lv)

05/14/2013 6:02 AM

I'm not sure from where you hail.. but in the UK and other parts of the world you run a 4 core cable.

With regards to your added suggestion of RF shielding from harmonics (which is another add-on from yourself) I would suggest that as the Op only asked about earthing.. why did you then add the totally un-related subject of RF shielding for VSD's?

Can we not stick to the question posed by the OP, and stop added un-related comments and suggestions?

__________________
The square root of nothing is what you make it!
Register to Reply
Guru

Join Date: Feb 2013
Posts: 2004
Good Answers: 31
#28
In reply to #26

Re: Earthing Cable with the Armoured Power Cable (Hv/Lv)

05/14/2013 6:40 AM

Your idea is sound, but toatlly untrue in this case and that is on all accounts. Sorry to let you know this. The screen is for draining purposes, not RF or VFD sheidling. 4 Cores are common as dirt, ABC (triplex) comes with a catentry wire which goes to earth and it comes with 4 conductors. I wonder where you are or where you have worked, as I really wonder about comments on this site and just how systems are operating out there. I have to wonder. The time has come the Walrus said.......

Register to Reply
Guru

Join Date: Oct 2009
Location: sometimes Wales,UK.. was Libya, now Oman!
Posts: 1715
Good Answers: 117
#29
In reply to #28

Re: Earthing Cable with the Armoured Power Cable (Hv/Lv)

05/14/2013 12:35 PM

Hi IQ

In many respects you have good points, however I would offer a little bit of advice to you, our latest 'Newbie'.

AS you have stated, "you wonder"... as do we all at some of the questions and at a lot of the answers... But we temper our replies, and offer words of encouragement and point the OP or even someone who has answered towards safe working practices.

You wonder about the comments on the site, I think many of us do, but... if it wasn't for education I'd be a clever as those you wonder about!!

A full on verbal attack is not what is needed and certainly not be tolerated, by the OP, the other users and the mediators....

So when you see, in your opinion, a comment that doesn't not make sense or is plain stupid, take a deep breath and pause! Once you master the art of biting your tongue, then you will enjoy CR4, and be able to offer good sound advice that will be well received.

__________________
The square root of nothing is what you make it!
Register to Reply Off Topic (Score 5)
Commentator

Join Date: Jan 2013
Posts: 70
#30

Re: Earthing Cable with the Armoured Power Cable (Hv/Lv)

05/14/2013 3:09 PM

SWA cable is proven to be a good earthing method for several years.

The gold rule for that is to follow a rigorous procedure to do this work. The armour is not only a mechanical protection. The cable armour shall be earthed at both ends of any interconnected equipment, the armour wire whichever be galvanized steel or aluminum, the ampacity should be able to withstand 1 sec. fault to earth current ( find it in cable cataloge)

A good practice to do a cable glanded should be done at least as follow:

  • Select the proper gland size
  • Select the gland material according to the area to be installed
  • remove the cable sheath
  • clean-up the armour wire to get a good contact
  • insert the ring brace to fasten the armour
  • Interconnect the ring brase by mean of conductor to the motor earth bolt
  • Insert a gland shroud or any wrab element to isolate the motor-gland union from external corrosive ambient.
  • Use an earth loop tester to measurement the right impedance value to permit the CB or fuses clean the fault under short circuit to earth.

The additional earth conductor is not required always in SWA cable when a good work is done

Bye

Register to Reply
Guru

Join Date: Oct 2009
Location: sometimes Wales,UK.. was Libya, now Oman!
Posts: 1715
Good Answers: 117
#31
In reply to #30

Re: Earthing Cable with the Armoured Power Cable (Hv/Lv)

05/15/2013 12:06 AM

"The additional earth conductor is not required always in SWA cable when a good work is done"

Wrong!

__________________
The square root of nothing is what you make it!
Register to Reply
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#32
In reply to #31

Re: Earthing Cable with the Armoured Power Cable (Hv/Lv)

05/15/2013 3:16 AM

If statements are supported by "quotes" from rules,regulations,standards it would be better appreciated.

__________________
pnaban
Register to Reply
Guru

Join Date: Oct 2009
Location: sometimes Wales,UK.. was Libya, now Oman!
Posts: 1715
Good Answers: 117
#33
In reply to #32

Re: Earthing Cable with the Armoured Power Cable (Hv/Lv)

05/15/2013 4:42 AM

If statements are supported by "quotes" from rules,regulations,standards it would be better appreciated.

That my friend is a two way street.... if one makes a comment without substantiating evidence, then I feel perfectly entitled to replying in the same mode that the statement was made, without support.

To me the statement requires support, but alas the person making the statement has not, and therefore I think has not read any type of electrical code, but is quoting from practices either seen or done himself.

Now if you have anything to add to the OP's question, I would like to hear it

__________________
The square root of nothing is what you make it!
Register to Reply Off Topic (Score 5)
Guru

Join Date: Feb 2013
Posts: 2004
Good Answers: 31
#40
In reply to #32

Re: Earthing Cable with the Armoured Power Cable (Hv/Lv)

05/16/2013 4:14 PM

See other posts. "There are none so blind as those who will not see". "The truth can only be found if you look for it."

Register to Reply
Commentator

Join Date: Jan 2013
Posts: 70
#34
In reply to #31

Re: Earthing Cable with the Armoured Power Cable (Hv/Lv)

05/15/2013 12:22 PM

I want to know why is it wrong, please explain yourself, I had beem working for years in a chemical plant and it work perfectly, all CB trip and fuses blow out.

The additional conductor is require in unarmoured cable as far as I know

Waiting for your explanation to know something else

bye

Register to Reply
Guru

Join Date: Feb 2013
Posts: 2004
Good Answers: 31
#35
In reply to #34

Re: Earthing Cable with the Armoured Power Cable (Hv/Lv)

05/15/2013 3:58 PM

Take a cable theory course. They are expensive. I will tell you this, the subject is very debatable, but standrad practise is Gland all SWA to earth. Short run cables earth one end only, long cable runs earth both ends. SWA IS mechanical protection BUT, it IS electrical protection as well. Proof, disconnect the SWA on a 1kV cable, both ends, hit the live cable with a pick, or JCB, to a core. If you survive, let me know how you feel when you get out of hospital.

Disconnect the copper tapes on a 11kV un-armoured, XLPE cable, from earth, repeat the process with the pick or JCB, let me know when you are out of hospital.

In the USA it is different, a pole falls over, the line stays live, they have a different earthing system. So, in sensible countries, the SWA is glanded to earth, even in petrol-chemical companies and explosive manufacturing environments. The SWA comes in contact with a live core, the earth fault relay trips out making the system safe, no or little arcing, no high amperage, no high temperatures and no injuries. Saves cable, saves you, saves expense, Clever folks we are and we teach for free. And your un-armoured cables are normally in ducts or on cable racks, not direct buried. NB on a 220KV cable the insulated sheath can have a standing voltage of 150V, hence transpositioning of cores and link boxes every 1km or near enough that distance. And the armour is down to earth, usually a corrugated sheath of aluminium. Do a cable theory course. Or employ me!

Register to Reply
Guru

Join Date: Oct 2009
Location: sometimes Wales,UK.. was Libya, now Oman!
Posts: 1715
Good Answers: 117
#36
In reply to #35

Re: Earthing Cable with the Armoured Power Cable (Hv/Lv)

05/16/2013 2:05 AM

nice one.. you beat me to it!! GA

__________________
The square root of nothing is what you make it!
Register to Reply
Guru

Join Date: Oct 2009
Location: sometimes Wales,UK.. was Libya, now Oman!
Posts: 1715
Good Answers: 117
#37
In reply to #34

Re: Earthing Cable with the Armoured Power Cable (Hv/Lv)

05/16/2013 2:18 AM

"I want to know why is it wrong, please explain yourself,".. I don't have to explain myself to anyone

"I had beem working for years in a chemical plant and it work perfectly, all CB trip and fuses blow out." If what you state is truthful then Sir, you have been damn lucky so far, as I know from personal experience chemical plants and the like are hard on glands of any type.

"The additional conductor is require in unarmoured cable as far as I know". Yep as far as you know.. so there is a gap in your education and you ability to read the posts in the chain. I strongly suggest that you expand your horizons, find a good technical book of electrical standards, IEEE or the UK electrical codes and give your an education.

__________________
The square root of nothing is what you make it!
Register to Reply
Commentator

Join Date: Jan 2013
Posts: 70
#38
In reply to #37

Re: Earthing Cable with the Armoured Power Cable (Hv/Lv)

05/16/2013 1:19 PM

By the way Mr brich, the electrical design, project, erection and guarantee of chemical plant that I mentioned were made by an English company from your country ( Simon Carves LTD) based in cables BS 5464, BS 6262 and IEC 502 and supervised by LOYS Insurance. Also CMP Gland manufacturer also from England made special FLP glands for hazardous area, maybe I had been lucky But any way I'll will take your recommend for future, just to be more careful in may next project revisions

Register to Reply
Guru

Join Date: Feb 2013
Posts: 2004
Good Answers: 31
#39
In reply to #38

Re: Earthing Cable with the Armoured Power Cable (Hv/Lv)

05/16/2013 4:03 PM

You started off so bold with your opening statement. Now you have faded. I suggest you update on IEC standards quickly, IEC 60840, 2011 to start with and all the associated standards recorded inside. If these are the standards you use. Be smart, check with your supervisor, buyers, design engineer, etc, Find out what standards they work to. Read there standards sitting on the bookshelf, then get the updated ones to read. And honestly, if you come here with well verse questions, offering proper details, (voltage, cable types, country, etc.), I am sure we will be happy to assist you, but guess work, none of us can help you with. Every system in every country is different and has it quirks. Happy reading. Happy learning.

Register to Reply
Register to Reply 40 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!