Fatal Case Study of Electrocution

05/17/2013 10:01 PM

A fatal case of electrocution. A Welder tried to disconnect faulty 2 phase welding transformer and connect a spare welding transformer without disconnection of supply. In the process he happened to touch the live wires. he was electrocuted and was declared dead before reaching hospital.

there was an RCCB 40A, sensitivity 30 mA followed by a MCB 63A.

I want to know why the RCCB didn't trip while he was touching the live wires.

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
2
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#1

Re: fatal case study of Electrocution

05/17/2013 10:29 PM

Too many unknowns, his age and health, the points of contact of his body and the equipment, phase to phase, phase to ground, voltages involved, age of equipment, etc. First you need a lawyer and then a forensic engineer onsite, not online. Remember, phase to phase contact is just another load to the RCCB. From Wikipedia:

"...An RCD will help to protect against electric shock where current flows through a person from a phase (live / line / hot) to earth. It cannot protect against electric shock where current flows through a person from phase to neutral or phase to phase, for example where a finger touches both live and neutral contacts in a light fitting; a device can not differentiate between current flow through an intended load from flow through a person..."

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Reply Good Answer (Score 2)
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#2

Re: fatal case study of Electrocution

05/17/2013 11:08 PM

That's not what the're designed for....

__________________
All living things seek to control their own destiny....this is the purpose of life
Reply
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#3

Re: fatal case study of Electrocution

05/17/2013 11:59 PM

The severity of shock depends on voltage,duration,leakage/fault current,body resistance, PPE,Earth Fault Loop Impedance etc

__________________
pnaban
Reply
Guru
Hobbies - Fishing - New Member

Join Date: Jun 2008
Location: Raleigh, NC USA
Posts: 13529
Good Answers: 468
#4

Re: fatal case study of Electrocution

05/18/2013 1:41 AM

Electricity doesn't necessarily kill; it's the ground that we need to watch.

I'm sorry for your loss.

__________________
Those who would give up essential Liberty, to purchase a little temporary Safety, deserve neither Liberty nor Safety. Ben Franklin
Reply
Guru
Hobbies - Fishing - New Member

Join Date: Jun 2008
Location: Raleigh, NC USA
Posts: 13529
Good Answers: 468
#5

Re: fatal case study of Electrocution

05/18/2013 1:47 AM

I'm not an engineer, but my guess would be, that he conducted electricity,and the RCCB didn't know to trip. Humans are just bags of salt water.

__________________
Those who would give up essential Liberty, to purchase a little temporary Safety, deserve neither Liberty nor Safety. Ben Franklin
Reply
Guru

Join Date: Dec 2010
Posts: 1686
Good Answers: 116
#6

Re: fatal case study of Electrocution

05/18/2013 3:40 AM

If the designer followed a 40 amp RCCB with a 60 amp MCB, one wonders if he got the rest of the design right.

Did the wires that killed the careless welder go through the RCCB??

Reply
Commentator

Join Date: May 2013
Posts: 86
Good Answers: 2
#7

Re: fatal case study of Electrocution

05/18/2013 6:47 AM

The answer is in the question itself. He had touched both the live wires without any linkage to earth. Probably he was wearing shoes. The burn marks on the body may provide clue about how the shock had gone through his body. If it happened as suspected above, RCCB will not trip. The breaker ratings are very poorly selected, to say the very least and the poor guy may have paid for with his life for somebody else mistake.

Reply
Guru

Join Date: Sep 2009
Posts: 1056
Good Answers: 88
#8

Re: fatal case study of Electrocution

05/18/2013 6:57 AM

RCCB trips on current differences between energized and return conductors, i.e. it detects leakage to earth, not supposed to be there, possibly by a human body touching a leaky equipment. This wasn't the case for the poor guy, he obviously made conduct between phases. Too much confidence can get you very much dead. Seen it happening many times, and many more times not happening just by luck, including of course incidents I got myself in. RIP. S.M.

__________________
Life is complex. It has a real part and an imaginary part.
Reply Score 1 for Good Answer
Guru

Join Date: Jun 2006
Location: Ottawa Canada
Posts: 1975
Good Answers: 117
#9

Re: fatal case study of Electrocution

05/18/2013 9:16 AM

I am sorry for your loss.

A GFI "should" protect a person from unbalanced shocks, but it looks like he completed a circuit from the output to ground. The Ground Fault Interruptor did not detect an unbalanced load, but rather a simple load, which it is designed to allow through.

Of course, that is a guess which assumes all equipment is working properly otherwise.

The equipment should be packed up without anybody touching, or changing anything, and be subjected to a forensic exam. It will be crime scene evidence until your coroner releases it. That might be your job, I recommend that you get independent assistance from a licenced electrical engineer to examine the equipment to find out if the GFI was faulty or mis-installed.

If your task is to be the engineer in charge of the plant, then your task is to determine if there is some underlying intrinsically dangerous situation which has been found by this tragedy, and to rectify it so that it never happens again. Start here, and get on site expertise in on it. Hide nothing. Cover up nothing. Now is the time, for the sake of the family, to find out the truth, and determine how to make things safe for other workers.

Again, my condolences on the loss of an employee who was just doing his job. Such tragedies MUST be used to make things better for all.

__________________
If it was easy anybody could do it.
Reply
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#10
In reply to #9

Re: fatal case study of Electrocution

05/18/2013 10:18 AM

If current flows from phase to ground GFCI should trip,but not trip if current flows from phase to neutral. In work places the employer should ensure workers wear PPE like shoes,gloves etc

__________________
pnaban
Reply
Commentator

Join Date: May 2013
Posts: 86
Good Answers: 2
#14
In reply to #10

Re: fatal case study of Electrocution

05/18/2013 1:01 PM

The tragedy here is that the worker would most probably have been wearing his shoes. If he was bare foot he would have had at least half a chance of surviving the shock because ELCB would / could have tripped. He would not have been wearing any insulating gloves though. Just bad luck and karma.

Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#11

Re: fatal case study of Electrocution

05/18/2013 11:35 AM

Although the other issues raised are mostly still valid, it's really all much simpler than that.

An RCCB with 30ma sensitivity is NOT meant for personnel protection, it is only for equipment protection against damage from arcing ground faults. He would have been in cardiac arrest before the 30ma threshold was attained even if the fault caused a current flow imbalance with respect to ground reference (which as mentioned, may even have never happened given the nature of the fault). Here in the US, personnel protection cannot excede 6ma, I believe it is similar for IEC regulations. But 6ma is unrealistic for something like a welder. That's why you have safety protocols on tasks involving the use of electricity.

Sorry for your tragedy, learn from the mistake.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Reply Score 1 for Good Answer
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#13
In reply to #11

Re: fatal case study of Electrocution

05/18/2013 12:07 PM

5ma RCDs are used in children's wards in hospitals

__________________
pnaban
Reply
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#17
In reply to #11

Re: fatal case study of Electrocution

05/19/2013 10:23 PM

The tripping current of RCD(mA) and the value of earth fault loop impedance(ohms),when multiplied(mAxohms/1000)should not exceed 50V,the safe touch voltage for adults. That's why BS recommends RCD of 30mA in consumer units(for a group of circuits) in homes and offices for many lights and sockets. In US 6mA is used for a single GFCI.

__________________
pnaban
Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#12

Re: Fatal Case Study of Electrocution

05/18/2013 11:41 AM

Just an annoying side issue from a grammar Nazi.

"Fatal case of electrocution" is redundant. Electrocution alone means it was fatal, electrocution means death by electric shock. If he had not died, it would be just an electrical shock. So saying "fatal electrocution" is the same as saying "death by electric shock death".

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Marine Engineering - New Member

Join Date: Sep 2008
Location: Vancleave, Ms about 30 miles inland from Biloxi and the coast
Posts: 3197
Good Answers: 106
#15

Re: Fatal Case Study of Electrocution

05/18/2013 1:38 PM

Sorry about the incident, but he should have known better than to work on circuits that are still activated. I've known electricians who will work on live circuits and it's just a matter of luck that they didn't get electrocuted. I'm sure some did. My son does this and it drives me crazy. Sometimes there is a need to work on live circuits, like on hi tension lines, but they are equipped with the proper safety gear to do so. No one else should ever work on live circuits.

__________________
Mr.Ron from South Ms.
Reply
Power-User

Join Date: Mar 2011
Location: oz
Posts: 252
Good Answers: 10
#16

Re: Fatal Case Study of Electrocution

05/19/2013 4:43 PM

Never rely on a RCD, 2% of them fail.It is only there to reduce the chances of a fatal electric shock.

Reply
3
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#18

Re: Fatal Case Study of Electrocution

05/20/2013 3:50 AM

Interesting. If the poor individual managed to contact two phases without making a circuit >30mA to ground/earth, then the RCCB wouldn't trip and the hapless individual would have simply become an unintended load across the two phases. It is unlikely that the load would have exceeded the 40A trip setting.

Was a qualified electrician there and available to isolate the supply? Why was the job carried out live? Why was there no Permit To Work system in place? What are the chances of a repeat event occurring, and what could be put in place to prevent its recurrence?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply Good Answer (Score 3)
Reply to Forum Thread 18 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

67model (1); eltech (1); JRaef (2); kramarat (2); Pattabhiraman (2); pnaban (4); PWSlack (1); RAMConsult (1); ronseto (1); SimpleMind (1); SolarEagle (1); Yusef1 (1)