Power Factor Correction

05/17/2013 5:37 AM

In an educational campus , feeded by 33 KV supply voltage at 33/11 KV substation and 11/.433KV substations at different places. The power factor correction equipment shall be installed at which supply voltage 33 KV, 11 KV or 0.433V.

Please share your views. thanks

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Power factor correction

05/17/2013 5:59 AM

Wherever it is both economic and appropriate, determined by the campus' power factor and the utility company's tariff structure.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
3
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#2

Re: Power Factor Correction

05/17/2013 8:05 AM

Near the loads; i.e., 0.433kV.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply Good Answer (Score 3)
Power-User

Join Date: Nov 2011
Posts: 171
Good Answers: 1
#3

Re: Power Factor Correction

05/17/2013 9:03 AM
Register to Reply Score 1 for Off Topic
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#4

Re: Power Factor Correction

05/17/2013 9:35 AM

You're the consultant, why don't you tell us your views and we will comment on them, after all you're getting paid we're not. If you're not willing to present your plans then go with PWS's response.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply Score 1 for Good Answer
Member

Join Date: Jun 2009
Location: Canada
Posts: 7
#5

Re: Power Factor Correction

05/17/2013 11:51 AM

On the load side!!

But tt is not as easy as u think. It depends on the load of the feeder, size and type of cable and generation (solar/wind type) if any etc. You have to do the proper analysis for capacitor size and location with the help of any powerdesign software.

I hope this helps!!

Register to Reply
Guru

Join Date: Dec 2010
Posts: 1686
Good Answers: 116
#6

Re: Power Factor Correction

05/17/2013 2:49 PM

I would suggest downstream from where the supply company has meters on which he charges you for reactive power. The voltage level will depend on where you have the reactive loads which need compensating and the cost of doing it at one voltage compared to another. There is no magic answer which substitutes for gathering detailed information on the system to enable evaluation of options

Register to Reply
Power-User

Join Date: May 2013
Posts: 351
Good Answers: 22
#7

Re: Power Factor Correction

05/17/2013 11:44 PM

The cheapest way is to do it in bulk, but then it must be variable and changible for power factor shifts. It must be after the metering point. It is more costly to do it at the loads, but that way it can come in when the load is switched on. That eliminates the need for a variable bulk reactive power and the automation to drive it.

Register to Reply Score 1 for Good Answer
Commentator

Join Date: May 2013
Posts: 86
Good Answers: 2
#8

Re: Power Factor Correction

05/18/2013 6:28 AM

Hi, It is economical to provide the compensation at 433 volts level. Are you planning for automatic scheme or fixed compensation scheme. If only APFC systems are provided, you may face problem of low power factor reading at 33 KV utility billing meter, particularly at night / low load times. This will lead to penalties by some local utility boards. If you are facing this problem, you will have to additionally provide required rating of fixed capacitors suitable to provide compensation for transformer losses, blind zone loads of APFC etc. An other option is to make use of the 33 KV load current and voltages for measurement and use these for providing compensation at 433 volts level. In this case, the APFC relay measurement inputs have to be suitable for 110 volts and 1/5 amps CT secondary. Both options have been personally used by me in installations with good results. Of course selection of KVAR rating of each switching stages is critical. Pattabhiraman

Register to Reply Score 1 for Good Answer
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#9

Re: Power Factor Correction

05/20/2013 6:58 AM

Judicious compensation would be:

Partially individual (for steady loads)

Partially Group (with APFC Scheme)

Partially Central

And, not to forget, the compensation required for the transformer no load reactive power consumption

Register to Reply Score 1 for Good Answer
Register to Reply 9 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

4wsilver (1); 67model (1); anijher (1); electricalexpert65 (1); nobodysomebody47 (1); Pattabhiraman (1); PWSlack (1); RAMConsult (1); Tornado (1)

Previous in Forum: Battery AH Capacity   Next in Forum: Fatal Case Study of Electrocution

Advertisement