Brine and Cooling Water Mixup

05/29/2013 5:59 PM

Dear Members,

Warning: Long mail ahead

The company i work for is a process plant which use different utilities like Brine at -20 Deg, Hotwater at 90 Deg and Cooling tower water for equipments like reactors and driers for process. Each equipment has a inlet and outlet manifold, where individual utilities are connected. When operator desires to cool the reactor he manually applies brine similarly when he desire to heat the reactor, he will close the cooling valve and open hot water valve. Attached image for reference

Now the problem is during this operation accidentally or due to valve malfunction(i.e Valve passing),different utilities are getting mixed up each other which is highly undesirable. As lot of energy is wasted in bringing a utility to the desired temperature. Problem is more serious with brine which is a mixture of water and methanol in (90%+10%), and at -20 Deg, when this gets mixed with hotwater or cooling water it looses its energy and becomes useless and additionally its treatment is also costly.

I am looking for method by which the utility mixup can be better averted or if possible a system to alert the operator in the event of mixup.

We have below at our end.

1. Putting Pneumatic valves in the utility line and interlocking them, averts the possible of accidental opening of valves, but it doesnt negate the possibility of valve passing

2. I have tried putting specific gavity sensor in each utility line, and monitoring them continously . In the event of mixup of utility with one another the specific gravity would change and generate an alarm. But his has got a limitation, the specific gravity band available for measurement is too low and practically tough to measure. Example brine has a specific gravity of 0.81 where as hot water or cooling water specific gravity near to 0.9 to 1.0. This minor difference cannot be measured.

Looking forward from members, how are others addressing this kind of issue.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
3
Guru

Join Date: Jun 2010
Posts: 1296
Good Answers: 104
#1

Re: Brine and Cooling Water Mixup

05/29/2013 6:36 PM

You could use interlocking valves to prevent more than one utility to be open at any one time, and to require the corresponding inlet and outlet valves to be opened together. This can be done manually or with air-operated valves and a PLC.

You have a different problem with cross-contamination, even if the system is operated as intended. The reactor jacket is full of whatever utility you are using when you switch. Then you are mixing the new utility with whatever's in the jacket until it is all flushed out.

Register to Reply Good Answer (Score 3)
Guru

Join Date: Dec 2005
Posts: 1602
Good Answers: 19
#11
In reply to #1

Re: Brine and Cooling Water Mixup

05/30/2013 10:35 PM

took the words right out of my mouth. Interlocking the supply and return valves is the way to go. Mechanical interlock is somewhat more fool-proof, but air operated or PLC controls might do the same thing.

Good not on cross contamination. Can the vessel be drained between utility switch-overs?

__________________
Eventually, one needs to realize that it is far less important to be the smartest person in the room than it is to sit next to that person and make friends.
Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#2

Re: Brine and Cooling Water Mixup

05/29/2013 6:50 PM

I agree with bigg. Valving and controls are easy enough to implement.

I'd add a purge or diverter valve and return the brine or water to their respective systems, or to drain.

Register to Reply
Guru
Hobbies - CNC - New Member Hobbies - DIY Welding - New Member Engineering Fields - Electromechanical Engineering - New Member

Join Date: Aug 2007
Posts: 23647
Good Answers: 420
#3

Re: Brine and Cooling Water Mixup

05/29/2013 7:16 PM

1.) As others have mentioned by having them controlled with a PLC.

2.) Or if manual (budget) by having a flow plate.

But you will still have a problem with operator era.

Or

3.) Train your personnel and hold them accountable. But to be accountable, they have to be competent.

__________________
“ When people get what they want, they are often surprised when they get what they deserve " - James Wood
Register to Reply
Commentator

Join Date: Nov 2007
Posts: 86
#4

Re: Brine and Cooling Water Mixup

05/29/2013 7:58 PM

Dear members,

If you could notice there is ball valve in the picture at the bottom, operator before changing to any utility opens this valve and applies air pressure through one of the inlet valves and flushes the reactor jacket.

We are more concerned about contamination or mixup during utility is in operation. Secondly we have some system which have pneumatic valves running on PLC, but here too the we are facing this problem but with less intensity. PLC operation doesnt negate the possibility of mixup if the valve is slightly passing or if the valve isnt closed 100%. If if there is a slightest passing, at about 5-6 Bar pressure the loss is huge over a period of time.

We have trained the operators on using the system, but the pointer stops at what if the valves are passing or not completely closed? I guess some thing that alerts operator on mixup would be ideal.

Register to Reply
5
Guru

Join Date: Jun 2010
Posts: 1296
Good Answers: 104
#5
In reply to #4

Re: Brine and Cooling Water Mixup

05/29/2013 8:24 PM

You can implement a double-block and bleed set-up. And limit switches on air-operated valves to confirm position. Oh, and preventive maintenance.

Register to Reply Good Answer (Score 5)
Guru

Join Date: Mar 2012
Location: Out of your mind! Not in sight!
Posts: 4424
Good Answers: 108
#6
In reply to #5

Re: Brine and Cooling Water Mixup

05/29/2013 9:26 PM

Have to agree here. Look at your maintenance schedule to prevent leakage from the valves. Maintain them before they leak. And never forget there is a live to everything. A valve that is in service so many years or hours will even with good maintenance fail at some point. So a replacement plan for equipment has to be implemented.

__________________
Common Sense Dictates
Register to Reply
Guru
Hobbies - CNC - New Member Hobbies - DIY Welding - New Member Engineering Fields - Electromechanical Engineering - New Member

Join Date: Aug 2007
Posts: 23647
Good Answers: 420
#7
In reply to #5

Re: Brine and Cooling Water Mixup

05/29/2013 9:40 PM

Bingo,

i would also add a leak detect, if a seal is going bad to avoid contamination.

__________________
“ When people get what they want, they are often surprised when they get what they deserve " - James Wood
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#8

Re: Brine and Cooling Water Mixup

05/30/2013 3:24 AM

Many process reactor jackets have an air inlet, a drain outlet and an air vent. Correct sequencing of valves can be carried out using any programmable device according to a pre-agreed protocol that has passed through a HazOp Study. Responsibility for correct operation then lies with the Utilities Designer, the Controls Engineer and the Maintenance Manager, which is where it should be.

No-one comes to work to be chided. It just doesn't happen in a well-run company.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Commentator

Join Date: Nov 2007
Posts: 86
#9

Re: Brine and Cooling Water Mixup

05/30/2013 2:20 PM

I wonder how are others addressing this problem, after all they must also be facing this kind of problem. What about any ideas on detecting the mixup any known techniques in place?

Register to Reply
Anonymous Poster #1
#10
In reply to #9

Re: Brine and Cooling Water Mixup

05/30/2013 4:03 PM

Have you read the posts above yours?

Register to Reply Off Topic (Score 5)
Power-User

Join Date: Jun 2007
Location: Center of the Known Industrial Universe - TUGGERAH 2259 - Australia
Posts: 259
Good Answers: 52
#12
In reply to #9

Re: Brine and Cooling Water Mixup

05/30/2013 11:04 PM

You've seen several good plans for preventing the mixup.
Since "S**t Happens" you are wise to seek also to detect a mixup.

Specific gravity measurements have not served you well, so it's worth a look at a conductivity sensor, for example:

http://www05.abb.com/global/scot/scot203.nsf/veritydisplay/4e2c7fbcb4be8725c1257958004f8da2/$file/DS_TB404-EN_C.pdf

Such a sensor will betray the presence of brine where it's not expected.

Mark Bingham
Relativity PL

Register to Reply
Guru
Safety - Hazmat - New Member United States - US - Statue of Liberty - New Member Engineering Fields - Chemical Engineering - Old Hand

Join Date: Mar 2011
Location: Lubbock, Texas
Posts: 14331
Good Answers: 162
#16
In reply to #9

Re: Brine and Cooling Water Mixup

05/31/2013 8:58 AM

Have you looked into a conductivity sensor for the fluid in the jacket? This might reveal (1) whatever the active fluid is in the jacket, and (2) if there is a trend taking place during one of the services. You could intentionally add something that is conductive (not necessarily corrosive) to the different services to distinguish them, the other is to use colorants in the different services and monitor them with a flow through spectrophotometer.

__________________
If it ain't broke, don't fix it. Just build a better one.
Register to Reply
Associate

Join Date: Dec 2010
Posts: 33
Good Answers: 1
#13

Re: Brine and Cooling Water Mix up

05/31/2013 2:18 AM

Is passing one of the fluids through a coil wrapped around the equipment ( between the equipment and outer shell) such as it will be completely isolated from the other fluid feasible? This will spare you from draining at least the brine mixture.

Register to Reply
2
Commentator

Join Date: Jan 2006
Location: Western flank of the Pennines in Lancashire England
Posts: 93
Good Answers: 8
#14

Re: Brine and Cooling Water Mixup

05/31/2013 3:21 AM

The valve interlocking has been dealt with by others but your concern with valves passing has not. One method which is used very commonly in the gas industry is to apply the double block & bleed assembly of 2 main automatic valves in series which are normally closed and a third small automatic normally open valve valve venting the space between the two main valves. If the first valve is passing it will drain out of the vent valve. When the utility is required the vent valve is closed and the two main valves are opened. If you want to go a step further you could apply a pressure test to the trapped volume once the vent valve has closed and before the main valves are opened.

Register to Reply Good Answer (Score 2)
Power-User

Join Date: May 2007
Location: Sweet home Alabama
Posts: 144
Good Answers: 7
#15

Re: Brine and Cooling Water Mixup

05/31/2013 8:15 AM

I am making many assumptions here. you are trying to conserve energy and not the OH solution. You are like many batch reactors you want to heat to temperature quickly and control at temperature. Cooling costs more than heating and refrigeration is limited more than heating. you neglected to show a recirculating loop on the diagram.

If i am right:

I suggest you watch the return temperature (not the outlet temp, but they may be the same). You should find that when it switches from heating to cooling' there is a lot of cold brine that goes into the jacket before cold brine comes out of the jacket. Switch the return flow on dropping temperature. There will be a mass imbalance because now the brine system will be droopping while hot liquid is returning to the hot system. No it will not always balance out on the backside because heating will use different volumes and return on different temperature conditions. Some of the optomization will require you to understand how the brine storage system works. If there is a warm brine return tank and a cold brine storage tank that overflows back to the warm tank is typical.

Not enough information to be more help.

Register to Reply
Guru

Join Date: Jul 2012
Location: Madison, WI.
Posts: 2074
Good Answers: 77
#17

Re: Brine and Cooling Water Mixup

05/31/2013 1:43 PM

Greetings Srao,

i agree with the other posters as to the mechanism and their application.

Still it seems you are trying to make the system "fool proof".

If that is your goal then your only option after implementation of the above posted control systems is Not To hire Fools!

__________________
Knowing is the end result of learning, not believing.
Register to Reply
Guru

Join Date: Dec 2005
Posts: 1602
Good Answers: 19
#18
In reply to #17

Re: Brine and Cooling Water Mixup

06/03/2013 10:00 AM

I heard an old joke: It is no use to make things 'fool-proof'; Mother Nature keeps providing better fools! That's one reason I prefer the term "fool-resistant".

__________________
Eventually, one needs to realize that it is far less important to be the smartest person in the room than it is to sit next to that person and make friends.
Register to Reply Off Topic (Score 5)
Guru

Join Date: Jul 2010
Posts: 669
Good Answers: 176
#19

Re: Brine and Cooling Water Mixup

06/05/2013 9:04 PM

I can't imagine not automating the piping and valving to solve the bulk of your issues, but if you still want to determine which fluid is in the pipe, 2 methods come to mind.

Refractive index is used to determine concentrations in aqueous solutions. A quick test by a prominent vendor like K-patents could determine how much the index changes and whether the magnitude of difference is sufficient to trigger an output.

The Siemens clamp-on ultrasonic flowmeter is used to differentiate grades of diesel, kerosene or gasoline, because the speed of sound (sonic velocity) is unique to each grade. In fact the flowmeter is sometimes used not as a flowmeter but to calculate API gravity of the fluid in the pipe.

A test would determine whether the sonic velocity for you fluids is different enough [over operating temperature range(s)] to be useable as a fluid identifier.

Register to Reply
Register to Reply 19 comments