Necessity of Alkalizer and Online Dissolved Oxygen Monitoring System

05/28/2013 7:28 AM

Dear All,

Please help me understand, why is it necessary to have Alkalizer and Online Dissolved Oxygen Monitoring System in power plant for Generator Closed Circuit Cooling Water System (Primary Cooling Water System)?

I have heard people saying that alkalizer is not mandatory for oxygen rich stator water system or stator winding with SS hollow conductors. I want to understand what is the theory behind this?

Also, I want to know more about Online Dissolve Oxygen Monitoring System. It is said that it is best suitable to find in cooling water system of power plants which operates in low oxygen regime at neutral pH.

Now next question is whether both Alkalizer and Online Dissolve Oxygen Monitoring System can be found in same plant?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
3
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32209
Good Answers: 839
#1

Re: Necessity of Alkalizer and Online Dissolved Oxygen Monitoring System

05/28/2013 7:57 AM

Because acidic conditions and the presence of oxygen favours corrosion in many metals.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply Good Answer (Score 3)
Participant

Join Date: May 2013
Posts: 4
#6
In reply to #1

Re: Necessity of Alkalizer and Online Dissolved Oxygen Monitoring System

06/14/2013 7:48 AM

Thanks, PWSlack.

From your answer, I understand that it is better to provide alkalizer. But regarding dissolved oxygen in water, how is it possible that it will not be in DM cooling water?

Do u have any information reagrding at what levels acidic and oxygen content combination is harmful to stator windings of generator?

This will be great help.

Thanks, again.

Register to Reply
Guru
Popular Science - Cosmology - New Member Technical Fields - Technical Writing - New Member Engineering Fields - Energy Engineering - New Member Engineering Fields - Electrical Engineering - New Member Engineering Fields - Control Engineering - New Member Engineering Fields - Electromechanical Engineering - Old Member, New Association

Join Date: Apr 2008
Location: Lexington, KY
Posts: 1639
Good Answers: 73
#2

Re: Necessity of Alkalizer and Online Dissolved Oxygen Monitoring System

05/28/2013 8:01 AM

Pick a system, from here. These all have O2 monitoring, etc.

__________________
A great troubleshooting tip...."When you eliminate the impossible, whatever remains, however improbable, must be the truth." Sir Arthur Conan Doyle
Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#3

Re: Necessity of Alkalizer and Online Dissolved Oxygen Monitoring System

05/28/2013 4:19 PM

The best people to ask about the necessity of an alarm system are the people that designed the system.

Is that to simple?

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Participant

Join Date: May 2013
Posts: 4
#7
In reply to #3

Re: Necessity of Alkalizer and Online Dissolved Oxygen Monitoring System

06/14/2013 7:52 AM

Thanks for reply, TonyS. That's what I wanted to know from industry veterans. If any body who has worked in such systems earlier can help me out.

Register to Reply
Guru
Safety - Hazmat - New Member United States - US - Statue of Liberty - New Member Engineering Fields - Chemical Engineering - Old Hand

Join Date: Mar 2011
Location: Lubbock, Texas
Posts: 14331
Good Answers: 162
#4

Re: Necessity of Alkalizer and Online Dissolved Oxygen Monitoring System

05/29/2013 8:59 AM

Many generators use gas cooling as primary coolant, and the gas is cooled by water flowing through heat exchangers. I am not familiar with the system you describe, so could be a good person, and describe this in a bit more detail? Usually a closed loop cooling system that has no water leaks, there is not much requirement for chemical addition, and I have seen a few of those where no conditioning of the water is needed, other than a small addition of either nitrite solution, molybdate, or silicate. When the pH of these systems is above 9.2 and up to around 9.6 or so, corrosion has nearly vanished.

__________________
If it ain't broke, don't fix it. Just build a better one.
Register to Reply
Participant

Join Date: May 2013
Posts: 4
#5
In reply to #4

Re: Necessity of Alkalizer and Online Dissolved Oxygen Monitoring System

06/14/2013 7:42 AM

First of all, thanks all for showing interest in my question.

Dear James, Answering to you query, large machines - in the range of 500MW and more - applies water as well as gas cooling for stator and rotor. So, my question relates to closed loop cooling water system (primary coolent of stator winding), that is DM water chemistry.

Now having understood this, I would again ask to u and other engineers that is it OK if any customer says do not provide alkalizer and oline dissolved oxygen monitoring system for optimized solution of cost saving, life and over all performace?

Thanks.

Register to Reply
Guru
Safety - Hazmat - New Member United States - US - Statue of Liberty - New Member Engineering Fields - Chemical Engineering - Old Hand

Join Date: Mar 2011
Location: Lubbock, Texas
Posts: 14331
Good Answers: 162
#8
In reply to #5

Re: Necessity of Alkalizer and Online Dissolved Oxygen Monitoring System

06/15/2013 9:15 AM

Stainless steels operate in a different regime of conditions than carbon steels. To simply make a blanket statement that dissolved oxygen would be OK in such a case would be sophomoric. Stainless steels can undergo a stress-crack corrosion mechanism leading to complete failure of the metal when conditions of (1) stress, (2) oxygen, and (3) chloride or sulfate are all present. High stress systems - those where the temperature difference is the highest will experience the higher failure rates. To avoid this, in some instances, the cooling loop needs to have a higher degree of pure water where the surface temperatures are high. These plants will have a primary coolant system (cooling tower circulation), and a secondary loop (purified water goes here), with appropriate chemical additives to minimize anodic corrosion mechanisms.

__________________
If it ain't broke, don't fix it. Just build a better one.
Register to Reply
Register to Reply 8 comments

Good Answers:

These comments received enough positive votes to make them "good answers".
Copy to Clipboard

Users who posted comments:

James Stewart (2); NotUrOrdinaryJoe (1); PWSlack (1); TonyS (1); whoisme (3)

Previous in Forum: The Neon Light   Next in Forum: RTD Sensor Connect To VFD

Advertisement