RTD Sensor Connect To VFD

05/28/2013 11:55 PM

Dear all.we have 25 Hp vfd drive .we want connect RTD temp sensor to VFD for auto control of motor.please give the suggest to connect anolog input

Register to Reply
Pathfinder Tags: anlog input to VFD
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#1

Re: RTD sensor connect to vfd

05/28/2013 11:58 PM

if this is the best you can muster for information, it indicates that you probably should not be attempting this task. There is a LOT more to it that what it appears you think it is and this is not the place to learn it.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#2

Re: RTD sensor connect to vfd

05/29/2013 12:02 AM

My suggestion is to read the operator's manual.

It will have things like the manufacturer's identity, and maybe some good instructions.

With no useful information, like brand, model # etc. etc. there's not much to do here.

You might engage a professional to help you.

Register to Reply
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#3

Re: RTD sensor connect to vfd

05/29/2013 12:32 AM

Check the drive manufacturer's website as they may have a product designed for this purpose.

Alternatively you could try an RTD to analog (0/4-20mA) converter. That may do the trick, but you may need some sort of analog scaling converter to get the right temperature control or speed settings. Hopefully the suitable converter you find will be adjustable enough.

__________________
jack of all trades
Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#4

Re: RTD sensor connect to vfd

05/29/2013 12:33 AM

RTFM.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply Score 1 for Off Topic
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#5

Re: RTD sensor connect to vfd

05/29/2013 3:04 AM

Connection is one thing; actually obtaining control is another. Is there a PID controller within the drive, for starters? It will be in the manual that came with it.

If in doubt, consult a Controls Engineer.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Power-User

Join Date: Jan 2008
Location: kuwait
Posts: 132
Good Answers: 2
#6

Re: RTD sensor connect to vfd

05/29/2013 6:13 AM

just use A/D converter and a set-point (BCD or something which suits you ) make comparator circuit (single/multi set-points ) obtain the outputs from it and create your logic circuit and command the speed inputs of vfd by your logic .that,s all

__________________
love4everyone
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#7
In reply to #6

Re: RTD sensor connect to vfd

05/29/2013 6:22 AM

The original poster may need to do some loop tuning as well...

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Oct 2006
Location: Surrey BC Canada
Posts: 1571
Good Answers: 42
#8
In reply to #7

Re: RTD sensor connect to vfd

05/29/2013 11:14 PM

Loopy loop tuning?

Register to Reply Off Topic (Score 6)
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#9
In reply to #8

Re: RTD sensor connect to vfd

05/30/2013 3:16 AM

Proportional, integral and derivative. Agreed - it's an iterative process.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Jan 2008
Posts: 1753
Good Answers: 59
#10

Re: RTD Sensor Connect To VFD

05/30/2013 8:03 AM

It is only a full product development cycle, that's all. Perfectly suitable to the engineering department of the product's developer. Recommended interconnects are detailed in the manual. Outside that, you are on your own. Or hire capable adviser.

By the way, your desire is to control some processes. RTD or some such is not and cannot be a required specification.