Improve Voltage Drop Using Capacitor Bank

05/22/2013 3:50 AM

I have installed Automatic Voltage controller of 400KVA of input range 340-460V output 400V but now i am getting input of 290V and it has gone beyond the range of my Automatic Voltage Controller.
I want to know should i buy new AVC of 400KVA of input range 280-460V/400V or can i install capacitor bank to decrease the voltage drop?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Help: to improve voltage drop using capacitor bank

05/22/2013 4:07 AM

The first thing is to find out how and why the voltage drop is being caused. That snippet is absent from the original post.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply Score 1 for Good Answer
Power-User

Join Date: Jun 2007
Location: ether
Posts: 371
Good Answers: 1
#2

Re: Help: to improve voltage drop using capacitor bank

05/22/2013 5:47 AM

why would you install a capacitor bank?

__________________
“For no man can forbid the spark nor tell whence it may come.” ? Francis Bacon
Register to Reply
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#3

Re: Improve Voltage Drop Using Capacitor Bank

05/22/2013 3:54 PM

What is your supply voltage normally and why is it dropping down to 290V? Is it being caused by short term or long term voltage sag due to large loads on the grid switching on?

Depending on your situation a step-up transformer may be a better option, especially if the voltage is continuously lower than you local (400VAC?) supply. Just make sure that the output voltage of the step-up transformer won't go above 460V and damage your AVC.

__________________
jack of all trades
Register to Reply
Member

Join Date: Oct 2012
Posts: 7
#9
In reply to #3

Re: Improve Voltage Drop Using Capacitor Bank

05/25/2013 4:02 AM

Recently we have installed 2 No 25KVAR capacitor bank at input side on 2nd Stone crusher where no AVC is installed. When we switched on the capacitor bank the voltage drop decreased from 290V to 300V but when the stone crusher is started the input current increased and the voltage dropped again and crusher motors tripped. We are planning to add more capacitor bank and install a AVC on this crusher so that the voltage drop is decreased by capacitor banks and it comes in the range of our AVC. My question is that will this work?

Register to Reply
Guru

Join Date: Feb 2010
Posts: 1013
Good Answers: 36
#10
In reply to #9

Re: Improve Voltage Drop Using Capacitor Bank

05/25/2013 5:13 AM

Not likely!

Your source and transmission cables are to be checked. The drop is too high for these corrections. You are aggravating the condition. The AVC needs to draw more current from the low voltage available at the input, in order to pump the voltage up. ...

Register to Reply
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#11
In reply to #9

Re: Improve Voltage Drop Using Capacitor Bank

05/26/2013 3:05 PM

I don't think it will. Capacitors help with power factor correction, not voltage sag, so what you are seeing is likely an interaction not a potential fix. I could be wrong, but you need to do more research before spending a lot of money on something that may actually make things worse.

See if you can find the actual cause of the voltage drop, because if your grid supply is too weak causing the voltage sag under load you will need to consider increasing the size of your transformers instead.

__________________
jack of all trades
Register to Reply
Guru

Join Date: Jan 2008
Posts: 1753
Good Answers: 59
#4

Re: Improve Voltage Drop Using Capacitor Bank

05/22/2013 10:57 PM

If I understood you correctly, you have a 400kVA device (a sort of variable transformer) to stabilize the output voltage. But now the voltage feeding it dropped below its permissible lower limit. Did I understood correctly?

I have to presume, it is a new installation, where you try to maintain proper voltage for a new or expanded old load. Otherwise you would not need it.

Well, I have news for you. When you overload the Grid to the extent, that its voltage sags that badly, after a while no amount of local installation correct the Grid's bad sag.

Get a better, stronger, heftier feed. Then you will not lose a high % of the input voltage.

Register to Reply
Guru
Engineering Fields - Mechanical Engineering - New Member

Join Date: May 2008
Location: CHENNAI, TAMIL NADU, INDIA.
Posts: 1851
Good Answers: 65
#5

Re: Improve Voltage Drop Using Capacitor Bank

05/22/2013 11:51 PM

Dear Mr.bhupinder,

Your post does not indicate 1. the Incput-Voltage to the system. 2. The Load details - whether you use low speed motors and whether highly inductive loads.

Then we can suggest some solution.

DHAYANANDHAN.S

Register to Reply
Member

Join Date: Jan 2013
Posts: 6
#6

Re: Improve Voltage Drop Using Capacitor Bank

05/23/2013 3:19 AM

1. Analyze why the voltage dip that big (decrease the voltage to 290V).

2. If you found the reason due to voltage drop, try solve that first or ask your consultant to solve that if you can't.

3. If the problem can't solve, you have two choice, buy the new ones or buy a step up transformer.

Register to Reply
Guru

Join Date: Feb 2010
Posts: 1013
Good Answers: 36
#7

Re: Improve Voltage Drop Using Capacitor Bank

05/23/2013 6:29 AM

The Voltage drop to 290 is too low to correct with a bank of capacitors!

Also, if the input varies wildly from 290 up to 400V, then your problem is elsewhere.

Even a AVC of such a wide input range will not last long with wild variations!

better find out why !

Register to Reply
Member

Join Date: Apr 2013
Posts: 5
#8
In reply to #7

Re: Improve Voltage Drop Using Capacitor Bank

05/24/2013 10:25 AM

X2. You may be attacking the symptoms not the root of the problem.

Good Luck!

Register to Reply
Register to Reply 11 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

bhupinder (1); billjacobs (1); dhayanandhan (1); electronick (1); hurricane193 (1); jack of all trades (2); LAA_Lucke (2); leveles (1); PWSlack (1)

Previous in Forum: Manual Changeover Switch Overheat Cause   Next in Forum: AC & DC in 1 Cable Ducting

Advertisement